simple National Electrical Code question

This is an electrical question pertaining to derating more than three conductors in a single run of conduit.
I am feeding a 54 amp, 220 amp tankless hot water heater, and a 5000
watt, 220v A/C with electric heat from the main panel through 1 1/4" conduit.

tankless water heater through 1 1/4" conduit. Amd I plan to run 15 feet of #10 wire to the A/C through the same size conduit, and place the A/C on a 30 amp breaker.
There will be four current carry conductors in this conduit. I don't have a copy of National Electrical Code handy. The answer to this question can be found in the National Electrical next to ampacity capacity of wire size or conduit fill.
Can anyone help me calculate the derating of these conductors?
You can just email me the formula from the national electrical code.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I hope it is a 220 VOLT heater not amp.
Depending on where you live you might need to also increase wire sizes due to ambient heat. If you run #4 and #8 there will be no problems.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Using THHN wire :
#10 ampacity = 40 amps 4-6 wires - 80% derating 80% ampacity = 32 amps you require (5000/220)*125%( amps #10s on a 30 amp breaker is ok. Use a #10 ground
#6 = 75 amps 80% ampacity = 60 amps you require 54 * 125% = 68 amps - - 70 amp breaker so use #4 - good for 95*.8vamps #4s on a 70 amp breaker. Use a #8 ground
A 1 inch conduit is all you will need. Just make sure you use THHN.
RE

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
#10 may carry 40a however, 90 degree Celsius terminals do not exist.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

The terminals are not in the conduit he is derating
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
What kind of dork uses #10 for a 40a load?
wrote:

The terminals are not in the conduit he is derating
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| What kind of dork uses #10 for a 40a load?
A pyromaniac?
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
You didn't read the question. The 40a was referring to derating, the load was 5kw or 20.8a
wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Hey greg...my reply was to sqlit. Thanks for your useless interjection.
wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
so, what you're saying is:
Does the NEC allow for 2 #10 wires and 2 #6 in a 1 conduit ? that's rather obvious., unless you want to run an additional in conduit for the fun of it...
I could tell you how many #6's and how many #10's you can use in 1 rigid conduit but that would take all the fun out of it, now would it ? };-)
you're work is done ~>