Transformer

480 (delta) -to- 208 (wye) transformer being used for step-up purpose (rather than step-down).

Is it mandatory to use neutral in the wye hook-up?

Grounding is provided by same-size conductors as the phase cables.

No flames, please. It's a sincere question.

Thanks, Sparky

Reply to
SparkyGuy
Loading thread data ...

If there are 3 transformers connected wye the neutral is required or else the neutral point will float and the voltage across the 3 transformers will be different depending on the secondary load.

(If there are 2 transformers - Scott or T connection - I don't think you need the neutral.)

The secondary system will be ungrounded?

-- bud--

Reply to
Bud--

Bud sez:

It's a single 3-phase transformer labeled for use as 480 (delta) -to- 208 (wye) step-down. Which, reading your statement above, means that phase voltages will be different in the primary and secondary depending on loading. Yes?

Common ground between supply and load, at the transformer chassis.

Sparky

Reply to
SparkyGuy

Grounding of the neutral is preferred for safety, and it prevents non-symmetrical loading of one phase from shifting the voltage and phase of the others.

Reply to
Robert Baer

Be aware that doing this results in a wye-delta transformer configuration. This has a problem that if you lose a phase, the transformer will try to power the lost phase from the other two. Therefore, expect the breaker to pop whenever you lose a phase, when it attempts to backfeed the local grid.

On the other hand, if you don't connect the wye common point to the neutral, it won't do this. Even if the load on the delta side is unbalanced, the configuration won't try to generate any neutral current, it happens to work out. You'll still have single phasing, of course.

But before you do this, run it by someone with more knowledge of these things than myself, as well as whether code allows this. I do know that a local electric company does this when powering an old segment of delta-connected distribution system from a higher voltage wye system. The common connection of the primarys don't connect to the neutral.

Reply to
Michael Moroney

Neutral on the wye is mandatory. There is no neutral on the delta side. Each delta phase is feed from two of the hots. Instead of having three power circuits like AN, BN, CN, you get AB, BC, CA. If you tie any delta phase to ground you will be chasing voltages on the grounds.

Donald

Reply to
Donald Kinney

WELL BY PROVIDING THE NEUTRAL ON THE STAR POINT,WE CAN REMOVE THE 3RD HARMONICS .THE THIRD HARMONICS IF NOT GROUNDED COULD RESULT IN HEAVY CURRENT FLOW THAT CAN DAMAGE THE TRANSFORMER WINDINGS AND MAY ALSO TRIP THE WHOLE POWER SYSTEM

Reply to
dukeadil_007

If the transformer has 3 sets of coils I'm going to change my answer. I think the connection on the delta side would force the voltages on the wye side to be substantially equal. I think the voltages on the delta side would be a little closer to equal with a connected neutral and losses would be lower since the delta side is not forcing a balance on the wye side. Anyone with a better theory?

Particularly some small 3 phase transformer units are made with 2 sets of coils with a Scott/T connection which could be connected without a neutral.

The transformer 480V delta side would be ungrounded unless you "corner" ground one of the phases.

-- bud--

Reply to
Bud--

Not always, local regulations vary. It is, however, customary and typical. It has advantages as other responders have noted.

That is fine, always works OK and is always legal if all leads are of sufficient size.

Reply to
joseph2k

I think that is correct. Any 3-phase transformer with a delta on one side (pri or sec) has the benefit that the delta winding internally circulates third harmonic currents and balances the wye-side so that the neutral is reasonably stable. This means that the star point may or may not be earthed and, (if it is), does not require a heavy gauge connection. It also means that a wye-connected secondary allows a 4-wire supply that can have simultaneous balanced and unbalanced loads without much penalty.

Contrast that with a wye-wye transformer, where the neutrals can be very unstable, requiring heavy gauge neutral wiring.

In the UK the delta-wye is the standard 11KV 3-wire to 240V (line-neutral) 4-wire configuration for domestic and industrial distribution.