On Fri, 03 Jun 2005 19:42:50 GMT HorneTD wrote: | snipped-for-privacy@ipal.net wrote: |> On Fri, 03 Jun 2005 17:21:11 GMT HorneTD wrote: |> | snipped-for-privacy@ipal.net wrote: |> |> On Fri, 03 Jun 2005 02:58:31 GMT HorneTD wrote: |> |> |> |> | Mount a four hole lug of appropriate size on an insulating stand off, |> |> | bug the three conductors onto a short pigtail off of the breaker using |> |> | spit bolts or insulating displacing connectors as appropriate, use an |> |> | insulated multi tap block to join the four conductors to the jumper from |> |> | the breaker... There is always a code compliant way to do it. You just |> |> | have to invest the time or the money in hired expertise to find out what |> |> | that way is. |> |> |> |> If I would approve of things like pigtails and splices, I'd just run some |> |> 600 kcmil from the main breaker down a raceway and splice off each of the |> |> 4/0 feeds into the 3 panels they go to. But my intention is to absolutely |> |> avoid splicing (having seen the mess when they fail). I believe the risk |> |> is less by just stranding the 4/0 into 2 adjacent holes on the same lug. |> |> Or can you show me code that says not to split stranded wire into two holes? |> |> I'm not convinced about the "fracturing" issue since this will involve less |> |> mechanical stress on the wire than typical wire bending that takes place in |> |> typical panels, especially if I use the larger box that would be needed to |> |> put all those pigtails below the breaker. |> |> |> | |> | 110.3 Examination, Identification, Installation, and Use of Equipment. |> | (B) Installation and Use. Listed or labeled equipment shall be installed |> | and used in accordance with any instructions included in the listing or |> | labeling. |> |> So basically, you can't figure out a better way to do it. |> |> At this point I will now ignore all followups that do not have a constructive |> solution not involving splices, pigtails, or other unsecured connections. |> | | Undoubtedly because they are code compliant and your method is not. | Would you mine explaining how an insulated terminal block is an | unsecured connection?
Your description of why not to mix current carrying conductors in the same hole ...
On Wed, 01 Jun 2005 20:04:08 GMT HorneTD wrote:
| It is the thermal cycling of the current carrying grounded conductor | (neutral) that makes having it in the same termination as the Equipment | Grounding (bonding) Conductor (EGC) an unsafe practice electrically. | There has yet to be devised a terminal that can use one pressure | producing part to maintain good electrical contact with two conductors | that are thermally cycling at different rates and times. If you look at | the breakers that are listed to hold two separate conductors you will | see that the conductors are separate from each other and the screw has a | pressure washer under its head. The addition of the pressure washer or | plate allows solid contact between both conductors and the plate into | which the screw is threaded. The pressure washer will flex sufficiently | to permit unequal thermal cycling without the connection failing. | | In thirty years of electric work I have seen many connection failures | caused by improper torquing of connections and by using a single | terminal to terminate multiple conductors. The reason that it is safe | to use a single terminal to terminate multiple EGCs is that they do not | carry current during normal operation and they are not subjected to | repeated thermal cycling.
... would just as readily apply to phase conductors as well as the neutral. If you have 2 or more different loads (hence different thermal cycling characteristics) fed by different conductors in the same hole, the same problem will occur. A pigtail is thus like that. Maybe this is why pigtails have failed. Your earlier post further reinforces my intent to avoid all pigtails with 3 or more conductors (those with 2 will be avoided as well, but your post doesn't really reinforce my intent against those).
But I hardly would consider putting a 600 kcmil and 3x 4/0 together on the same pigtail. Maybe cad-welded ... maybe.
As for a terminal block, how is it any different than a lug on a circuit breaker, other than taking up even more space. How is it that a terminal lug would be safe enough to be listed as a terminal block and not as part of a circuit breaker?
A friend of mine is a metal machinist. Perhaps I'll just have the exact lug needed manufactured for me.
BTW, did you know that a common practice when 2 more more panels are needed in parallel is to put 2 wires in the lugs, one coming from the service entrance metal, and the other going to the 2nd panel? What I wonder is if you would cringe at that? I would. Yet it is common, and has the same issue you explained before. But I will be avoiding such a thing.