I am hoping to get instructions on the proper use of a megohmmeter in the testing of a 3 phase 460 volt 29 FLA AC motor. The motor in question has been blowing fuses on an intemitent basis for a couple of days, when the fuse is replaced the moter starts and runs for approx

3-4 hours and then one or two legs will blow again. When starting the motor amps are fine as per name plate and the supply volts are dead on 460. As of this time the heaters on the motor starter have not tripped, only the fuses blow and not always the same phases. So back to the point of the post, what is the correct way of using a hand-crank type of megohmmeter to test the motor? I dont have experience with a megger and have recieved conflicting advice. Any help is appreciated.
Reply to
0zzy
Loading thread data ...

Disconnect the motor leads, test the wire and motor seperately. Pay attention to the motor terminations! Hand crank,,, yikes, I would test the conductors and motor to ground at

1500v for a minute. Then take a reading. Bigger is better. Anything over 1 meg ohm should be fine, 10-100 would be much better. Something I remember is 2.5-3 times operating voltage for low voltage testing.

Any chance of moisture in the motor? If so dry it out for 24 hours with hot air and re-test.

Then test the motor phase to phase, I would use a regular ohm meter on your VOM first. What kind and size of fuses are you using?

Reply to
SQLit

Such a megger is for measuring the insulation resistance. Disconnect all power and put one lead on any one of the three phase leads going to the motor, the other lead to a good ground connection that is also tied to the motor frame in some way. Crank until the reading stabilizes.

If its over 1 megaohm, then that's not the problem. If it is under, separate the supply cable from the motor at the motor terminal head and check the motor again. It it is good, check each of the three cable conductors separately.

From your description, it sounds like a temperature related fault. If the motor was overloaded, I'd expect the motor starter overloads to trip instead. To blow a fuse requires some sudden fault developing. Any 'acrid odors', or 'visual inspection' clues? Open the motor terminal head and take a look at the cable/motor-lead connections. This often can develop a fault if the insulating tape is rubbing against the inside of the terminal head.

If this is a temperature related fault (and it sounds like it since it starts and runs for a while before faulting), try to do the tests the moment the thing blows a fuse, before things cool off.

Good luck,

daestrom

Reply to
daestrom

Since only the fuses blow and the motor overloads do not trip, I would recalculate the fuse size to make sure they are correct for the application. You have not given all the information. What is the hp of the motor, the FLA on the motor nameplate, the application for the motor, what type and model of motor controller and size, and what type of fuses are you using? Also how old is the motor and how long in feet is the circuit?

Reply to
electrician

Some more information on the motor etc. : the motor is 20 years old, it is 29 FLA, it is running an air handler, the fuses are RK5 40 dual element time delay, the circuit lenght is approx 40 feet. There are no signs of heat or burning, no unusual smells, I opened the "pecker head" and it looks fine. The motor starter is a Square D Nema 2. When testing the motor should I test the 3 phase leads starting at the motor starter or open the "pecker head" and test the 3 phases there? Also do I need to test phase to phase at the motor and if so what readings should I look for? Many thanks to all of you.

Reply to
0zzy

Testing phase-phase with anything other than a very sensitive milliohm meter is pretty much a waste of time. The difference in resistance between a good motor and one with a fault is often much less than 0.5 ohm (not megaohm, just ohm).

If you were recording the insulation value for trending/maintenance rule, I'd say to measure at the 'pecker head' with the line leads disconnected. But for troubleshooting, don't bother disconnecting all the leads, just test from the motor side of the starting contactor. Unless one of the phases was open, the megaohm reading will be the same for all three phases (plus or minus winding resistance of

Reply to
daestrom

You fail to mention whether the motor is delta or wye. It may be best to disconnect all windings (marking them correctly for re-assembly) and then megging winding to ground and winding to winding.

Reply to
Don Kelly

What about the bearings getting hot and causing problems? I think you said in another post it was fused at 40 amps with a FLA of 29. The US code permits fuses up to 175% of the value in Table 430.250. (Exceptions apply) Possibly the motor overload is mis-sized or malfunctioning? Dean

Reply to