Grounded neutral in an old sub-panel

The existing (old) sub-panel is fed by 2 phases and an uninsulated neutral conductor. There is no ground bus, return conductor to the service entrance,
nor connection to a ground rod. The conductors are in conduit when leaving the main panel and arriving at the sub-panel, but not in between (they're stapled to the flat roof under the roof's insulation & paper).
I want to replace the sub-panel with a modern one with safe breakers and add a ground conductor, which will be run via another route (I want to keep the project manageable, so don't want to run new conductors).
Since the neutral conductor is uninsulated, it is in contact with the sub-panel (it is in the conduit bringing the feed conductors into the sub-panel). In a sub-panel the neutral and ground are not supposed to be connected.
My question is this: How do I install this new sub-panel and new ground conductor such that the neutral and ground are separate?
JJ
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The short answer is no. Run a new feeder. You can't run a neutral separate from the hot leads and you can't use the bare wire in your existing cable for a neutral.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@aol.com snipped-for-privacy@aol.com posted to sci.electronics.design:

This is not a new installation , it is a modification.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| snipped-for-privacy@aol.com snipped-for-privacy@aol.com posted to sci.electronics.design: |
|> wrote: |> |>>The existing (old) sub-panel is fed by 2 phases and an uninsulated |>>neutral conductor. There is no ground bus, return conductor to the |>>service entrance, nor connection to a ground rod. The conductors are |>>in conduit when leaving the main panel and arriving at the |>>sub-panel, but not in between (they're stapled to the flat roof |>>under the roof's insulation & paper). |>> |>>I want to replace the sub-panel with a modern one with safe breakers |>>and add a ground conductor, which will be run via another route (I |>>want to keep the project manageable, so don't want to run new |>>conductors). |>> |>>Since the neutral conductor is uninsulated, it is in contact with |>>the sub-panel (it is in the conduit bringing the feed conductors |>>into the sub-panel). In a sub-panel the neutral and ground are not |>>supposed to be connected. |>> |>>My question is this: |>>How do I install this new sub-panel and new ground conductor such |>>that the neutral and ground are separate? |>> |>>JJ |> |> The short answer is no. Run a new feeder. |> You can't run a neutral separate from the hot leads and you can't |> use the bare wire in your existing cable for a neutral. | | This is not a new installation , it is a modification.
However, if a new wire is run, it becomes an installation subject to the current code. At the very least, that new wire itself is considered and one wire alone doesn't meet code. If you get to elect to include the other wires then they all together have to meet the code for the new wire to be considered compliant. Actually, you don't get to elect that if the other wires are part of the circuit of the new wire. So if you do this kind of work, the whole thing must meet current code.
If a new wire is not run, but a new sub panel is added, that sub panel must meet code. It must be fed with a feeder that is correct for the type of ciruit or electrical system involved. In the case of the OP's wiring, it _appears_ to be suitable for _only_ circuits that are 240V only. Connecting a neutral wire of a branch circuit to that uninsulated feeder wire would make the sub panel itself non-compliant with current code. Only the 240V circuits would have a chance to comply because they have no neutral that needs to be connected (AFCI and GFCI protected circuits would not be able to be operated unless their operation can be done on 240V but such devices are not currently manufactured as far as I know).
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hire an electrician.
Chances are if the neutural are gounded, you'd have a hard time dismantling the old one without feeling the buzz.
If you're going to do it yourself anyway, you'll need to run another wire to connect ground to something grounded, check your local regulation for proper ground rod or hookup. Also replace the old neutural wire with those that are insulated.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Holy smoke!
I *hope* you mean on the *interior* side of that flat roof...

That's a Code violation. The ground conductor is required to be run in the same cable or raceway as the circuit conductors.

By installing a new feeder, with three insulated conductors of the proper size. IN CONDUIT THE WHOLE WAY. If you use metal conduit securely bonded to the boxes at both ends, Code allows the conduit itself to be the equipment grounding conductor. Otherwise, you'll need to run a fourth conductor for equipment ground.
Also, make sure that the feeder is protected by an appropriately-sized breaker in the main panel (not taken directly off the hot lugs of the main breaker, as so many DIYidiots seem to be fond of doing).
--
Regards,
Doug Miller (alphageek at milmac dot com)
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

the

NEC requires ground to be in the conduit with the feeds? Rats! The roof is new and while I am experienced with electrics, I don't want to puncture that expensive new roof for conduit & conductors, unless there's no other way...

breaker,

Breaker already exists in the (1980's vintage) service-entrance panel for the sub-panel feeds.
JJ
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yep. There is an exception for retrofitting a ground wire on a branch circuit to provide a ground for 3-prong receptacles, but it doesn't apply to your situation.

Abandon the existing feeder in place, and run a new one on the inside of the roof.
--
Regards,
Doug Miller (alphageek at milmac dot com)
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Doug Miller snipped-for-privacy@milmac.com posted to sci.electronics.design:

Hmmm. That abandon has different meanings in different jurisdictions. Get a local electrical contractor to check the local variation for you.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Doug Miller snipped-for-privacy@milmac.com posted to sci.electronics.design:

For new installations. For modifications it is a bit more complex.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

You are kidding, right? Run, run away fast... Totally replace the existing setup, get those wires off the roof!

The current system is a hazard, and needs full replacement. If you touch it, do it right. If you don't do it right, and later there's an accident (and there *will* be) you will be held responsible.

No, that is not an neutral conductor. It is a ground conductor.

Install it according to code. There is no other alternative. That includes getting that non-code, hazardous, existing wiring under the roofing removed, and replaced with soemthing that meets code.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
OK, since it looks like going up on the roof is the current :-) solution...
This provides 2 possibilities for the conduit: 1) run supply feeds (2 hots + neutral + ground) to the sub-panel or 2) gut the sub-panel and use it as a junction box; run circuit conductors from the junction box back to the service-entrance panel (which contains the main disconnect, sub-panel disconnect, and breaker for the air-conditioning unit) where there are busses and spaces for more breakers.
What do y'all think the best option is?
In either case, through and over the roof with conduit. This means exposed to the desert weather (winter, sometimes to freezing; spring & fall, rain; summer, 140 F degrees - but its a *dry* heat :-).
What size and type of conduit and conductor should I use for: 1) supplying a 100A sub-panel? Individual conductors or SE? or 2) connecting the 10 individual circuits back to the SE panel? Itemized list of conductors for this option? Can I use one large neutral conductor? (7 fifteen amp circuits, 1 twenty amp, 1 two-pole thirty amp circuit (4-wire for dryer)).
JJ
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Look, it is clear you are in over you head on this project. Get a qualified electrican to do the job, and they will both do the job right, and you'll be happier.
Asking 'what size conduit' is a very basic question, and if you can't figure that out then the rest of the job is probalby going ot be just as difficult, and you are likely to make mistakes that will later come and haunt (or kill) you.
A sub-panel works. Size of conduit is based on size of wire. Size of wire is based on current loads and breakers.
You must have a hot, neutral and ground for *each* circuit when you have multiple circuits. You cannot combind these as you are suggesting.
Your box is going to be holding about 150 amps of breakers. How far between it and the main box? You are talking 0 AWG wire probably, maybe something larger if the distance is great.
This is not a trivial problem or project. Please get professional help.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Incorrect. Shared neutral circuits are permitted by Code (although not seven circuits sharing one neutral). There is also no Code requirement for separate grounding conductors for multiple circuits in the same conduit.

Unless all of those circuits will be in use at one time, there's no need for either the box or the feeder to be rated at the sum of the individual branch circuits. 100A over AWG3 wire should be just fine.
--
Regards,
Doug Miller (alphageek at milmac dot com)
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
PeterD wrote:

JoJo, please listen to the advice above. I like hacking at things that I have never done before too, but this isn't the place for it.
--
Guy Macon
<http://www.guymacon.com/
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

As noted in my first post, metal conduit is an acceptable equipment grounding conductor if properly installed.

Why?
You'll be running smaller conductors, but a whole lot more of them. What's the point?

The first one, hands down.

Why not under the roof? Why is it necessary to pierce the roof?

AWG3 copper or larger, with insulation rated at least 75 deg C, in 1-1/4" or larger conduit. Individual conductors will be easier to pull than an SE cable. Use wire-pulling lube, too -- it makes the job *much* easier. So does larger conduit. I'd use 1-1/2" or maybe even 2".

Why would you even consider doing that?
--
Regards,
Doug Miller (alphageek at milmac dot com)
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks, Doug, for your comments.

Flat roof. This is an "exposed beam" ceiling with tongue-and-groove slats lying on those; there is no attic. Directly on top of the ceiling are 2x6 lumber. On top of that is (probably) plywood, with paper roofing over that. Then sky. This raised portion of the roof provides a sort-of utility space. To run conduit via the roof (either over or under the outermost surface) means puncturing it somewhere.
I've abandoned the idea of running over or through the roof space. The sub-panel is in the laundry area near an outside wall, so I plan to run the conduit through that wall and around the house under the eaves. Being a flat roof, the eaves are equal on all sides which will provide weather protection all the way to the SE panel.

So, minimum 1-1/4 inch conduit, AWG#3 conductors (2 phases, neutral) = 100 amps (the rating of the new sub-panel). The ground conductor can be #8, right?
Since there are going to be 4 wires in the conduit, do I need to derate them? Derating only applies with more than 3 conductors? Does the ground conductor count?
Total cable run (horiz & vert) ~50 ft.
Can EMT be used in this application (with weathertight fittings)? Under the eaves it will be out of the sun and direct rainfall.

It was suggested by a retired electrician. Puts all breakers in one place, albeit outside... Consider the idea abandoned.
JJ
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Perhaps you could attach conduit to the underside of the beams?

That'll work.

Right.
Derating applies with more than three current-carrying conductors, which INcludes the neutral but EXcludes the ground.

Yes.
Waaaaaaaay too much work IMO.
--
Regards,
Doug Miller (alphageek at milmac dot com)
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Doug Miller wrote:

A true neutral - that carries only the unbalanced current of the 2 phase conductors in this case - does not count. If there is a 60A load in any combination between A-B, A-N, B-N there will only be 60A 'going' and 60A 'returning'.
--
bud--

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

That is not correct. Any current-carrying conductor must be counted.
--
Regards,
Doug Miller (alphageek at milmac dot com)