We have 750 KVA generator in our Press.Last week this generator malfunctioned. Meanwhile we arranged a generator of 1200 KVA. Press operates perfectly on 1200 KVA gen. and Power utility comapny. it might be because of harmonics generated from DC Drives in Main panel of Press. We measured harmonics at load side. When load is connected to generator (750KVA), 8.5% THD observed. Magnitude of 3rd harmonic is 8.2%. When load is connected to main Distribution sytem (Power Utility company), THD bacame 2.3% with 3rd harmonic 0.108 % and 5th harmonic
2.077%. My questions are:- why press operates perfectly at 1200 kva Genset and Main Distribution system ?
- why 3rd harmonic is more when load is connected to 750 KVA gen.
- is the problem laid in genset?
- How to mitigate the harmonics