Curious about some links posted for "Understand PID control"

Nov 06, 2005 26 Replies

- lots of back and forthing snipped -

I think the real item of interest here is that Peter's system is using a form of integrator bounding that ends up working the same as Jerry's circuit. The difference is that Jerry's way is easier to implement but more obscure in its operation for a beginner. Peter's way looks, with the exception of a rather complicated integrator limit, like a PID that you may see in a textbook.

I suspect that the two forms are essentially, if not exactly, the same behaviorally because of the way that Peter's method limits the integrator.

I'm tempted to believe that, but if Peter's PID-style integrator has the same time constant as a classical PID integrator, then it's not equivalent to Phelan's. By time constant, I mean the time constant of an equivalently performing op-amp integrator; namely, the R-C consisting of the input resistor and the feedback capacitor.

Jerry

Consider placing the closed loop poles on the real axis. That is safe. Then the response is either critically damped or over damped. However, one must be mindful of the location of the zeros since they are not placed.

Peter Nachtwey

I don't understand this comment at all. However, I am not claiming that that the integrator limit I use makes a PID equivalent to Phelan's. I am just claiming and demonstrated that a PID doesn't need to overshoot and its response will be faster because a PID has zeros which extend the bandwidth. This contradicts the advantages the pages on your webpage. BTW, the incremental ( velocity ) form of PID doesn't need to overshoot either.

By time constant, I mean the time constant of an

¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯ The digital world allows one to do things that can't be done in the analog world.

Peter Nachtwey

I have gotten into trouble even with that, in the case of a system consisting of two integrators and an adjustable low-pass stage. Anything with three poles on top of each other ended up with a poorly behaved controller (I _think_ it wasn't minimum phase, but I can't remember). I had to go to a pole-placement rule that put one pole closer to z = 1 than the other two, then everything was fine.

The point being that while I could make a pole-placement rule that worked, I had to do it by working backwards from a few example controllers that I reviewed for robustness using other means.

I have had a lot of success with pole placement. If you check my equations you will see it is very simple.

Peter Nachtwey

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required