|> | It's possible it is an NEC Code Violation to switch off the Neutral side |> | in anything of that caliber without switching off the Hot side also., if |> | it's a Caged Assembly Protected from Unauthorized Access & Personnel, it |> | passes as a job well done. |>
|> It's definite. |>
|> NEC 404.2(B) Grounded Conductors. Switches or circuit breakers shall not |> disconnect the grounded conductor of a circuit. |>
|> Exception: A switch or circuit breaker shall be permitted to disconnect a |> grounded circuit conductor where all circuit conductors are disconnected |> simultaneously, or where the device is arranged so that the grounded |> conductor cannot be disconnected until all the ungrounded conductors of |> the circuit have been disconnected. |>
|> -- |> ----------------------------------------------------------------------------- |> | Phil Howard KA9WGN |
formatting link
|>
formatting link
| |> | (first name) at ipal.net |
formatting link
|>
formatting link
| |> ----------------------------------------------------------------------------- | | Ground wasnt switched just the nuetral. I contacted the manufacturer and | found thast I was correct. This allows a ground fault to be detected without | actually turning the motor on. As far as this being unsafe it is documented | in the equipment lit and only people familar with the equipment should be | working on it
Switching the neutral is not necessary to detect ground faults; it's just the cheap way to do it. This thing should not be sold to the public.