Resistivity of Romex (NM) cable

I'm interested in calculating some voltage drops for my shack service feed... Does anyone know where I can find a table of resistivities (ohms
per unit length) for various Romex (NM or non-metallic sheathing) wire? Also for THHN? Please include the source for your data if possible so that I may follow up.
Thanks,
Jason
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

that
FYI the VD calculator has the idiot proof code put in as follows:
if (Math.round((((2*materialk*(eval(form.distance.value))*(eval(form.amperes.va lue)))/cmask)*voltsk)*10)/10<=voltage) {
form.voltdrop.value=Math.round((((2*materialk*(eval(form.distance.value))*(e val(form.amperes.value)))/cmask)*voltsk)*10)/10; } else {
form.voltdrop.value=voltage;
Located at http://www.electrician.com/calculators/vd_calculator.htm
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
What about 6 and 8 AWG?

that
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

that
Probably the Number one site on the Internet for Voltage drop is http://www.electrician.com There you find excellent voltage drop calculators and even a voltage drop slide show.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Jason Dugas wrote:

Romex or THHN makes no difference as far as resistivity/voltage drop is concerned. The info you seek is available in any copper wire table, such as:
http://www.physics.montana.edu/edl/documents/edlpages/copperwiretable.htm
14AWG--2.575 ohms/M' 12AWG--1.619 ohms/M' 10AWG--1.018 ohms/M'
Be sure to remember the TOTAL wire length, not a one-way distance when computing voltage drop.
As far as allowable ampacities and derating factors for various types of cable, look in the National Electrical Code.
Bob Weiss N2IXK
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Jason Dugas wrote: |> I'm interested in calculating some voltage drops for my shack service |> feed... Does anyone know where I can find a table of resistivities (ohms |> per unit length) for various Romex (NM or non-metallic sheathing) wire? |> Also for THHN? Please include the source for your data if possible so that |> I may follow up. |> |> Thanks, |> |> Jason |> |> | | Romex or THHN makes no difference as far as resistivity/voltage drop is | concerned. The info you seek is available in any copper wire table, such as: | | http://www.physics.montana.edu/edl/documents/edlpages/copperwiretable.htm | | 14AWG--2.575 ohms/M' | 12AWG--1.619 ohms/M' | 10AWG--1.018 ohms/M'
That seems a little high. The figures I have are:
AWG Dia-mils TPI Dia-mm Circ-mils Ohms/Kft Ft/Ohm
10 101.90 9.8140 2.5881 10383 0.9989 1001.1 11 90.741 11.020 2.3048 8233.9 1.2596 793.93 12 80.807 12.375 2.0525 6529.8 1.5883 629.61 13 71.961 13.896 1.8278 5178.3 2.0028 499.31 14 64.083 15.605 1.6277 4106.6 2.5255 395.97 15 57.067 17.523 1.4495 3256.7 3.1845 314.02 16 50.820 19.677 1.2908 2582.7 4.0156 249.03 17 45.257 22.096 1.1495 2048.2 5.0636 197.49 18 40.302 24.813 1.0237 1624.3 6.3851 156.62
I'm also working on putting together a web page to calculate voltage drop. There is one out there that has been referred to before, but it produces wrong answers (such as large negative voltage drops).
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

(ohms
that
as:
http://www.physics.montana.edu/edl/documents/edlpages/copperwiretable.htm
Try http://www.electrician.com It is my understanding that the advanced voltage drop calculator took over 10 years to write. Yours truly, Gerald Newton
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Try http://www.electrician.com | It is my understanding that the advanced voltage drop calculator took over | 10 years to write.
You mean this one? http://www.electrician.com/vd_calculator.html
That's the one that produces wrong answers!
Let's try it out. Put twenty 60 watt light bulbs (240 ohms for 120 volts each, for a net resistances of 12 ohms) at the end of a one mile run of 18 AWG copper wire. Power it with 120 volts That's a load of 10 amps.
Plug the numbers in:
1. Copper wire 2. 18 AWG 3. 120 volts 1-phase 4. 5280 feet 5. 10 amps
So you gonna believe that you will get -694.8 volts on those poor bulbs?
Maybe that's what is driving those "free electricity" crackpots :-)
I'm working on my own program. When I get it done, I'll post the URL here so you guys can see if I got it right or not.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

over
--
> | Phil Howard KA9WGN | http://linuxhomepage.com /
http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| You may have found an idiot proofing error, but in 99.9 per cent of the | voltage drop problems a user that is familiar with electrical work can use | the program to find practical useful answers. The program is not written | for idiots; it is written for electricians. | hint: electrician.com
I'll believe physicists and engineers before I'll believe an electrician.
| If the answer is negative, then obviously all the volts are dropped in the | conductor. Any 1st year electrician apprentice should know that. But
Really? You think there will be ZERO VOLTS at the load? You really have no concept of physics, do you.
According to my tables, the 5280 foot run of 18 AWG copper wire, at a rating of 6.3851 ohms per 1000 feet, will have 33.713328 ohms for the full 5280 feet, and 67.426656 ohms for the full loop. Adding in the 12 ohms of load makes the total ohmage of 79.426656. So, at 120 volts that's a current of 1.5108278 amps. That puts a voltage difference of 18.1299336 volts across the load, and 101.8700664 volts across the wiring. The total watts in the load is 27.3912077 (divided across the 20 bulbs means each dissipates only 1.36956 watts). The remaining 153.9081283 watts is dissipated in the wires at 0.0145746 watts per foot per conductor.
| more than that, the ampacity of No. 18 is not 10 amperes. Voltage drop | alone does not solve all the problem, the ampacity of a conductor is solved | using different equations and Tables. Additionally, for No. 18 NEC | Section 726.23 requires overcurrent protection no larger than 7 amperes. | Also, the advanced voltage drop calculator finds the approximate temperature | of a conductor and finds the voltage drop for that temperature. Read the | article
Did you mean 725.23?
I suggested looking at table 310.16 under the 90 degree insulation column for copper and note the ampacity for 18 AWG wire there is 14. That's for wiring in raceways or buried, up to 3 conductors. Now have a look at table 310.17 and see what the ampacity for 18 AWG wire in free air is 18.
For the purpose of calculating voltage drop, the ampacity is not really relevant. The temperature would be, but the temperature coefficient does not alter the above values radically.
And finally, with a total resistance of 79.426656 ohms at 120 volts, the current is only 1.5108278 amps, anyway. That's well below virtually every rating for 18 AWG wire. You might not have much light, but the wire is definitely not going to burn up.
| http://www.electrician.com/articles/advanced_voltage_drop_calculator.html | for some enlightenment. | | You appear to be more into electronics and ham radio than electrical work. | Perhaps you should stay away from the electrician page until you serve an | 8,000 hour apprenticeship and an additional 8,000 hours as a Journeyman | electrician and then get your electrical administrators license then you | might be able to use electrical calculators without evaluating them as a | technician.
If electricians use calculators or formulas that result in violations of physics, then I sure as hell don't want to hire them to wire anything of mine. I'll play it safe and wire my own.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I fixed the program so that you don't get a negative voltage. It took four lines and 15 minutes:
if (Math.round((((2*materialk*(eval(form.distance.value))*(eval(form.amperes.va lue)))/cmask)*voltsk)*10)/10<=voltage) {
form.voltdrop.value=Math.round((((2*materialk*(eval(form.distance.value))*(e val(form.amperes.value)))/cmask)*voltsk)*10)/10; } else {
form.voltdrop.value=voltage;
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

four
It is much more elegant now. One more request, for those of us who don't live in Alaska... How about defaulting the ambient to something warmer than -40C? 30C would be nice :)
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| |> I fixed the program so that you don't get a negative voltage. It took | four |> lines and 15 minutes: | | It is much more elegant now. One more request, for those of us who don't | live in Alaska... How about defaulting the ambient to something warmer | than -40C? 30C would be nice :)
Or plot a graph across the range of lowest case ambient to highest case of insulation breakdown. Or at least list a table for every 5C step.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I ran this on another commercial calculator that I use, and it gave "vd0%" as the answer. These calculators do assume a constant load, since they are designed for real world application where this is a good estimate of actual operation, not precise physics. They give good results when used in more realistic calculations, with voltage drops up to perhaps 15 or 20%.
Of course, you are also assuming a constant resistance for the bulbs, which is not real physics either. The problem you gave would result in no lights, regardlss of the actual voltage drop number. Not a very useful installation by any calculation result.
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| |> If electricians use calculators or formulas that result in violations of |> physics, then I sure as hell don't want to hire them to wire anything of |> mine. I'll play it safe and wire my own. | | I ran this on another commercial calculator that I use, and it gave | "vd0%" as the answer. These calculators do assume a constant load, since | they are designed for real world application where this is a good estimate | of actual operation, not precise physics. They give good results when used | in more realistic calculations, with voltage drops up to perhaps 15 or 20%. | | Of course, you are also assuming a constant resistance for the bulbs, which | is not real physics either. The problem you gave would result in no lights, | regardlss of the actual voltage drop number. Not a very useful installation | by any calculation result.
Certainly it is not a useful configuration. It was chosen so that the current would not be so excessive as to melt the wire, yet still show results that are obviously in error without having to manually run the formula through on a hand calculator to be sure.
I think what you are using is something that would be more appropriately called a "voltage configuration analyzer". If your "vd0%" is meant to say "this situation cannot be practically compensated for", that I could agree with that. Another poster suggested the purpose was really to see how much drop was present in a constant current situation where in the case of 20 60-watt light bulbs we want a constant current of 10 amps. But the only case where that would be a real world concern is if you are going to be raising the voltage to correct it. That still could be done in the example I gave, but quite impractical since the feed voltage needed would be 794 volts (which would also exceed the rating of 600v wiring for a big part of the path, and 18 AWG wire generally is rated well less than that).
If you are a distribution line engineer calculating what transformer taps to use to ensure that a given drop ends up with the correct voltage at the far end, then you do need a calculator that deals with a constant load situation. You also need to do that kind of calculation over the full range of loads so you don't end up with excessive voltages when the load is reduced. The calculator on that web page would still be inappropriate for that case.
The case more people end up needing to work with is where changing the supply voltage is not generally an option (other than to jump up to the next higher voltage increment to reduce the I^2R losses). Marginal cases deal with trying to understand how much voltage is actually going to be present at the far end, and selecting the correct wire size to get things into an acceptable range. That was how this and other threads like this have started. The calculator on that web page would still be just as inappropriate in this case as well.
A more practical calculator for the distribution line engineer would consider the choices available for transformer voltages, drop wiring, and the full load range, then plot a graph showing voltage swings with changes in load for each of the choices. A smarter application could dismiss any choices considered out of range, and even advise exactly the best choice, including the costs of equipment, materials, and the energy loss.
A more practical calculator for someone trying to decide what wiring to go with to light up the barn would take the supply voltage, distance, load figures, and show the end result voltage under various wire choices across the load ranges. These cases generally don't involve voltage change other than choosing 120, 208, 240, 277, 347, 480, or 600. They rarely involve the use of a transformer or variac. And of course they don't invole a one mile distance, either.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I am not sure which ones you have used, but the one I use the most takes into account conductor material, raceway material, conductor temperature, circuit configuration (1ph, 3ph, conductors/phase, etc.), type of load (constant current or constant VA), type of current (AC or DC). It will solve for any one of the following, given the other two: Conductor size, conductor length, and voltage drop. It also calculates series voltage drop for a string of loads. I am at a loss as to what to call it if it is not a voltage drop calculator (which is what the program calls it).
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| |> A more practical calculator for someone trying to decide what wiring to |> go with to light up the barn would take the supply voltage, distance, |> load figures, and show the end result voltage under various wire choices |> across the load ranges. These cases generally don't involve voltage |> change other than choosing 120, 208, 240, 277, 347, 480, or 600. They |> rarely involve the use of a transformer or variac. And of course they |> don't invole a one mile distance, either. | | I am not sure which ones you have used, but the one I use the most takes | into account conductor material, raceway material, conductor temperature, | circuit configuration (1ph, 3ph, conductors/phase, etc.), type of load | (constant current or constant VA), type of current (AC or DC). It will solve | for any one of the following, given the other two: Conductor size, conductor | length, and voltage drop. It also calculates series voltage drop for a | string of loads. I am at a loss as to what to call it if it is not a voltage | drop calculator (which is what the program calls it).
Voltage drop happens, but that may not be what people need to know. Instead, people need to know what to change to make the load voltage be correct. For what you do as an engineer, you need to know all those things. And for most people most of the time, that's what gauge wire to use. You could call the program by any name of any data is gives you. So if you want to call it by the name voltage drop, then go ahead. I'll call what I would use to solve a problem by what it is that defines the name of the problem. But we're probably not talking about the same program. The program on the web site is definitely not the one I would use to determine whether AWG 8 wire is enough to power my barn 200 feet away. The program you described is probably overkill (does it model the cooling level of airflow).
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

my
Why not? It doesn't directly calculate it, so you need to plug in a few wire sizes to determine the correct one, which only takes a few seconds. I am not saying it is perfect, but it seems to work OK based on a few quick trials that I ran. I don't use it regularly, and this is not an endorsement, just an observation.

Actually, it is quite simple to use. It does not calculate the actual conductor temperature. It allows you to select the temperature of the wire (60, 75, or 90 C) and then calculates the voltage drop at that temperature. In many cases this gives a conservative solution, and further precision is not necessary.
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| |> The program on the web site is definitely |> not the one I would use to determine whether AWG 8 wire is enough to power | my |> barn 200 feet away. | | Why not? It doesn't directly calculate it, so you need to | plug in a few wire sizes to determine the correct one, which only takes a | few seconds. I am not saying it is perfect, but it seems to work OK based on | a few quick trials that I ran. I don't use it regularly, and this is not an | endorsement, just an observation.
The voltage drop values it gives are not correct. It assumes that you have adjusted the supply voltage to force the current to stay the same. With the supply voltage constant, increased resistance in the wiring causes the current to drop. That calculator does not account for that.
The extreme case I posted shows it more obviously in that the voltage drop exceeds the supply voltage. But even in non-extreme cases, it is still assuming a constant current.
If you already had a situation where you can measure the existing current then you can plug that current in and see what the voltage drop is. But that is a situation where you are perhaps operating with the wrong voltage at the load, and thus the wrong current. If you know what voltage drop is with the wrong current, it's not telling you want to do to get the right current.
|> The program you described is probably overkill (does it |> model the cooling level of airflow). | | Actually, it is quite simple to use. It does not calculate the actual | conductor temperature. It allows you to select the temperature of the | wire (60, 75, or 90 C) and then calculates the voltage drop at that | temperature.
So how will you know what temperature the wire will rise to? It's asking you to actually set up the situation, measure the current and temperature, then it will tell you how much voltage drop you have? If I did set it up and could measure the current and temperature, don't you think I could just as easily measure the voltage at the load and do a simple subtraction?
The usefulness of a calculator is for predicting a situation where you know certain starting parameters like what the load is, what the supply voltage is, and what kind of wire you have (or are considering using). Temperature knowledge would at this point be the ambient temperature. The numbers you gave look more like common insulation ratings rather than expected operating temperatures. A more useful calculator would model the temperature rise over time and how that affects the circuit. But to do that you also have to consider the thermodynamics of the situation, and that is the hard part as you now have to consider so many factors about how the wiring is enclosed. It might be better to just take load characteristics, supply voltage, wire size, and minimum ambient temperature, and plot a graph over temperature rises showing running current, load voltage, voltage drop, and wattage loss.
| In many cases this gives a conservative solution, and further precision is | not | necessary.
But the calculator on that web page isn't giving the correct answer to begin with, because it isn't working in the real situation most people have.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
know

Temperature
operating
That is exactly what they are. You are doing a worst-case calculation at the temperature limit of the wire. If it runs cooler, you have a margin of safety.

loss.
Bear in mind that the loads that you use as input for most of these calculations are estimates to begin with (i.e. va/sq ft lighting & receptacles, diversity factors, etc.) Actual measurements almost never agree with them. All of the extra complexity and precision that you are proposing for the calculator won't provide results any more accurate than these estimates.
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.