I recently worked on an electrical system at a fairly large hospital. There were two 2 (approx) megawatt transformers in parallel supplying power at
13.8 kv on the primary. Each transformer had the 480 volt side XO solidly grounded with a copper main bonding jumper. There was approximately 35 amperes flowing through each bonding jumper as measured using a CTs. I called the engineer and he said it had been that way for years and to not worry about it. Has anyone heard of this high of charging current?- posted