Leeson 3 phase motor wiring

I've got a spare 3 phase Leeson 1-1/2 hp motor I need to test out and use on a temporary project. Of course the wiring diagram is missing. It has 6 leads numbered 1 through 5 and a #8. I know what to do with 9 wire units, this one is very likely a single voltage unit, 208/230 volt. What is the most likely wiring configuration? I can guess but I usually need to replace a fuse or two before I get it right.

Reply to
RoyJ
Loading thread data ...

Roy,

Are you sure you don't mean 6 leads numbered 1through 6 and a #8 lead which is ground ?

If this is so then std. hookup should be: line 1 to (1 and 2) together; phase 2 to (2 and 4) together; phase 3 to (3 and 5) together.

Diagrams found at:

formatting link

Bob Swinney

Reply to
Robert Swinney

Thanks for the link. The Leeson site was much less helpful.

I think you meant "line 1 to (1 and 6) together" but that still doesn't seem right on this motor. I won't have a chance to look at it some more until tomorrow. Think I'll get the sensitive ohm meter out and check things more closely.

I need to make some sort of switch or starter relay. I just hate plugging 3 phase twist locks in under load. :)

More later.

Robert Sw> Roy,

2 to (2 and 4)

formatting link

Reply to
RoyJ

Take a look at

formatting link
Scroll down to "Electrical - Phase Converter Information" then to "Induction Motors and Phase Converters". There you will find some examples of start and run circuits that will be much safer than plugging twist locks in under load.

Bob Swinney

I think you meant "line 1 to (1 and 6) together" but that still doesn't seem right on this motor. I won't have a chance to look at it some more until tomorrow. Think I'll get the sensitive ohm meter out and check things more closely.

I need to make some sort of switch or starter relay. I just hate plugging 3 phase twist locks in under load. :)

More later.

Robert Sw> Roy,

2 to (2 and 4)

formatting link

Reply to
Robert Swinney

I wasn't seriously thinking about just plugging it in! This project is slated to have a VFD after I find a suitable motor so this is just temporary hookup for speed and power draw tests. I'll have to dig in the projects box for a 3 pole relay. I know I have a multipole toggle switch with suitable ratings but I'm not comfortable with doing testing with it. Fingers get too close to the source of the magic smoke.

I picked up several boxes of various relay's, c> Take a look at

formatting link
Scroll down to "Electrical - Phase

Converter Information"

examples of start and

is ground ?

phase 2 to (2 and 4)

formatting link

Reply to
RoyJ

An update.

I got a chance to look at it more carefully. 1 to 2 reads 1.1 ohm. 3 to

4 reads 1.1 ohm. 5 and 8 read noth> I wasn't seriously thinking about just plugging it in! This project is
Reply to
RoyJ

What does 4:1 read ? is it a delta or a wye and are 5 and 8 center taps or taps on two windings ? - e.g. 7 reads xx to 1...

Martin

Mart> An update.

Reply to
Martin H. Eastburn

Any one want to do an "I should have told you so"????

I was told the offending motor was a 3 phase unit. I needed a 3 phase for the project, I BELIEVED the motor was a 3 phase. So I conveniently ignored the cap in the bump on the case. And I even ignored the starting switch to the cap when I tore it apart.

Turned out to be a dual voltage, cap start, 208/240v, s> An update.

Reply to
RoyJ