phase converters

I realize the extent of my confusion about phase converters. I thought that phase converters were motors/generators coupled on one shaft. It
turns out that they are some complicated combinations of capacitors.
I am curious why phase converters are not made as motor/generators.
i
--


Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

There are different types of phase converters.
A static phase converter is just a couple caps and probably a relay that allows a 3 phase motor to start and run off of 2 windings. It does not develop full power (about 2/3) but is still useful.
A rotary phase converter is basically a 3 phase motor running off of single phase power. It will regenerate the third phase well enough to run a smaller 3 phase motor pretty well. Commercial products use a custom wound motor that works a little better than a standard 3 phase motor (so I'm told).
Phase converters are not made from motor generators because it is expensive and not necessary unless you have a unique application such as a need to generate 50 Hz from 60 Hz.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Chuck
Although I dont mean to correct you about the 2/3 power statement, most 3 phase motors will develop its full name plate HP even when fed single phase. They will slow to a lower RPM than the name plate RPM rating, and get hotter, quicker with single phase than with 3 phase. It is interesting to me to learn that an idler of equal size of the tool motor provides very little MAX. HP performance compared to no idler at all when fed from single phase. The HP from a 3 phase motor driven from single phase without an idler will perform very nearly the same at that same tool motor driven thru an "equal size" idler up to about 60 percent of MAX. HP name plate on the tool motor.
Maybe thats where the 2/3 HP figure comes from. Idlers and tuning do help the tool motor measurably when the 3 phaes tool motor is heavily loaded.
Jerry

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I think I read that on the phase a matic web site but I could be wrong. I always thought it was related to the fact that the the motor is running on only 2 out of its three windings. At 2/3 rate HP, the two working windings will be drawing full rated current. Anything over 2/3 would imply that the 2 working windings must draw more that full load current. Based on this logic, I accept the 2/3 rating

Wouldn't that imply that it might be operating outside of safe limits?

From what limited testing I have done, I agree that an idler motor does not apear to do much until the tool motor is at a higher slip than the idler motor. There was a guy on here that stated his surface grinder did not work perfectly with a rotary phase converter and worked much better with a VFD. This appears to support this conclusion.
One thing that a RPC does do is provide instant reverse that you cannot get with it.
Frankly I decided not to get two wrapped up in phase converters because I prefer VFDs.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Would it be correct that all these phase converters that are not based on motor/generators, are unable to run more than one 3 phase device at a time. The reason for this suspicion is that they seem to do something wholly different when a motor starts, than what they do when it runs.
So, with such a 1 phase converter, I cannot have a compressor and a mill.
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

That is not correct. Rotary phase converters are often used to run multiple machines. One at a time or even more that one at a time.
Do a web search for "phase a matic" and read all about it.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    Agreed -- but he said "*not* based on motor/generators", which I think he intended to also exclude idlers used as rotary phase converters. The idler motor is serving both as a motor and a generator at the same time.
    "Static" phase converters ("Phase-o-Matic" is an example) are not only limited to running one thing at a time, but are also designed for a fairly narrow range of load motor horsepower. If you need to start a 1HP motor, and a 2-1/2 HP motor, the odds are that you can't even switch the converter from one load to the other to run one at a time, because the starting capacitor value will be wrong for at least one of them.
    "Rotary" phase converters, build around an idler motor, can not only run more than one load motor at a time, but can even handle more load horsepower when doing so, because each load motor already running off of it contributes to the "rotary converter" effect. So, if you have a 1HP motor on your lathe, and a 1-1/2 HP motor acting as your idler, you have a greater chance of starting another machine whose motor is perhaps a 2HP rating if the lathe motor is already running.

    Yes, that will help. Note that "Phase-o-Matic" makes both static converters and rotary converters. (And a static converter can actually serve as the starting equipment on an idler for your own rotary converter.)
    Enjoy,         DoN.
--
Email: < snipped-for-privacy@d-and-d.com> | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I did not mean to exclude idlers. At the time when I asked my question, I did not understand the role of idler. Now I do understand its role, thanks to Jim Rozen's pictures.

Would it be also correct to say that after the phase converter started the 3 phase motor, the third leg can be turned off?
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
    [ ... ]

    Only if you want to have the lowered long-term horsepower out of the motor that running it from a "static" phase converter would give you.
    There is little point to doing this, and lots of reasons to *not* do this.
    The *start* capacitors are removed from the idler motor once it is up to speed. This can be done for you by a "static" converter, if you already have one, or don't want to chase down the parts needed to build the starting circuit.
    For better efficiency, you may want to use run capacitors between L1 and the generated phase, and/or L2 and the generated phase.
    For lower current from the breaker (real + imaginary current), you may wish to add capacitors across L1 and L2, adjusting the value until the current from the breaker is at a minimum. On a residential system, you are not charged for the imaginary current, but it can cause nuisance trips of the circuit breaker, which can't distinguish between "real" and "imaginary" current.
    But both of these are fancy tweaks, and you can run without them, just as you can run without a start capacitor if you use a single phase "pony motor" to spin up the idler.
    If *I* were to build a rotary converter, it would be self-starting, and would have both run capacitors and the current-reduction capacitor.
    Enjoy,         DoN.
--
Email: < snipped-for-privacy@d-and-d.com> | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Iggy sez: Would it be also correct to say that after the phase converter started

Static phase converters, i.e. Phase-a-Matic, etc, only energize the 3rd leg during start-up time. After that brief interval, the static phase converter effectively switches "off" (back to a standby mode) and your 3-phase motor continues to run on single-phase power. No 3-phase "power" is available from a static converter except for starting purposes. This takes advantage of the fact that a 3-phase motor will continue to run on single-phase "power" after the motor is spun-up via auxiliary means, be that a rope, start capacitors, large hamster, etc.
IMO, if you made the effort to learn a bit about RPCs before trying to jump in and build one, you'd find most of the "mystique" would fade away. You'd be left with the confidence and good warm fuzzy feeling of being in command of your project. There is a wealth of information re. RPCs on the Internet. If you can find a copy of "The Home Shop Machinist", Nov./Dec. 2000, it has a pretty comprehensive article about RPCs.
Bob Swinney
wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks Bob. I like the idea of building a homemade RPC, because it is likely not going to cost too much (if I can find a suitable 3 phase motor, which should be possible), and it is not going to take up too much space.
i

--


Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Correction: Make that Nov/Dec 2001 Home Shop Machinist. Damned proof reader, anyway!
Bob Swinney
wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
and-d.com says...

phase-A-matic ( -a- rather than -o- )

They're limited to *starting* one load at a time. Once you have one motor running it (and every subsequent motor) acts like a rotary converter allowing you to start another motor, up to the capacity of the branch circuit.

I think most phase-A-matics have a 2:1 range, 3/4 to 1-1/2 HP, for example. You can get around this by creative use of the motors in other machines as RPCs as mentioned above. Not convenient, but will work in a pinch to get something going that the static converter won't otherwise start. One very important thing to note is that you should never connect anything with sensitive electronics to the leg being generated by a static converter. There are likely to be spikes present on that leg that may damage solid state controls, etc.
Ned Simmons
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks to all. I have another question. For a phase converter motor, how important is the RPM? I am a little puzzled that 3 phase motors have different RPMs, 1740, 1750, 1800, 1760 etc. I cannot understand how it can be with 60 HZ incoming power.
In any case, with a motor that is not spinning at exactly 1800 RPM, how would the third leg agree with the incoming 60 Hz frequency? I am quite confused.
Do I need a motor that is rated for precisely 1800 rpm, or can I get away with a 1760 RPM motor?
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I
I suspect that you arent actually "confused". Perhaps you dont yet have enough information to show you what the induction motors do and how they work. If you want to get involved with studying the theory of electric motors, there are alot of good books and web sites that have all the information on these 3 phase motors. If you want to build a RPC so you can have decent 3 phase available in your shop, I'd suggest that you get Bob Swinney to send you a copy of his writings.
Note: The 3 phase motors commonly being referred to here in RCM are induction motors. They necessarily run at an RPM slightly lower than the synchronous RPM which is determined by the number of poles in the motor's construction. By far, the most common 3 phase motor used to power machine tools is the "1750". Actually the name plate RPM indicates the RPM to which the "1800 RPM" falls when the motor is fully loaded to its name plate HP. An unloaded 1750 3 phase motor will spin at close to 1798 RPM, depending on its static load from the fan and bearing load. The motor's RPM will gradually drop to the name plate RPM when it is loaded to its name plate HP.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I would agree with that.

Is that the article on metalwebnews?

Oh, now I understand a little better. That makes full sense to me. I'll continue reading, for now.
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Iggy sez:
" ..... > Is that the article on metalwebnews? ...."
I suspect you are referring to Jim Hanrahan's excellent article, most generously contributed to the Internet several years ago. While the article is "classic" in every sense of the word, I would not recommend it as a "first read" on RPCs unless you already have some background in the subject. Hanrahan's article describes 'self-starting' rotary phase converters, although it fails to make the distinction between "self-starting" and the balanced type more commonly used in the home shop. The "self-starter" has no auxiliary, "start caps", relying instead on gross amounts of single-legged run capacitance.
The self-starting RPC is inherently an "unbalanced" device. "Self-starting" works against the object of achieving any sort of balance among voltages of the 3 phases. Self-starting is achieved through the use of excessive amounts of "run capacitance"; enough that if some means of switching out isn't employed, the RPC will be drastically out of voltage balance and incapable of delivering nearly perfect 3-phase power.
RCM's own Fitch Williams ran many posts a few years ago on voltage balanced RPCs. IMO, Fitch gets all the accolades, credit, and all kudos for waking up the home shop crowd to the advantages of the auxiliary-started, voltage balanced RPC. If I had a drink at the moment, it would be raised to Fitch.
Thanks, to Jerry Martes for recommending my writings, but I've just about given all of them out short of enlisting attention of the copyright police!
Best regards to all,
Bob Swinney
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Thank you. I am reading an article at http://home.att.net/~waterfront-woods /, if you have any other suggestions, I will appreciate. I found some posts by Fitch to rec.crafts.metalworking, as well, and will soon look at them.
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Someone wants $100 for a [supposedly] nice condition used 10 horse motor... It is not exactly very cheap, but I can have it right now...
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Its a time/money/hassel trade off. Lost creek machine in Ottawa, IL sells used 3ph motors for $10 per HP. Same price so its not out of site, but not cheap either.
Something to think about: You will need start and run caps. The bigger your idler motor, the more caps you will need. If you are buying the caps new, you might incure more cost for the caps than your motor. I recommend that you figure out what you need before you buy parts because you will spend more to build a 10HP converter than a 5HP converter.