Modify a temp-controlled fan circuit?

May 01, 2009 11 Replies

First reply

Dave Platt

Most of those thermistors have a negative resistance coefficient of temperature. Warm them up and the resistance drops. It looks to me as if R1695 (fixed) and R1696 (thermal variable) are setting the speed... nominal total would be 7k ohms, and it would decrease at higher…

Read the full reply

This motor and its drive circuit are one unit (the circuit board is on the end of the motor opposite the impeller, in the air stream):


It seems to me that the element in the lower right corner (RT1696) is a thermistor, or such. This is what controls the motor speed?



The manual this is from describes the thermistor (RT1696) as:



RES.,THERMAL:5 K OHM,10 PERCENT



No generic pn is given. It is a little green teardrop with a red dot on top.


If I want to boost the minimum speed, or alternatively, push the entire speed range up by a few hundred rpm, do I add an adjustment pot in series with RT1696?



Or...?



Thanks,


Most of those thermistors have a negative resistance coefficient of temperature. Warm them up and the resistance drops.

It looks to me as if R1695 (fixed) and R1696 (thermal variable) are setting the speed... nominal total would be 7k ohms, and it would decrease at higher temperatures.

If you were to replace R1695 with a smaller value, or perhaps a 2k pot, this would "fool" the rest of the circuit into "thinking" that the temperature is higher than it is. If this circuit is designed to fan-cool something, the fan speed would increase.

If a 2K pot was installed and adjusted lower, this would not only set a higher minimum speed but it would add a fixed positive differential to the temperature curve of R1696?

Thanks for your assistance.

R1695 is defined:

RES.,FXD,FILM:2K OHM,1 PERCENT,0.125 W

Replacing with a trimpot, use just the wiper and one leg? Or...?

Thanks,

Depends on whether the temperature coefficient of the thermistor is positive or negative. Check it with an ohm meter and see if the resistance goes up or down as you warm it. You can then connect a variable resistor either in series or parallel to get the effect that you want. Something around 1K in series or 100K in parallel would be a good place to start. Feel free to experiment.

Yes, try a 5K trimpot, wiper and one leg will work, or you can connect the remaining leg directly to the wiper so that if the pot develops a dead spot, the resistance will go up to the value of the pot rather than open circuit. I would put a 1K or so resistor in series with the pot as well so that it can't be reduced down to 0.

Replace R1695 with a 2K pot with 1K in series.

Is it an NTC or PTC resistor ? In any event a trimmer in series in place of R

1695 would give you some adjustment. Say 4k7 / 5k

Graham

It's wise to tie the wiper to the other end of the track to avoid opens.

Graham

^^^^^^^^^^^^^^^^^^^^^^^^^

^^^^^^^^^^^

Negative temperature coefficient of resistance. ;-)

Cheers! Rich

You could simply bypass the whole controller and run the fan balls-to-the-walls continuously, if it's rated for continuous duty.

Have Fun! Rich