DC Meter To Read AC ma: Possible ?

Hello:
I wish to set the heat-anticipator on a heating thermostat by mesuring the current flow thru the circuit when energized.
It's probably about 400 or so ma, ac
But, I only have a meter that reads in dc ma.
Any way around this ?
Any conversion factor ?
Or, would it just blow my meter (dial type) ?
Thanks, B.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Robert11 wrote:

If you have ac volts ranges, you can stick a suitable resistor into series with the circuit and measure the voltage drop - and use the resistor value to convert to current. eg a one ohm one watt resistor will drop 0.4v ac when 400mA ac is flowing through it. A ten ohm resistor would drop 4v ac under the same circumstances but would need to be a couple of watts rating or more.
Or you can stick the meter at the centre of a full-wave bridge rectifier. But you would have to calibrate it, say using fixed resistors and a known supply voltage. It would be highly non-linear - particularly at low readings..
--
Sue