Hi to all
I was told by SIEMENS that the analog input module doesn't have this
facility. It needs to be done by the application software.
Isn't that strange?
They told me the thermocouple modules DO detect open circuit...
Thanks in advance !
Eduardo.
Re: S7-200 auto detects broken 4-20 mA current loop ?
Which particular Siemens card are you talking about ?
Broken Sensor Protection on thermocouple circuits has long since been a
feature of most systems, presumably because of their tendancy to fail
and the need to create an alarm or trip. It is normally done via a
separate monitoring signal that causes the signal to go hard to top or
bottom of the scale depending on the application.
Steve
www.mtl-inst.com
ebriosso@gmail.com wrote:
Re: S7-200 auto detects broken 4-20 mA current loop ?
Not necessarily, 0mA could imply open circuit cabling, 25mA could mean a
short circuit.
Also some intelligent transmitters can be configured to fix the output
current at specific current levels corresponding to detected faults, ie
a broken thermocouple in the case of a temperature transmitter. The
system is then programmed to display specific error messages.
Steve
www.mtl-inst.com
Re: S7-200 auto detects broken 4-20 mA current loop ?
Yes, The statement 'the sensor is broken' is a bit of a generalisation from
the sensors POV
'the sensor loop is broken' is better...I meant to imply that 0 and +24mA
are common and easily detectable fault conditions in an analogue loop...for
which the cabling is the most likely culprit
Now that would be handy
Site Timeline
- » Greenhelm Engineering Opportunities
- — Next thread in » Industrial Control Group
-

- » Stepmotor vs brushless DC servo
- — Previous thread in » Industrial Control Group
-

- » Measurement validation for process signals
- — Newest thread in » Industrial Control Group
-

- » What is it? Set 442
- — The site's Newest Thread. Posted in » General Metalworking
-