On Sun, 2 May 2004 09:34:53 -0400 nospam wrote: | Not sure if anyone here is familiar with the term | "R-56 Standards & Guidelines". It's a collection of | codes (NEC, etc), that Motorola compiled - along | with a set of best practices - that are recommended | when installing new communications equipment sites. | | Having said that, one of the items mentioned is to | have the "neutral bonding conductor" connected to the | grounding strip in the service panel. | | Which should in turn be presumably connected to | earth ground.
It should be connected to at least TWO earth grounds.
| Now, if you connect neutral to ground, and you have | a "short" condition - aren't you in effect providing | a circuit path to still operate the equipment ? (in | other words, mis wire something to work off hot and | ground, it'll still run - since ground and neutral are | already jumpered together!).
Yes, if something is miswired by being attached to the grounding conductor instead of the neutral conductor, it could function correctly.
| What safety does this provide ?
Separate neutral and grounding conductors are intended for cases where the wiring is correct, and a fault occurs. Fault current on the neutral has to go all the way back to the point where neutral and ground are bonded before it can come back along the grounding wire to any grounded chassis. That forces a single reference to ground and zero current in the grounding wire, and thus zero potential between a grounded chassis and actual earth ground (like a water pipe or wet concrete floor).
The bonding is not intended to provide safety for cases where the circuit is miswired using the grounding wire instead of the neutral wire. Historically, since the days of Thomas Edison, the neutral wire was considered to be the ground safety wire. In cases of imbalance (of which a line-to-ground fault is a serious case), voltage can be present on the neutral-pretending-to-be-ground wire. This is due to the voltage drop along the conductor back to where it is grounded to earth. Humans touching a chassis connected to neutral, and also to some true ground source, get that voltage drop applied to them (they become a new neutral path). In the case of a fault, the current, and thus the voltage drop, can be substantial. In the case of a neutral circuit failure, equipment may still operate, but the hazard is also now worse.
The whole purpose of a separate grounding (not neutral) wire is to provide a means to reference ground on equipment chassis in a way where circuit imbalances (which should not cause power interruption) do not introduce voltages to humans coming into contact with equipment.
Of course, in fault conditions, the fault could very well be from line to ground instead of neutral. There is no perfect safety anywhere. It's just better WITH a ground wire than without.
One way to enhance safety is to use radial ground wiring. Instead of having a ground wire jump from one outlet to another, the ground wire for each goes all the way back to a panel. You probably should also have each outlet on a separate circuit breaker. While a home might have many outlets wired in sequence for unanticipated usage, in an industrial setting, most outlets are there for a definite purpose. Those should be individually protected, which gets you that radial ground wiring.
| Or am I missing something ?
Perhaps you are missing a thorough safety inspection that would detect a miswired circuit.
You could also install ground current sensing equipment attached to either an alarm or a shunt trip. One sensor would concurrently measure all current carrying conductors, including neutral, in a single CT window. As long as all current returns by no other path than these conductors, then you do not have a ground fault. You could further put a sensor on the actual grounding conductor as a means to detect after-the-fact wiring errors if you are paranoid. But the extra sensor would be redundant since such an error would be detected by a current imbalance in the current carrying conductors. Such sensors would be located between the neutral-to-ground bonding point and the loads.
If you have a mission critical data center or communications center, these sensors would trigger alarms. Otherwise a "minor" wiring accident in one part of the data center could trip everything on the same system. Wiring each individual circuit through its own GFI breaker can help isolate areas and prevent a massive outage. A GFI breaker has a miniature current imbalance sensing system. These are not generally used in a data or communications center.
Safety training for all staff that could be doing any work on equipment (not just those authorized to work on power circuits) should be part of the program.