When wiring up electrical service configured as 3-phase corner-grounded delta, it would seem that the appropriate way to connect overcurrent protection would be to make the 2 ungrounded wired breakable, and pass the grounded wire straight through. That would imply using equipment that is wired the same way as center-tapped 1-phase. NEC states that a 2-pole breaker must not be used for such service unless it is marked as being rated for both 1-phase and 3-phase (240.85). I would presume that is because of the higher hot-to-ground voltage and the effect it could have on interruption capability (as in NEC note in 240.85).
Is a 2 pole plus neutral breaker panel what is typically used for 3-phase corner-grounded delta? I can't imagine using a 3-phase panel for this.
Are such breakers readily available?
Does the higher hot-to-neutral voltage decrease the interruption current rating, considering that the neutral wire isn't passing through the breaker (disregarding GFCI breakers where the neutral wire is involved).
Would these or other issue vary whether the configuration is closed-delta or open-delta ("V")?
Are corner-grounded delta configurations ever used at voltage levels above
240 volts (in the US), such as maybe 480 volts or 600 volts? Have utilities ever used it for primary distribution?FYI, I'm not referring to delta configurations where one of the windings is center-tapped to get 240/120 volts for conventional single phase compatible lighting voltage.