What would the voltage reading be when measuring between the hot and neutral on a 115 volt motor when the rotor is locked? - Should there be a drop because I'm reading the difference between the voltage going in on the hot and the voltage returning on the neutral? Or should it maintain close to 120? Background below.
My Dad has a problem with a motor not starting under load (grain handling system). It has been fine for several years, but now won't. We replaced the start cap, checked the centrifugal switch and checked the voltage on various parts of the circuit. This is a 1.5 hp motor on the end of about
75' of 12 gauge wire, hooked on a 15 amp breaker on a panel located about 200 yards from the pole. The 200 yards is wired with 3 heavy insulated aluminum cables roughly 1/2 inch each (the wire not including the insulation). 2 hots, and ground, with the ground tied also at the breaker box and several other locations around the farm. I checked and retorqued all conections in the system. When checking the voltage, it was 240 volts at the panel and 120 everywhere it should be. When the motor is plugged in, the voltage at the motor drops to 87 between the hot and neutral. At the panel, it is 100 volts, and 230 between the two hots on the panel. Same readings when the motor is plugged in to the other hot side of the panel. All these are with the rotor locked. Motor starts fine in the shop with a smaller load.Thanks,
Wayne Sippola Avid lurker