WireGuide 2005 sells for $199 and is sold by Vision Infosoft. I found several problems with their program. I downloaded the trial version to check it out against my own program written in JavaScript. I found these problems so far.
WireGuide 2005 Service/Feeder Calculations
- 20 ampere and 9 conductors input lists No. 12, rated 14 amperes on
- 25 ampere and 3 conductors input lists No. 12, rated 25 amperes on
- 31 ampere and 6 conductors input lists No. 10 rated 24 amperes on 35 ampere OCPD
- Only 75 degree C. insulation and terminal temperatures supported. (derating using 90 degree insulation ampacities is not allowed but is a common practice)
- No provisions for continuous load and noncontinuous load inputs.
- Only copper donductors are supported.
In my opinion, WireGuide 2005 is not NEC compliant and a warning should be attached to let users know.