Subpanel bonding (3-phase mains) question

Is it never allowed (US National Electrical Code) to bond the ground bus bar
to the neutral bus bar?
I opened a subpanel and found that both the ground bus bar and cabinet were
bonded to the neutral bus bar.
Is this allowed under any circumstance?
This is a "Y" 208/120 configuration utilizing 5 conductors in an industrial
building.
Thanks.
Reply to
Mike Cook
Loading thread data ...
Is it never allowed (US National Electrical Code) to bond the ground bus bar to the neutral bus bar?
I opened a subpanel and found that both the ground bus bar and cabinet were bonded to the neutral bus bar.
Is this allowed under any circumstance?
This is a "Y" 208/120 configuration utilizing 5 conductors in an industrial building.
Thanks.
Reply to
notme
No, according to the NEC it is not allowed in a subpanel at all.
Reply to
Rich.
No. As long as it is a sub-panel. Not to be confused with a seperately-derived system(after a transformer).
RE
Reply to
Ryan Evans
With the exception of feeders to separate buildings under previous editions of the US NEC it is not permissible. -- Tom Horne
Reply to
Tom Horne
Single building, not large (2000 sq ft?) one service entrance, one main panel, 3 or 4 subpanels.
It looks like this bond needs to be broken...
Thanks, Mike (OP)
Reply to
Mike Cook
When you say 'sub-panel', it may be confusing. A step-down transformer fed from the service entrance, that in turn feeds 208/120 to a panel is not a sub-panel. In that case the first panel off the transformer is not a usual 'sub-panel' but a fed from a separately derived source (the transformer).
You mentioned 208/120 in an 'industrial building', so I think the building service is not 208/120 directly but may be a higher voltage and you have a step-down transformer inside the building.
In that case, the ground/neutral *should* be bonded in the first panel after the transformer.
Now, any other panels fed from the first panel after the step-down transformer are true 'sub-panels' and thus should not have the ground and neutral bonded.
So just to be clear here, are you talking about a true 'sub-panel', or the first panel downstream of a step-down transformer?
daestrom
Reply to
daestrom