Not quite, 4-pole, *single* shaft 'nukees'. One HP and three LP mounted all in-line with the generator. Some of that 40MW (seen it on the oscillograph traces) goes into the exciter I'm sure.
Regarding LP blades, you're right they don't 'like it'. GE warns about running with less than 5% load for any length of time and they recommend not breaking vacumn at all unless it's an emergency. Saw a nice video they developed from one plant where they mounted the camera and strobe light in the exhaust hood. After tripping, the last stages 'wave' back and forth something awesome.
In the units I've worked with, that is what the 'backup unit protection' is for. Some times the 'anti-motoring' is a series of limit switches and the backup is reverse power relay. Sometimes it's the other way around. Usually 'backup' protection uses a different method of detecting the problem from primary, whatever it is.
Also seen a series of valve limit switches in the close permissive. Trying to protect from inadvertant energizing.
Guess it depends on how sensitive the 32 is set at. Can't imagine how long you have to motor to get a high exhaust hood temp. On the 4-pole units I work with, that would be a lot longer than the 32 relay.
Why operators afraid of setting off the 32? I've seen some plants that basically depend on it when shutting down. Basically they say 'reduce the steam flow and verify the turbine trips when MW goes below zero'. Some bug-a-boo about letting the protective relays activate?
One of the things I've seen plants during outages is 'backfeed'. They open the generator disconnects and bring line power backward into the step-up transformer. Then with 24kV on the low side, they feed the 'hotel loads' of the plant from the normal service transformer. I can't stress to them how disasterous it would be if they missed that one step of 'open the generator disconnects'. But your experience brings it into crystal-clear focus.
IIRC, the steam unit near me installed an electric motor. They get them up to about 3000 (2-pole unit) and then pull them into sync from there. Been awhile though, maybe it was higher RPM.
Well....
50MW for 3 minutes is about 15 teraJoules. If it *ALL* went into the water (none into heating steel, or excitation or other losses), that would heat up about 45 metric tonnes of water to boiling. But you mentioned about 10 MW in generator losses, and certainly the steel runner and casing take a lot of heat to warm up as well, and how much water is in one of those casings.Anyway, seeing is believing (usually:-) and if it doesn't warm up that much, it must be true. Mind you, I wouldn't want to test how long you could go. From what I've seen of hydro-generators, the tolerances are tight on the rotor of the generator (~ 1/8 inch or better). How tight is the fit on the runner?