| I was doing some reading on gfci's and they referred to a neutral to ground | short upstream of the gfci would trip it. | | aren't the neutral and ground buss connected and wouldn't this be seen as a | short ? | | also are there any known devices or configurations that trip gfci's even | when they are functioning properly ?
There can be confusion as to which is "up" and which is "down". To avoid that risk, I'll use different terms.
Ground an neutral are bonded together at the service entrance. From there power goes through a branch breaker and eventually to a GFCI receptacle and is connected to the "line" side. The receptacle outlets, as well as the screws labeled "load" on the other side, are thus protected.
The GFCI device looks for a current leakage by some means, usually with a small current transformer with both the hot and neutral wires running in parallel through the single CT. As long as all the current going out one wire comes back through the other, they cancel and the CT sense zero net current and all is well. As soon as the neutral is connected to the ground wire at the load, then the current that would normally just flow on the neutral alone can now also flow on the ground wire. And some of it actually will flow on the ground wire. However much does flow on the ground wire, it is that much which does not flow on the neutral, and does not cancel out the hot wire current, which leaves the CT with a net current. When that current is equal to or higher than some value between 2 milliamps and 6 milliamps, the GFCI is supposed to open the circuit and prevent the current flowing.
If neutral and ground are connected together on the load side but there is no load, the GFCI may, or may not, trip open as a result. If other circuits are sufficiently out of balance between the two opposite hot wires in the split single phase system, then that voltage on the neutral can go out to the load and back over the ground (parallaling it's already low resistance path back to the transformer neutral connection). It can be enough to trip the GFCI. But if things are in balance, there may be zero voltage on the neutral and it won't see anything to trip on.
Connections between neutral and ground that are on the line side of the GFCI won't be detected since they won't result in any current through the CT of the GFCI.
GFCI devices in portable cords and extension devices also include things to detect damage that such cords could have happen such as an open ground. I've not seen how this is done, but I would suspect that a high resistance is connected to the hot wire and to the ground wire through a current transformer or other sensor. The a circuit detects if the current is flowing and if there is also voltage present. If voltage is present and that tiny current is NOT flowing, then it opens the circuit. This is a bit more tricky because you have to make sure that plugging or unplugging the cord does not false trip the circuit by having voltage detected before the test current is detected. So there might be a time delay in there. This kind of test for ground wire continuity is needed because otherwise damage to the ground wire would not prevent load operation, though without the protection the ground wire provides. Cascading two such cords could be tricky if the test current on one can trip the GFCI of the other. So I would think they would have to have test currents well below the 2 ma level. But that could also make it more susceptable to problems like RF energy.
Battery operated power tools are obviously safer, but not all tools can be practically run on batteries.