Motor start capacitors?

If you have a short, then wouldn't the inverter shutdown? The 60A or 70A main is there to protect downstream wiring and devices from overcurrent, not the power supply.

You seem to be saying you want a bigger inverter, capable of supplying a higher fault current because you want to trip the main breaker. Why not just have the correct size breaker on the inverter output? I suspect the manufacturer already has that in their unit. Just because the main breaker in your panel might not always trip before the inverter output, doesn't mean you have less protection.

daestrom

Reply to
daestrom
Loading thread data ...

| If you have a short, then wouldn't the inverter shutdown? The 60A or 70A | main is there to protect downstream wiring and devices from overcurrent, not | the power supply.

And that's what I want it to protect.

| You seem to be saying you want a bigger inverter, capable of supplying a | higher fault current because you want to trip the main breaker. Why not | just have the correct size breaker on the inverter output? I suspect the | manufacturer already has that in their unit. Just because the main breaker | in your panel might not always trip before the inverter output, doesn't mean | you have less protection.

The main breaker is the example of what the inverter cannot deliver. The problem exists even for small branch breakers. Even a 20A breaker needs

100A fault current instantly to do a magnetic trip.

My whole point is the "short term" current delivery capability of inverters on the market is terrible. It needs to be similar to that of a transformer rated for your needs with infinite availability on the primary, at least of about a 10% equivalent impedance. These inverters are apparently non-linear. I don't want an inverter that's going to shutdown when I start the garbage disposal motor.

Reply to
phil-news-nospam

So, if the various breakers are designed to protect the downstream components adequately, and the inverter is not capable of sending enough current to trip the breaker, the inverter is not capable of sending enough current to damage the downstream components. QED.

If the inverter *is* capable of sending enough current to trip the breaker on thermal trip (even if not the magnetic trip), then the thermal trip on the breaker is able to protect the downstream components as it is designed and you still don't have a problem.

About the only thing that can be damaged by a mid-level fault that passes more current than the inverter can supply, but not enough to trip the breaker is the inverter. The downstream equipment is safe because it can handle anything the breaker can pass, so since the breaker passes it, it's safe.

daestrom

Reply to
daestrom

|> | If you have a short, then wouldn't the inverter shutdown? The 60A or |> 70A |> | main is there to protect downstream wiring and devices from overcurrent, |> not |> | the power supply. |>

|> And that's what I want it to protect. |>

|>

|> | You seem to be saying you want a bigger inverter, capable of supplying a |> | higher fault current because you want to trip the main breaker. Why not |> | just have the correct size breaker on the inverter output? I suspect |> the |> | manufacturer already has that in their unit. Just because the main |> breaker |> | in your panel might not always trip before the inverter output, doesn't |> mean |> | you have less protection. |>

|> The main breaker is the example of what the inverter cannot deliver. The |> problem exists even for small branch breakers. Even a 20A breaker needs |> 100A fault current instantly to do a magnetic trip. |>

| | So, if the various breakers are designed to protect the downstream | components adequately, and the inverter is not capable of sending enough | current to trip the breaker, the inverter is not capable of sending enough | current to damage the downstream components. QED. | | If the inverter *is* capable of sending enough current to trip the breaker | on thermal trip (even if not the magnetic trip), then the thermal trip on | the breaker is able to protect the downstream components as it is designed | and you still don't have a problem. | | About the only thing that can be damaged by a mid-level fault that passes | more current than the inverter can supply, but not enough to trip the | breaker is the inverter. The downstream equipment is safe because it can | handle anything the breaker can pass, so since the breaker passes it, it's | safe.

So you think a short circuit should just sit there and not be opened.

Imagine the scenario of some child pulling a plug out half way and putting some metal object in between the prongs.

Reply to
phil-news-nospam

Been there actually done that. As a small boy, I 'discovered' that you can take metal staples from my father's desk and they fit just nicely in a wall outlet. Lot's of sparks, a burnt finger, and a scared dog. No blown fuse, no fire, not much else.

Placing a fault of your type across the outlet will either a) pass enough current to trip the breaker (if the inverter can supply enough for that individual branch circuit), b) pass enough current to cause the inverter to shutdown, or c) pass just enough current to get really hot but not trip the breaker or shutdown the inverter.

A) is not a problem, obviously the breaker tripping will stop the event B) is not a problem either C) may seem like a problem, but it is exactly the same problem if you use utility supply. Think about it. You're passing something like 19 amps through the 'fault' for a long time. Bad?? Yes. Related to the inverter supply?? No.

daestrom

Reply to
daestrom

[snip]

If the inverter (or the utility) can supply such a fault for an extended time, it may result in a fire. You are dissipating 2.3kW someplace where it isn't designed to be dissipated.

Reply to
Paul Hovnanian P.E.

|> So you think a short circuit should just sit there and not be opened. |>

|> Imagine the scenario of some child pulling a plug out half way and |> putting some metal object in between the prongs. |>

| | Been there actually done that. As a small boy, I 'discovered' that you can | take metal staples from my father's desk and they fit just nicely in a wall | outlet. Lot's of sparks, a burnt finger, and a scared dog. No blown fuse, | no fire, not much else. | | Placing a fault of your type across the outlet will either a) pass enough | current to trip the breaker (if the inverter can supply enough for that | individual branch circuit), b) pass enough current to cause the inverter to | shutdown, or c) pass just enough current to get really hot but not trip the | breaker or shutdown the inverter. | | A) is not a problem, obviously the breaker tripping will stop the event | B) is not a problem either | C) may seem like a problem, but it is exactly the same problem if you use | utility supply. Think about it. You're passing something like 19 amps | through the 'fault' for a long time. Bad?? Yes. Related to the inverter | supply?? No.

If it is short that would draw enough current on mains supply to trip the breaker, I want it to trip the breaker even with an inverter. Marginal cases may not be that important.

Arc fault breakers might fill in a lot of the problem cases.

Reply to
phil-news-nospam

You just don't get it...

Either the inverter will shut down, or the breaker will trip, in either event you're safe. I can't think of any reason why you'd want the inverter to be able to supply more current, for the sole purpose of tripping the breaker, that's stupid.

Either way, you're in *WAY* over your head, there's a good reason big inverters are expensive, they're very difficult to design properly.

Reply to
James Sweet

On Thu, 22 May 2008 06:06:42 GMT James Sweet wrote: | | |> |> If it is short that would draw enough current on mains supply to trip the |> breaker, I want it to trip the breaker even with an inverter. Marginal |> cases may not be that important. |> |> Arc fault breakers might fill in a lot of the problem cases. |> | | | You just don't get it... | | Either the inverter will shut down, or the breaker will trip, in either | event you're safe. I can't think of any reason why you'd want the | inverter to be able to supply more current, for the sole purpose of | tripping the breaker, that's stupid.

I can think of a reason. Just because you can't think of one doesn't mean you have a case to say there are none.

| Either way, you're in *WAY* over your head, there's a good reason big | inverters are expensive, they're very difficult to design properly.

Define "properly". Maybe "properly" means having sufficient fault current? More likely they are expensive because they are larger.

Reply to
phil-news-nospam

What is it then?

Properly as in it works as designed, isn't a safety hazard, doesn't emit RF radiation that interferes with other devices, and is reliable. I generally trust my design and construction abilities, but I would not wire up something I built to the service entry like that, it's too risky, it would not be certified, would not meet code, and if the house has an electrical fire, the insurance would not cover it. They are expensive because they are large, complex, carefully designed pieces of equipment full of expensive parts which have gone through safety certifications.

If you want to ignore everyone's advice and go ahead, then by all means go for it, but the risk is yours, and you will likely blow up enough spendy IGBTs in the process to offset any cost savings.

Reply to
James Sweet

| Properly as in it works as designed, isn't a safety hazard, doesn't emit | RF radiation that interferes with other devices, and is reliable. I | generally trust my design and construction abilities, but I would not | wire up something I built to the service entry like that, it's too | risky, it would not be certified, would not meet code, and if the house | has an electrical fire, the insurance would not cover it. They are | expensive because they are large, complex, carefully designed pieces of | equipment full of expensive parts which have gone through safety | certifications.

So then explain why it is the smaller sized ones are not so expensive. A 100 kVA inverter should cost 5 times as much as a 20 kVA inverter, if things were consistent. Instead, it's more like 30 times as much. Or are you saying the smaller ones don't meet code?

Reply to
phil-news-nospam

Actually, the wattage could be *less* with an inverter if it's output voltage drops.

Yes, it could result in a fire, but that depends entirely on *what* is dissipating the heat. It won't be the wiring, though if the circuit breaker is sized properly.

daestrom

Reply to
daestrom

Why should it? Much of it is economies of scale. The smaller inverters are made in much higher quantities than specialized larger ones, so the cost is far lower. They're also simpler, use lower power, less expensive components. You can't just take a $30 travel inverter and make it 100 times larger, it doesn't work that way. If you don't agree, don't argue, just build something that works, and then report back how easy it was and how much money you saved. Anything else is just trolling.

As for meeting code, a commercially built unit will have been tested by the appropriate regulating bodies for the region and will meet code if installed in the intended manner. One you build yourself that has not been tested will not meet code, the size is irrelevant.

Reply to
James Sweet

How are centrifugal switches implemented? Descriptions of one or two of the most common ways would be appreciated. I can see that one way would be to have some kind pin moving radially from centrifugal force acting against a against a spring. The pin can then trip a lever operated stationary switch so that the lever moves out of the pin's way after getting tripped.

I have Googled and Wickied, but all I have found so far are haystacks.

Bill

Reply to
Salmon Egg

The ones I've seen have a couple of hinged weights fly outward and cams push back a simple thrust bearing on the shaft, pushing open a contact. You might just pick up and old motor and pull the end bell off for a look, a picture is worth a thousand words.

Reply to
James Sweet

| Why should it? Much of it is economies of scale. The smaller inverters | are made in much higher quantities than specialized larger ones, so the | cost is far lower. They're also simpler, use lower power, less expensive | components. You can't just take a $30 travel inverter and make it 100 | times larger, it doesn't work that way. If you don't agree, don't argue, | just build something that works, and then report back how easy it was | and how much money you saved. Anything else is just trolling.

Aren't you the one that says not to build one?

I don't necessarily say I will save money building my own. But at least I will know it will have the ability to do what I want without having extra stuff in it I don't need.

| As for meeting code, a commercially built unit will have been tested by | the appropriate regulating bodies for the region and will meet code if | installed in the intended manner. One you build yourself that has not | been tested will not meet code, the size is irrelevant.

If they don't make what I need, there is no other choice.

Reply to
phil-news-nospam