Calculating value of C for a known value of L @ 60 Hz. to correct Power Factor

Apr 09, 2004 3 Replies

Anyone know a formula to calculate the Farad value of a power factor correction capacitor for a single phase 60 Hz. pure L inductive load, knowing the H inductance? I would think Xc = Xl, but not sure.



Thanks


Work in complex numbers. Imaginary (reactive) components have to cancel exactly.

Have a heart Walter, the questioner' skills are probably elsewhere than in complex numbers, and that's alright.

The answer is, a chat with a friendly electrical engineer who would pose questions about the fiction of a pure inductance load.(infinite impedance at total PF correction) He would also need to give a little circuit theory lecture.

For a power factor lesson look at:

formatting link
and go to tutorial 25.

Art

If the load really is essentially all L, then you probably want to stay away from full compensation. You could incur dangerously high voltages &/or currents, and if the inductance is subject to saturation, troublesome hysteresis effects.

Join the Discussion