Closed Delta 120/240V 3-phase service

Feb 10, 2008 161 Replies

| Except, there is no connection to one lug of the big can except to | the small can, so you get either: | | B | / | / | N-----A' | \ | \ | C | | or maybe | | B | / | / | A-N | \ | \ | C | | (trying to show a different voltage on A) | | or some combination. Not too useful IMO. | | There are quite a few of those things in inner city Philly, as well as | some other odd practices.

Curious-er and curious-er. It might need an investigation.

I wonder if maybe there might be a Scott-T inside that big can and the little can could be modifying it somehow.

In the situation under discussion were the only significant three phase load is the elevator a three phase auto transformer wired in boost configuration would solve the problem at a reasonable cost.

Tom:

Thanks for the suggestion. Could you elaborate a bit more on how this would be connected please...

Are you saying that you would have standard split phase 120/240V from one transformer... Then in addition to that, you would have 3 autotransformers (or one 3 phase autotransformer) for the 3 phase load?

I've never heard of anything like this. Aren't auto transformers not permitted (from the utility primary to customer secondary) because of safety concerns? Or if it is a customer provided transformer (perhaps a buck-boost XFR), wouldn't you need a utilility transfomer on the primary 3-phase line anyway?

It doesn't seem that you would be saving anything here.

Beachcomber

| In the situation under discussion were the only significant three phase | load is the elevator a three phase auto transformer wired in boost | configuration would solve the problem at a reasonable cost.

What if you don't have any need for three phase power at all? Suppose your building has elevators that work fine on single phase power. The building is so big, however, the power company doesn't want to drop only one phase into it; they want to have all three phases coming in, in some approximation of a balanced load. And you need to supply 240 volts, not 208, to each tenant. What would you set up?

On Sat, 16 Feb 2008 07:54:39 GMT Beachcomber wrote: | |>In the situation under discussion were the only significant three phase |>load is the elevator a three phase auto transformer wired in boost |>configuration would solve the problem at a reasonable cost. |>-- |>Tom Horne |>

| | Tom: | | Thanks for the suggestion. Could you elaborate a bit more on how this | would be connected please... | | Are you saying that you would have standard split phase 120/240V from | one transformer... Then in addition to that, you would have 3 | autotransformers (or one 3 phase autotransformer) for the 3 phase | load?

With just 2 extra small transformers, you can add a couple extra phases to a normal 120/240 split phase and end up with 4 lines, 3 of which are the same as 208 wye, if you use the original incoming three phase distribution to derive it.

Or you can do it with just 1 weird transformer. Using a single phase transformer with a 139/277 volt split phase, you wire it's primary B-C if the original single phase is A-N (or wire it C-N if the original single phase is A-B). Connect the 139/277 center tap to one line end of the 120/240. Voila, you now have a Scott-T emulating 277 delta.

  • | | N

Of course, the answer is D). That is why tower light monitors are required.

What is real fun is when you move to a different tower, and still have to monitor the lights at the old transmitter site. I had to do that at WACX. I used a 1.024 MHz crystal and divided it by 1024, then filtered it to get a fairly clean sine wave. A current transformer monitored the circuit. The sine wave was on, when there was at least one light out. That way, when the beacons flashed, the signal dropped for a second.

At the other end, I used a 567 tone decoder to detect the 1 KHz signal. There was a small, but bright LED in the mater operator's field of view. They logged when it started flashing, and when it stopped. If the light went out it meant there was no AC at the old site, and that was logged in and out, as well.

BTW: My choice would have been F). Find the idiot who wrote the test and make them re-write it so that all questions were closer to the proper answer. There should be no throw away questions on a test like that.

WPFB. the local AM & FM station in Middletown, Ohio had several engineers with a first class ticket. The AM was a daytimer, and later, allowed low power nighttime operation. They ran a background music service they called Musiplex as a SCA service. In the early days there were no commercial SCA equipment, so they built tuners & receivers and leased them, with their music service. One of the engineers must have been in love with Nuvistors. There was about a dozen nuvistors, and each section was built on a steel plate that mounted between a coupe sets of rails. The RF sections looked odd enough, but the 20 W PA amp look really funny.

formatting link

What makes you think that its up to you to chose? The utility company is going to tell you what is available. The elevator company is going to tell you what they need, as well. As usual, you're playing another of your long winded, and useless games of 'What if'...

I took the exams for First Phone, Second Telegraph and Amateur, in New York City, shortly after I was discharged fron the Army in 1946.

The FCC exam proctor noticed I was doing well on the first couple of elements I handed in and told me to do just about 80% and turn them in. If I didn't get the required 70% to pass, he'd give them back for me to try a few more questions. Of course I'd pick the easy question to answer first.

He said I had the record for most elements passed in one day. Probably also the record for the lowest passing score!

No, not "interleaved" but split. Invert each phase, as in a center- tapped transformer (I.e. split) and you're there.

Kinda like they do now on the pole.

Kinda...

Ok, I'm confused. This is different how?

Exactly (is there a difference?).

Right; split-phase "wye".

I don't. You seem to see a difference between this "star" and an ordinary 3-phase "wye" that delivers residential 240V split-phase. I don't see anything new or particularly interesting here, but am trying.

That's funny, because that's exactly how I get the 240V for my house off the 3-phases on the pole.

Nope. I'm still wondering why you see your "star" as any different than what we see on 90% of the poles in the country.

What if Phil bought his own bigass transformer?

I "worked" at WPGU-FM (at the time the only network affiliated student station) for a while. Their transmitter was on a 12-story dorm building about a mile from the studios (in the basement of another dorm building). THe logs were taken remotely over a phone line with a contraption that consisted of a rotary phone dial and meter. One of dial "positions" ('9', IIRC) returned the antenna light current, which was logged every half hour along with all the rest of the stuff.

As far as I was concerned, the whole test was throw away questions like that. It was a waste of a day and a trip to Chicago.

On Sat, 16 Feb 2008 14:16:04 -0500 Michael A. Terrell wrote: | snipped-for-privacy@ipal.net wrote: |> |> On Sat, 16 Feb 2008 06:38:55 GMT Tom Horne wrote: |> |> | In the situation under discussion were the only significant three phase |> | load is the elevator a three phase auto transformer wired in boost |> | configuration would solve the problem at a reasonable cost. |> |> What if you don't have any need for three phase power at all? Suppose your |> building has elevators that work fine on single phase power. The building |> is so big, however, the power company doesn't want to drop only one phase |> into it; they want to have all three phases coming in, in some approximation |> of a balanced load. And you need to supply 240 volts, not 208, to each |> tenant. What would you set | | | What makes you think that its up to you to chose? The utility | company is going to tell you what is available. The elevator company is | going to tell you what they need, as well. As usual, you're playing | another of your long winded, and useless games of 'What if'...

Maybe you should read some of the tariffs. Most jurisdictions do have some requirements that certain services must be made available of so requested. The only "what if" here is "what if someone knew what they were allowed to really ask for".

I think that logically, the process goes something like this.

  1. The architect or building contractor responsible for the electrical system needs to research the utility tariffs and policies and determine what services are available.

  1. Further research may be necessary to see what services are available at the specific location of the building under construction.

This may be different then #1.

  1. Given the available choices, it is up to the person designing the electrical system within the building the most economical and useful service, given the specific needs of the building (elevators, HVAC, pumps, machine shop tools, etc.) That is, should it be 120/208,
120/240, volt single phase or three phase, open wye, or closed-delta, etc.

#3 is the most interesting and the most difficult, apparently, from the comments offered on this thread. It doesn't seem that there are any carved-in-stone rules for what is best, only tradeoffs and different opinions.

Have I got this right?

Beachcomber

Progress Energy, who bought Florida Power, wouldn't let you provide any transformers. They did the calculations, and set their own transformers. Three phase availability was determined by your location, but generally any building above a certain level was three phase. Even small convenience stores and gas stations are three phase around here. The only home I've seen with an elevator had three phase power, along with an Onan diesel three phase generator with an automatic transfer switch.

I would have had to go to Detroit to take the test. In the mid '70s it would have cost me about $1000 to make the trip, including a several day stay. That was why I walked away from broadcast work for 15 years. I was tired of patching junk with no parts budget, zero downtime and idiot station managers who thought they could tune a TV transmitter like their ham gear.

Obviously, you don't and you've been flogging another dead horse. You can take any simple subject and turn it into mind numbing drivel. You've flogged this one for a week and made zero progress. Even if you got answers, they would only be valid for one location, not the entire planet earth.

You bitch about no availability of 208 volt appliances. How many do you see that are marked 240 VAC only? I see a lot that are marked

208-240 VAC. So your water heater is a few volts low. It won't make much difference in the output. If you buy at the right places, 208 volt stuff isn't hard to find, even in the deep south. If you are in an apartment, it is up to the landlord to provide the major appliances, and repair or replace them when they quit. So, if the building is big enough, they are supplied three phase. no matter how much you want to yak about what ifs, no one really gives a damn, except the local power company, and the owner of the building.

Power is a function of the voltage squared. So a 3kW heater at 240v becomes 2.25kW at 208v. It may not be significant if it's used for storage heating but as an instantaneous heater it would matter.

Gee thanks for that lesson. I've know and used it since the '50s. If you need that extra bit of heat, you can buy the proper heating element. Not at the over the counter type 'DIY' dumps, but at a real plumbing supply house.

On Sat, 16 Feb 2008 18:37:16 -0500 krw wrote: | In article , phil-news- | snipped-for-privacy@ipal.net says... |> On Fri, 15 Feb 2008 22:34:43 -0500 krw wrote: |> | In article , phil-news- | | | |> |> | Specifically, the six-phase "star" and three-phase center-tapped |> |> | wye. With any two phases any number of others is a few transformers |> |> | away. |> |> |> |> I don't know which you mean by "three-phase center-tapped wye". Maybe you |> |> can pick it out from this police lineup: |> |> |> |> * * * * * * |> |> \ \ / * * * | \ / \ |> |> \ \ / / \ / | | \ / \ |> |> N---* *---N---* / \ / | *---N---* N * |> |> / / \ / \ / | | / |> |> / / \ *---N---* *---N---* *---N---* | / |> |> * * * * * |> |> |> |> 1 2 3 4 5 6 7 |> |> |> |> If you don't see the guilty party, maybe you can draw a picture :-) |> | |> | #2 be the culprit. Your "split-phase" three-phase from another |> | post. |> |> That is the same as the six-phase "star" or "6 star". So if you can't |> see any difference, that's because there isn't any. I would not have |> called this a "wye" of any sort since it doesn't look like a "Y". But |> it could be TWO Y's interleaved. | | No, not "interleaved" but split. Invert each phase, as in a center- | tapped transformer (I.e. split) and you're there.

You mean like having 2 three phase 208Y/120 transformers, one fed 180 degrees out of phase from the other, and combining their outputs with neutrals tied together? That's what I meant by interleaved. If that's not what you are saying, then I don't understand what it is you are saying.

|> To make this derived system, you need either: |> |> 1. 3 single phase transformer cores | | Kinda like they do now on the pole.

Yes. Except instead of using 120-volt-only transformers (there are such things ... just 2 lugs on the secondary), they need to use the 120/240 volt transformers (plenty of those around) and understand the concept to know how to wire it up.

Metering that could be an issue. In the case of the apartment building, individual tenants would be metered at 120/240 so it's not an issue. But if this needs to be metered in its "6 star" configuration, it can be done with 3 CTs, each carrying the 180-degree-opposite conductor pairs running in opposing directions just as a single CT would be used for single phase power.

|> 2. 1 three phase tranformer E-core | | Kinda...

It could be done. The manufacturing just has to provide a pair of 120 volt windings, or a series 120/240 tapped winding, and sufficient terminal board space to deal with it.

|> Then you need to wrap these cores with 3 primary windings and 3 secondary |> windings. Usually the secondaries go on the inside and the primaries go |> on the outside, so the secondary at lower voltage and higher current has |> less winding resistance. | | Ok, I'm confused. This is different how?

The difference is that a traditional E-core 208Y/120 transformer would have only ONE 120 volt winding per core bar (times the 3 core bars). Two such windings at 120 volt each, or a 120/240 volt series winding (connected in series inside the winding instead of at the terminal board) would be needed for the "6 star" configuration.

|> Each of the 3 secondary windings needs to be either: |> |> 1. a pair of 120 volt windings which you can wire in series |> 2. a single 240 volt winding with a center tap right in the middle | | Exactly (is there a difference?).

Yes, there is a difference. In #1 you have 4 wires coming from the secondary winding to the terminal board. In #2 you have 3 such wires because the winding is series connected, possibly a continuous single wire, inside the winding itself, and just tapped at a mid-point.

It's a difference in construction. Some people might be more familiar with one over the other.

|> All of the center points of these windings are wired/bonded together and |> grounded. Then each of the three phases will have two poles 180 degrees |> apart. Some people will call this six phases. | | Right; split-phase "wye".

Keep the "wye" in quotes, then; it's not really wye. I would never call it a wye at all. It's a 6 pointed radial star.

|> |> Note that drawings are NOT to scale (relative to voltage). |> | |> | Close enough for government work. |> | |> | |> | |> |> |> Can you describe an electrical system configuration which is capable of: |> |> |> |> |> |> 1. Supplying 120 and 240 volts (not 208 volts) in single phase to all |> |> |> single phase loads. |> |> | |> |> | Look harder at a center-tapped wye. There is only 60degrees between |> |> | the "negative" of phase-A and Phase-B. |> |> |> |> I don't know which I need to look at. |> | |> | #2 |> |> Let me relabel the terminals like so: |> |> C' B |> \ / |> \ / |> A----N----A' |> / \ |> / \ |> B' C |> |> Between A and A' you have 240 volts. |> Between B and B' you have 240 volts. |> Between C and C' you have 240 volts. |> Between A and B you have 208 volts. |> Between B and C you have 208 volts. |> Between C and A you have 208 volts. |> Between C' and A' you have 208 volts. |> Between A' and B' you have 208 volts. |> Between B' and C' you have 208 volts. |> Between A and N you have 120 volts. |> Between B and N you have 120 volts. |> Between C and N you have 120 volts. |> Between A' and N you have 120 volts. |> Between B' and N you have 120 volts. |> Between C' and N you have 120 volts. |> Between A and C' you have 120 volts. |> Between C' and B you have 120 volts. |> Between B and A' you have 120 volts. |> Between A' and C you have 120 volts. |> Between C and B' you have 120 volts. |> Between B' and A you have 120 volts. |> |> Which connection pair do you need to ask about? | | I don't. You seem to see a difference between this "star" and an | ordinary 3-phase "wye" that delivers residential 240V split-phase. | I don't see anything new or particularly interesting here, but am | trying.

A true WYE is not split phase. That makes a contradiction of terms. But if you know of a manufacturer that makes such a transformer AND calls it "split phase wye" or some such thing, please do point to their catalog reference. I've looked at a lot of transformer catalog info online and have never seen such a thing in a single transformer.

|> |> |> 2. Divides up the single phase load in three equal groups in order to |> |> |> maintain a balance on each of the three phases of the utility supply. |> |> | |> |> | How does it divide anything? An imbalance can still be placed on |> |> | any one (or two). |> |> |> |> Of course an imbalance can always happen, and likely will. But it is a |> |> statistical thing. If a building has 54 apartments, connecting 18 of them |> |> to phase A, 18 to phase B, and 18 to phase C, would be "balanced" enough |> |> for utility purposes. If the supply were coming in as 120/240DCT, then |> |> all of the apartments would be on just one of the phases and the phase |> |> loading would be as lopsided as if the entire building were supplied with |> |> single phase power. If the utility insists on balancing the phases and |> |> rejects single phase service for this reason, they will reject 120/240DCT. |> |> If the supply is 208Y/120, that would satisfy the utility (18 apartments |> |> supplied with phases A and B, 18 suppleid with B and C, and 18 supplied |> |> with C and A). But it would not satisfied the need to have 240 volts. |> | |> | Sure, but your "six-phase" is no different than the normal three- |> | phase "wye". At least I don't see it. |> |> The normal three phase WYE is just: |> |> B |> / |> / |> A----N |> \ |> \ |> C |> |> Between A and B you have 208 volts. |> Between B and C you have 208 volts. |> Between C and A you have 208 volts. |> Between A and N you have 120 volts. |> Between B and N you have 120 volts. |> Between C and N you have 120 volts. |> |> There aren't any other ways to connect, and no way to get 240 volts. | | That's funny, because that's exactly how I get the 240V for my house | off the 3-phases on the pole.

Which connections give you 240 volts? If you are getting 240 volts from A-B or from B-C or from C-A, and if the phase angles really are 120 degrees as a true three phase WYE would be, then you are going to get 139 volts at A-N, B-N, and C-N. I don't think that is what you want.

FYI, I did find one utility offering 240Y/139 service for some portions of their service area, as a replacement for 240D.

Maybe you are getting ONE phase of 120/240 via ONE split phase transformer tapped to ONE phase (connected L-N) or TWO phases (connected L-L) of the primary distribution lines. But just because there is three phase on the distribution does NOT mean you are getting it. You are most likely getting one of: 208Y/120 three phase (my grandfather actually did get this at his home), or 120/240 single phase, or that old 240DCT/120 setup.

|> |> |> |> ... that is not the "6 star" I described? |> |> | |> |> | I still don't see the difference between that and a center-tapped |> |> | wye. Again, I'm not a power jock, so may be missing something |> |> | subtile. |> |> |> |> Maybe you saw something I didn't see. Check the above police lineup. |> | |> | Nope. You saw it, just one of us isn't "getting it" (I could easily |> | be missing something - 65h work weeks do that after a while). |> |> OK, hope the above helps. | | Nope. I'm still wondering why you see your "star" as any different | than what we see on 90% of the poles in the country.

208Y/120 is _very_ different. 208Y/120 has THREE line wires coming out at 120 degree phase angle equal intervals. The "6 star" (maybe we can call it 240*/208/120) has SIX line wires coming out at 60 degree phase angle equal intervals.

If I provide you with exactly 3 transformers which are wired up with one winding for the primary voltage and one winding for the secondary at 120 volts, it can be wired up by connecting the primaries in whatever they need for the type of service (delta or wye) and connecting the secondaries in a wye configuration. There, you have 208Y/120 just like 90% of the three phase poles in the country (I'll just accept your stats of 90% as I do not know the actual figures).

I have never seen, and never heard of, any "6 star" or 240*/208/120 setup anywhere. I have never seen any utility tariff (I've looked through a few dozen over the past few years) that offers such a service.

I HAVE seen a couple three phase setups where a 120/240 volt pole pig was used, and only HALF of it was wired up to get 120 volts. I HAVE seen one manufacturer detail that they do make cans with the 120 volt windings in parallel internally, and still have 3 lugs with one of them not connected. So these are not necessarily a case of wasting half the capacity. The 3rd lug may simply be there are part of the process of manufacturing only one set of empty cans instead of two different sets.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required