industrial signalling and noise immunity

I deal with alot of industrial 4-20mA. the cabling from tranducer/ transmitter to output is is always twisted pair, shield c/w a drain wire.

  1. twisted pair is so induced current signals (from magnetic fields) cancel, correct?
  2. shielding (foil etc), acts a faraday cage to the wiring within essentially 'shielding' the charges in the signal wire copper from outside e-fields influence, correct?
  3. what is the drain wire for?
  4. would there be negative outcome with using an overall shielded triad cable c/w drain wire, isolating one wire, in the stead of the twisted pair (ie if the contractor accidently pulled triad and not twisted pair)?
Reply to
jack007
Loading thread data ...

Sorry for 1) i should say it is differential and cancels

Reply to
jack007

The signal is differential, the noise is common mode and cancels.

Using a twisted pair (fed with a balanced circuit) improves noise reduction compared to non-twisted pair due to greater common mode rejection.

If the contractor "accidentally" pulled non-twisted when twisted was specified, the contractor should be required to correct the problem by pulling twisted pair. If that is not what was specified, consider a new contract to get the job done correctly. There is no substitute.