sequence susceptance measurements

Aug 20, 2004 1 Replies
Jump to replies (1)

Dear Group,



I've been asked to measure sequence susceptances (B1, B0) on an overhead line. Basically there are only 2 measurements that I can in practice perform:


1) measure capacitance from each phase to ground and
2) measure capacitance between phases.

So now I can convert from the capacitance to a susceptance at 50Hz and this gives me 6 values of B.



B(a-e), B(b-e), B(c-e) and B(a-b), B(a-c), B)b-c).



How can I convert these into the sequence susceptances B1 and B0?



also how does disparity in the first group (to earth) or the second group (between phases) effect the results.



Many thx



Danny


-- Daniel Indyk C.Eng C.Phys


Harder way (theoretically better) You will have a Baa which will be the sum of the Bae,Bab,Bac values (sum of admittances connected to the a line (earth as reference). Ditto for Bbb, Bcc. the resulting matrix will be Baa -Bab -Bac

-Bba Bbb -Bbc Bab=Bba etc.

-Bca -Bcb Bcc

Chances are that the Bab is not Bac and Baa is not Bbb etc (too much to hope for) This is an abc matrix which can be transformed to a zpn matrix . The result will not likely be diagonal and that is a lot of work. This is generally true for both impedances and admittances and is a fact that is generally ignored.

Easier way: If the equivalence of full transposition is assumed, then simply take B1 as the average of Baa ,Bbb Bcc values and a zero sequence value that is simply the average of your Bae,Bbe and Bce values. The results will be good enough- particularly for susceptances in a typical situation .

If the to earth results were the same and the between phases group were the same, the matrix would be symmetrical and converting to sequence components would result in a diagonal matrix - no coupling between sequences. This is what is generally done in the usual calculation of sequence impedances. In the case where the groups values differ, there will be coupling between sequences - this is generally ignorable as indicated above. Where it is not- then the advantage of sequence components is lost.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required