Hi. I'd would like to know if anyboy could help in my DCS migration.
Today I have a TDC3000 and I'm intending to make a full subsitution of
this system to ABB AC800 or Yokogawa CS3000. First, I'd like to know if
does anybody have experienced this kind of migration. Second, if does
anybody know if I can sell my currente system (as spare parts, for
example). Is there any used DCS market anywhere (in Brazil if
possible)?
Thanks a lot for the help.


Re: honeywell tdc3000


Hi Marcos,

I've been involved in a couple of migration projects, including a
TDC2000 to AC800 migration project.
a) On the hardware side, the only option is to do re-wiring. Exactly
how you do it is dependent on a number of factors, but after the
migration project the wires must be connected directly from the field
instrumentation to the new DCS.
b) The actual change-over of loops from the old system to the new can
be done either on-line or off-line with the process shut down and many
factors would determine the best choice for each case. A combination is
very often used; do the non-critical loops on-line with the plant
running attempting to cover most loops like this and then do the
critical loops off-line with the plant shut down.
c) One must at least evaluate to do automatic software configuration.
For the existing Honeywell system you can get text files ("EB"-files to
use the Honeywell term) of the software configuration. Now you must
write a custom computer programs to convert this to a format suitable
for the new system. Although I have done something similar, I would be
very sceptical and challenge this approach. (Let's just say I've learnt
the hard way that it's not always wise to be too clever).
The default approach that I would follow is to do the software
configuration of the new system from scratch.

I hope this helps.

Pieter Steenekamp



marcos_rhco wrote:
Quoted text here. Click to load it


Re: honeywell tdc3000


With regards to the hardware, Honeywell may be interested in buying the
spare equipment as part of their certified recycled parts program.

Check the information and 'buy back form' at:
http://hpsweb.honeywell.com/Cultures/en-US/Services/MaintenanceSupport/CertifiedRecycledParts/Default.htm

Good luck with your project.

Regards,

Stewart Peake.


Re: honeywell tdc3000


Marcos,

I have been involved in two migrations. The first was from a
TDC2000/Modicon PLC system to a Foxboro I/A DCS and it involved
installing new I/O cabinets and completely rewiring all the field
devices.  We performed the migration over a two year period and had
both systems running side by side until the migration was completed.
The upside was it was a slow transition for the operators, the downside
was it took forever and rewiring everything was very expensive.  The
second migration was from a Westinghouse WDPF to a Foxboro I/A system
using migration cards and utilizing the existing Westinghouse racks and
field wiring.  An 900 I/O point system was migrated in two days.  The
upside was it was quick and very cost effective,  the downside was the
operators had a very rapid transition to the new system, although that
is quite manageable with good training.  If you haven't seen the I/A
migration route I'd definitely check it out as a comparison to your ABB
or Yokogawa solution.


Re: honeywell tdc3000


Quoted text here. Click to load it

..of course the *downside* to retaining the existing racks and field wiring
is that you are now stuck with multi-vendor support issues and when the
Westinghouse bits fail at 12 midnight because a crucial speck of dust was
disturbed during the upgrade and you've run out of spares and can no longer
buy a replacement part (because Westinghouse are p*** that you didn't go
with them), you are back where you started.

To avoid all this, you still need to progressively change over the racks and
field wiring once the new system is up and running, and since you then need
to replace your I/O cards (again!) - because migration cards don't fit in
standard racks - the cost of the project skyrockets.

Although the side-by-side method is longer and more painful - at least you
wind up with a fully-supported and up-to-date control system in the end (and
happier operators and maintenance managers ;-)

Cameron:-)



Re: honeywell tdc3000


Cameron,
I am not sure what your experience was or what company it was with but
this was my experience with Foxboro.

The only Westinghouse components that were retained were the racks, the
field wiring assembly's, and a few power supplies.  It has been my
experience that the racks and the field wiring assemblies rarely have
anything go wrong with them unless you have a catastrophic failure.  If
I need one, and I haven't since the original system was installed in
1989, I can get one from someone other then Westinghouse.  Foxboro
anticipated that most vendors won't want to support a system that was
migrated to a competitors system and fully supports the completed
installation including the non-Foxboro components of the new system.
There is no need to replace I/O cards again after the project is done.
The new migration cards are identical to the latest Foxboro I/O cards
except they are in a form that will fit into a competitors frame,  in
my case it was a WDPF Q crate.  This was a compelling reason for us to
go the I/A route because the Westinghouse solution was to retain the
existing 15 year old I/O which would have put us into a bind in the
near future.  If any I/O needs to added in the future you can either
buy more migration cards if rack space is available or you can add a
new enclosure with standard I/O modules.  The standard I/O modules are
cheaper and it makes more sense to go that route if you are adding a
significant amaount of I/O.  Both the migration I/O and the standard
I/O co-exist on the same network and they are the same as far as the
system is considered.  We chose the side by side route for the first
migration because the TDC/Modicon installation was a mess and the I/O
was located in the control room and we wanted to distribute it in the
field.  The migration solution was chosen for the second project
because the WDPF installation was pretty clean and we would have never
been able to justify the capital expense of a complete replacement of
the field wiring.  Both routes have pluses and minuses.  I don't work
for Foxboro if that is what you are wondering.  I can say that they are
the most customer service oriented control system vendor I have worked
with in the past 18 years.


Re: honeywell tdc3000


Cameron,

I have to agree with Eric for three reasons; I like to work with Foxboro
gear and software, there is a hidden cost to all control systems -
documentation and time to make the changes. Most control systems are
self-documenting to some degree but I am still looking for a field
wiring system that is.

Speaking from personal experience, we have some control gear that is
very quickly approaching extinction and there isn't much I can do about
it because we lose so much revenue shut down. We have three different
kinds of outage; a 5 day annual outage, a 10 day outage every so often
and a 30 day outage every 4 or 5 years. We count the days from breaker
open to breaker closed, those days will include plant shutdown and plant
startup. That is the most I will ever get. So I would rather not change
my field wiring (why should I?) and live with better software and
operator interfaces.

Of course, I have also worked on complete upgrades in a previous life.
All of them were machines or materials handling lines where we had the
luxury of weekends where we could swing bits from one system to another.

Steve


cdorrough@nortonconsultants.com says...
Quoted text here. Click to load it

Re: honeywell tdc3000


Quoted text here. Click to load it

That's two reasons, and have never worked with the Foxboro gear so I can't
comment on the first one.  I agree that most customers don't take change
documentation and time into account - they just want it done, and done
now! - but again I can't see how that makes a partial conversion less
painful in the long run.

Quoted text here. Click to load it

The systems we tend to work on (airport refuelling, power generation and the
like) often cannot be shut down at all - changeovers must be done live with
proper training and procedures in place.  Breaker open to close must be
minutes not days... all the more reason to have a complete working system
right next to you that you can fall back to very quickly.

P'raps I got it wrong, but I took Eric's "field wiring" to mean connections
from the signal conditioning nests to the field and not the field wiring
itself, per se.  The better systems out there (Yokogawa, etc.) all allow you
to re-use the old nests and terminal blocks and literally unplug the old I/O
and plug in the new.

Quoted text here. Click to load it

If Foxboro have a _full_ range of I/O in "migration package" format to suit
Westinghouse racks - that's great and if so, they would be one of the only
ones.  Manufacturing I/O cards to fit different manuafcturer's racks is
extremely expensive and not very common in my experience.  More common is to
replace the old processor with a "Remote I/O Migration Module" allowing you
to use an entire I/O rack as 'Remote I/O", connected to the new node in the
cabinet next door using some form of high-speed comms.

With this sort of system, although it's great for testing and you can get
your new platform up an going really fast, the truth is that once a system
is "migrated", the old bits remaining are forgotten, just waiting for the
next I/O card to fail...

Cameron:-)



Re: honeywell tdc3000


wrote:

Quoted text here. Click to load it

Have you considered Honeywell's New Experion platform for your
migration? They offer large discounts on hardware costs for customers
who already have an installed legacy system like the TDC3000. I
haven't had any experience with ABB or Yokogawa but I have with
Rockwell's PLC5's and Controllogix and I'll take the robustness and
reliability of Honeywell any day over Rockwell.

Re: honeywell tdc3000


Quoted text here. Click to load it

Gee, it's a bit rough comparing a Honeywell DCS with a Rockwell PLC.  That's
a bit like comparing a Mack truck with a Morris Minor. :-)

BTW:  There's absolutely nothing wrong with either the ABB or the Yokogawa
product..

Cameron:-)



Re: honeywell tdc3000


    The Honeywell Experian system is a AB plc with a server connected to it
and a WEB browser connect to the server.  If you want IT to do process
automation by sending the work to India then Experian is the system you
want.  This is from first hand experience.

    I suggest you check out the new Allen-Bradley systems.  They can do
everything a DCS does for less than half the price, and there are many
independent integrator close by.



Quoted text here. Click to load it



Re: honeywell tdc3000


Quoted text here. Click to load it

If you look closely, I think you'll find that the CPU is *not* made by AB.
Honeywell only use the ControlLogix backplane, power supply and I/O 'cause
it's cheaper than making their own.

..and AB systems cannot do even half of what an average DCS can do.  For
starters, they're not even in the same market.

Cameron:-)



Re: honeywell tdc3000


I think you have it wrong.  The experian system cannot do want a PLC can do.
For one thing it cannot communicate with other systems. I know one place it
was installed and to get an OEM's PLC to communicate with it required hard
wire inputs and outputs to be wired from the PLC to the DCS.


Also, as far as cost, the AB I/O etc. is more expensive than the Honeywell.
There are several places where the experian system was installed and
Honeywell I/O was used because of cost.

In most processes you want to control temperature, pressure, etc and log
data.  The PLC systems can do all of this.  The DCS is great for large
integrate oil refineries especially when they spend the money for
optimization routines, but most application a PLC that is compliant with the
IEC 1131 programs can handle most applications



Quoted text here. Click to load it



Re: honeywell tdc3000


I got my information from Honeywell support.  I can even tell you who we
talked to.



That is because you did not know what you were doing. The Honeywell
Experion system can talk to just about any controller that was made to
talk to other systems.





Quoted text here. Click to load it



Re: honeywell tdc3000


Quoted text here. Click to load it
sits in the Rockwell chassis) can talk "peer to peer" to PLC's using
any of the following protocols, which covers all the cases I have come
across so far...
- Modbus RTU using the SIM module (Serial Interface Module) which
covers lots of PLCs.
- Allen Bradley DH+ using the SIM module
- Allen-Bradley PCCC or CIP via Ethernet or ControlNet to PLC5/
ControlLogix/etc.
- Profibus DP
- DeviceNet
- hardwired I/O

And there are a few neat things that I like about the Experion
Controllers which I have not seen done well (or in some cases at all)
in PLC's yet, such as:
- Viewing the logic charts with live data in the operator stations
without any additional configuration, just call up the tag detail in
the station.
- Truly only a single database for tags.  Build the logic and it is
available without any import, translation or anything, just use the
tag.
- Model Predictive Control in the Controller, which is a great
improvement over PID for controlling systems with transport delays.
- On-process migration for firmware and software upgrades so there is
no downtime for control of the process.
- Seamless controller redundancy which requires only configuration of
a couple of modules and no code.
- Advanced continuous control function blocks which automatically
support cascading loops, back initialisation, mode handling, safety
interlocks, etc.

There are of course some tasks which will be more suited to a PLC ,
like lots of fast digital I/O or fast sequencing, high speed motion
control, etc.
The top end of Experion can talk to PLCs from many vendors, and then
you can mix PLC's and C200's in the same system using each when they
make sense, and providing all the data on a common HMI.

Stew.

Quoted text here. Click to load it



Re: honeywell tdc3000


Quoted text here. Click to load it

Essentially what this means is you can link the Honeywell C200 platform to
Rockwell ControlLogix PLCs (in parts of the the plant that need fast digital
I/O processing) getting the best of both DCS and PLC functionality and at
the same time reducing the spares count.

A win-win situation for large mixed-use plants (steel milling, etc.) and
definitely the way of the future for all modern control systems.

Cameron:-)



Re: honeywell tdc3000
replying to marcos_rhco, Innovativeman wrote:
Quoted text here. Click to load it


I'm questioning your rationale on what you would like to change to [ABB AC800 or
Yokogawa CS3000].
It may be worth considering upgrading to Honeywell Experion - There would more
support from Honeywell.

The best resale would be a trade-in with Honeywell. There are re-sellers of PLC
and DCS used/surplus equipment -but
I don't think they would give you a better deal than Honeywell's trade-in.