voltage phase tester

I've been wondering just what technique these proximity voltage testers use, whether capacitive or inductive, and in particular if there is any rectification involved. The idea I have is to build one of these with some more advanced circuitry. That circuitry would have a high precision clock that would drift off expected time by no more than a few degrees of

50 or 60 Hz over the period of a few hours or a day. If the sensor can pick up the voltage waveform reasonably accurately, and not half-wave rectify it, then the circuitry could detect the phase timing and remember that when a "set" button is pressed. Then subsequent readings can be compared as to phase and report which phase wire is being detected, or even the number of degrees (which might not be too accurate if more than one phase is nearby). Anyway, the idea is to be able to reference one phase wire, and then be able to detect elsewhere which of the phase wires is that one, and which are different. It could be used to verify that hot wires are indeed opposite phase without having to make contact with the conductor (something you don't want to do often with higher voltages on live circuits, especially greater than 600 volts). Those working with higher voltages can have a sensor on the end of a hot stick feeding the waveform back to the analyzer via an LED.

Or has this already been done? I haven't seen anything more than just the little flash and beep gadgets made from this method of sensing.

If the method requires half-wave rectification, it would ruin the ability to do this with opposite phases of single phase, but it still could work with three phase power.

Reply to
phil-news-nospam
Loading thread data ...

space inserted here

If what you describe is what you want- then all you want is a differential voltage above some allowable minimum. The phase won't matter. When you use a conventional voltmeter between two wires- whether true rms or Radio Shack special (average+bugger factor) this is what you are doing. If the two points are at the same potential at any and all instants, such a meter will indicate it. If not- than that will be indicated. A simple detector will do this. Phase measurements are not needed. Part of the problem with a capacitive pickup device is that , as far as I know, even expensive devices (substation capacitive votlage devices) are not suited to accurate phase measurements without compensation and a fixed location with respect to the hot wire.

It may be possible, for 3 phase applications to set up a unit which can detect phase rotation but accurate phase measurement in a portable device with no actual contact..?

Reply to
Don Kelly

| If what you describe is what you want- then all you want is a differential | voltage above some allowable minimum. The phase won't matter. When you use a | conventional voltmeter between two wires- whether true rms or Radio Shack | special (average+bugger factor) this is what you are doing. If the two | points are at the same potential at any and all instants, such a meter will | indicate it. If not- than that will be indicated. A simple detector will do | this. Phase measurements are not needed. Part of the problem with a | capacitive pickup device is that , as far as I know, even expensive devices | (substation capacitive votlage devices) are not suited to accurate phase | measurements without compensation and a fixed location with respect to the | hot wire. | | It may be possible, for 3 phase applications to set up a unit which can | detect phase rotation but accurate phase measurement in a portable device | with no actual contact..?

I'm not trying to accomplish accurate; I'm trying to accomplish verification that phasing is correct after energization, and phase identification when working on hot wires, without having to come in contact with the wires. Plus or minus 30 degrees would probably do it, though it if were within 10 degrees I think there would be more confidence.

You wanna stick the probes of your Radio Shack voltmeter on live 12470 volt wires?

Reply to
phil-news-nospam

Phase identification could not be achieved on the basis described because the frequency drifts. In UK the frequency limit is + or - 0.1 Hz. That is 1 hz in

500 hz which is only 10 seconds. Thats a max slip from true 50hz of 360 degrees in 10 seconds.

I have determined phase using a simple capacitative coupler but needed a radio link back to a master freq reference signal. It works really well. I have done it over a distance of 50 km.

Robin Watson

Reply to
RbnWatson

| Phase identification could not be achieved on the basis described because the | frequency drifts. In UK the frequency limit is + or - 0.1 Hz. That is 1 hz in | 500 hz which is only 10 seconds. Thats a max slip from true 50hz of 360 degrees | in 10 seconds. | | I have determined phase using a simple capacitative coupler but needed a radio | link back to a master freq reference signal. It works really well. I have done | it over a distance of 50 km.

So looking at two (one being a known) phases at once would be required. OK, so I'll bury the idea.

Reply to
phil-news-nospam

differential

verification

----------- I got nervous when, during a light snowstorm, I saw winking from part way down an post insulator in a 735KV substation. it makes one want to check relative distances- to ground and to me..

I wouldn't want to be anywhere near with a RS meter. With proper meters and equipment- fine- but I really would prefer to put in a PT or properly designed capacitive voltage divider (inserting it dead- Thank you.) However- such capacitive devices in a portable situation may be questionable and not to be trusted except for indication of potential. However, I have been wrong before. Does the device you mention have compensation circuitry? If so it may be within the phase angle range that you indicate. If you can get a couple of such devices and apply them to a known line and compare the voltages on a 2 channel scope, you would have something to go on and could see the effects of variations of distances from the line or non-contact devices.

Reply to
Don Kelly

Don't bury it yet- if the two phases are in the same system, frequency shifts within normal bounds are not that important- relative phase is what you are looking for . How expensive a circuit would be to detect this is another problem but may not be all that great.