tuning formula for PT1 control path
- 01-12-2007
January 12, 2007, 9:47 am
I have a control path with PT1 behavior. However all the formulas for
controller tuning (Ziegler-Nichols, Chien-Hrones-Reswick) assume the
approximation for a deadtime of the system.
When setting Tu:=0 some constants become infinite with the existing rules.
Can anybody guide me to some tuning formulas that work for a PT1 path
(given K and T)?
pb
Re: tuning formula for PT1 control path
Peter Bencsik wrote:
PT1?
You left out Astrom-Hagglund tuning, which is a variant of
Ziegler-Nichols that's supposed to give better damping.
--
Tim Wescott
Wescott Design Services
http://www.wescottdesign.com
Posting from Google? See http://cfaj.freeshell.org/google/
"Applied Control Theory for Embedded Systems" came out in April.
See details at http://www.wescottdesign.com/actfes/actfes.html
Re: tuning formula for PT1 control path
Peter Bencsik wrote:
So what it Tu? That can't be right. Something is wrong.
That confused me too. I wish people would define their symbols and not
assume we all use the same ones.
That is strange normally it is the other way around. You need better
books.
Look at www.controlguru.com. There are FOPDT gain calculation formulas
there that will work when the dead time is 0.
BTW, it is easy to derive Kc and Ti in terms of Kp, Tp and Tc using
direct synthesis or pole placement. If that isn't in your books then
you do need new books.
Peter Nachtwey
Almost forgot
Kp = plant gain
Tp = plant time constant
Tc = closed loop time constant
Kc = controller gain
Ti = integrator time constant
Site Timeline
- » Competition
- — Next thread in » Industrial Control Group
-

- » Parameter Scheduling & Adaptive Control of Nonlinear Processes
- — Previous thread in » Industrial Control Group
-

- » Measurement validation for process signals
- — Newest thread in » Industrial Control Group
-

- » Re: shop press
- — The site's Newest Thread. Posted in » General Metalworking
-