Help me guys figure out chain of events
Approx two weeks ago the power went off and tripped the 100 amp /30 milliamp RCD ..
By turning off various circuits I put it down to the hot water heater .
So I just turned this circuit off via trip and isolated water heater with its double pole switch ..
4 days later ..........phase converter began to trip RCDDisconnected the sockets out of the converter .........
And gave it a try again ... one time in five it would start and run all day ..and start the machines .
So I investigated further Today .first disconnected all wiring to it ..took it down off its shelf...........took the top off the phase converter for the first time ever. ..and this is what I found
Picture one .....top removed showing layout ..and arrow points to the fault area.
My theory says that the wires leading out of this terminal block were never tight enough and arced and melted it ...
Now even when I turn the compressor on the RCD trips ........
Do you think my RCD has buggered up by the fault above ......and there isn't anything wrong with my water heater of compressor .
Should I fix the converter By substituting terminal block and get a new RCD.
I will be onto the makers on Tuesday .before I proceed
all the best..mark