Subject
- Posted on
Level Instrument for Interface measurement
- 07-04-2006
July 4, 2006, 2:04 pm
Hi all,
Can anyone give some idea to solve the below issue.
We are interested in measuring the Interface level in a closed vessel.
We got the idea of using the Radar level instrument for the same.
Having the Radar level instrument directly on the tank would solve th
issue. But the problem is that the vessel is highly pressurised and the
maintenance of the Radar level instrument would be a problem. So the
next step is go for an external chamber. In an external chamber how
the level of the two liquid levels can be maintained at the same height
of the vessel? How many nozzles are required in the vessel?
Expecting your replies....
S.Ramesh
Re: Level Instrument for Interface measurement
Ramesh,
Are the SG of two liquids significantly different? If the answer is YES,
then may be a radiation level detector is the answer. Speak to either your
local RONAN or OHMART or THERMO ELECTRON application representative to see
if they have used the radiation detector in a similar application.
Regards,
Raj
Re: Level Instrument for Interface measurement
If you have the money, an Enraf 854 servo-level gauge wuld be ideal for this
application. There is a high pressure version available and you simply
choose a displacer to suit.
If you only really need point level detection, try Drexelbrook's "The Point"
admittance level probe:
http://www.drexelbrook.com/products/SKU.cfm?Product_Id28&SKU_IDQ2
You haven't said exactly what it is you are measuring, but if it builds up
on tank surfaces, the Drexelbrook system would be better than the Enraf
displacer.
Cameron:-)
Re: Level Instrument for Interface measurement
In the old days we Instrument Engineers would probably have specified a
classical
displacer-type interface level transmitter. No doubt nowadays its essential to
use some highly
complex and fancy electronic sensing device!
Kelvin B. Hales
Kelvin Hales Associates Limited
Consulting Process Control Engineers
Web: www.khace.com
Site Timeline
- » Replacement to Advantech PCI 1762?
- — Next thread in » Industrial Control Group
-

- » Suitable instrument to protect overfilling Ammonium Nitrate solution road tanker
- — Previous thread in » Industrial Control Group
-

- » Measurement validation for process signals
- — Newest thread in » Industrial Control Group
-

- » What is it? Set 442
- — The site's Newest Thread. Posted in » General Metalworking
-