Controllers with aggressive setpoint response

Translate This Thread From English to

Threaded View


Hi, Just wondering is anyone aware of a process plant control application
where the control response to *setpoint* changes has to include derivative
action. Presumably it would be the inner loop of a cascade that requires
very snappy response.



Re: Controllers with aggressive setpoint response



On 06/13/2010 12:53 AM, Noodnik wrote:

Not process plants, no, but it's certainly common in servo applications
where the whole point of the system is to follow the command -- and
which is reflected by calling the input a command, and not a set point.

If nothing else, wouldn't you find it in servo valves (or whatever
they're called)?  Perhaps it's there, masquerading under the name "feed
forward".

--
Tim Wescott
Control system and signal processing consulting
www.wescottdesign.com

Re: Controllers with aggressive setpoint response






Example plant: With disturbance z2

1,570587 v1'' + 1,262046 v1' + v1 = v2
Damping d = 0,503517

Example 1: With derivative action
Page 1

Example 2: Witout derivative action
Page 2

If just using PID control there is no chance to find a better solution
without derivative action!

* http://home.arcor.de/janch/_control/20100613-derivative-action/



JCH

 


Re: Controllers with aggressive setpoint response




Under damped systems should have a derivative gain to dampen the
system response.  If you want to place all the poles there needs to be
one controller gain for each pole open loop pole.  The integrator gain
doesn't count because it comes with its own pole.  In JCH's example
the system has two poles and they are imaginary.  Therefore the system
is under damped so two gains are necessary, the P and D gains.


Not always.  For example cascaded loop with an inner velocity loop and
an outer position loop.  The inner velocity loop may be just a simple
PI controller because the error is in velocity units.  The P gain in a
velocity loop does about the same thing as the D gain in the position
loop which uses error in position units.