Re: Problem with 3-phase wiring.

Apr 02, 2004 4 Replies

Peter Jason brought next idea :



To get more heat we connect another bank of similar elements in parallel, to
> give a total of 2 x 12000 = 24000W.
>
> Of course these are totally resistive loads.
>
> But how do we connect the two banks in SERIES to get a very low heat output,
> often reqiured to heat viscous materials?

Have you thought about modifying a standard ready made star/delta contactor, as used for a motor starter?


Star would give you 240v across each element and delta 415v. Including the possibilty of switching the second set of elements would give you four different levels of heat input.

Nam Paik submitted this idea :

That would be one helluva big variac transformer, 3phase as well.

I figure with two separate star/delta controllers, each controlling one set of 3 heaters, you can get five separate power levels. (Off), 1/6, 1/3,

1/2, 2/3 and full power, if you can set each set of heaters independently to any of (off,star,delta). There are 9 possible settings, 3 of which duplicate 3 others. If you change the ratings of one set of heaters you have more different combinations.

On Fri, 02 Apr 2004 20:20:30 +0100 Harry Bloomfield wrote: | Nam Paik submitted this idea : |> Have you considered using a three-phase VARIAC (Variable AC) which |> allows you to produce any voltage from 0 to 100%? This allows you to |> adjust the heat output in fine increments since you can "dial" the |> output voltage. Power output is voltage squared divided by resistance | | That would be one helluva big variac transformer, 3phase as well.

You mean like this?

formatting link

Thanks for the replies. We might go the star/delta route using six 12KW elements.

Regards.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required