I just spent 20 minutes looking on the web for information about cable and breaker size, and finished more confused than I started.
My existing installation for my Synchrowave 180 welder (metal content) is a fifty amp two-pole (220 breaker) with 40 feet of 8 ga wire, in my garage. The circuit is dedicated to the welder. The Synchrowave is a TIG/stick welder. The manual for the welder recommended 8 ga wire. I noticed at Home depot that they only show 40 amps for 8 ga wire. When I started looking on the web, I saw that the maximum current for 8 ga wire varied quite a bit depending on which table that I looked at! On some tables, 50 amps is OK on 8 ga wire, but other tables say 40 amps. I think that I even found some tables with 60 amps for 8 ga wire. I have also seen references to it being permissible to increase breaker size for welders and motors.
I know that somebody is going to tell me that I should install size 2 wire with a 40 amp breaker, but my goal is to comply with code, and avoid ripping out installations that do not violate code.
So what is the applicable rule, table, and why?
Can I run my welder on a 40 amp breaker?
The reason this question has come up is that I want to put a 220V compressor on the same circuit as the welder, but now I am having second thoughts about the existing installation, let alone adding something to that circuit. Since I am out of space in my breaker panel, adding a separate circuit for the compressor is impractical.
Richard