Power Factor and New Power Company Digi Meters

Should I worry about this .
Does anyone here, have reason to doubt if these things, "correct"... for power factor .
My "units used" seems to have gone up since this meter was swapped from the old mechanical one.
All the best.....mark
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Whether or not they correct for power factor I don't know, but I suspect they are just a lot more sensitive to low currents. Our old mechanical one would not noticeably rotate even with things like VCR on standby and the bell transformer drawing current. I suspect the new one sees everything. Haven't attempted to calculate how much extra that would be.
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Both old and new measure true power, though there are moves afoot to meter kVAr's as well because of the increasingly bad power factors of modern loads. Industrially they already meter kVAr's but the technology to do it domestically was too expensive, not any more. Greg
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Greg wrote:

I ask all this because I'm in dispute with power company (BRITISH GAS) over this
suddenly having power bills of £300
when average before digi meter was under £170 ish
used the lathe yesterday for one hour ...it's on a rotary converter.
lathe is 2 hp converter is rated at 5.5 hp
20 units used in 24 hours according to the new meter. didn't do any cooking ...only TV and lights, computer and lathe used in the 24 hours.
All i ask people to do is ...check their digital meter when operating things with windings etc .
Just so that I've got something to back up me up when on the phone to them.
all the best...mark
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

My consumption certainly appeared to rise after the meter was changed.
Tim Dutton Dry-Dock Traditional & Modern canal craft repairs Vintage diesel engine service
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
mark wrote:

OK they have just been on the phone to me ...in the last few mins
It now seems that I've used 27 units since 12.30 yesterday ...'till 3 pm todays .
Guy on the phone agreeing that the domestic unit may not compensate for power factor .
Got to take regular readings now for the next 7 days .
Then they will delve deeper.
Urge everyone with these digi meters to look carefully at the power consumed when using equipment /tools etc with windings .
and report back here .
all the best.mark
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
mark wrote:

I've just measured the units used over a two hour period.
The converter was switched on and I was machining plastic...making an interface for an LPG conversion ...for the pipe to pass thru the floor of my car .
Over a two hour period I used 11 units
This cant be right......that's over 5500 watts draw.
If I was using that much, it would be so hot in the workshop It would be like having 5 1/2, one bar electric fires switched on .
The workshop wasn't hot !
This just cant be right. :(
All the best...mark
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

"correct"...
swapped from

meter
modern
do it

I ask all this because I'm in dispute with power company (BRITISH GAS) over this
suddenly having power bills of £300
when average before digi meter was under £170 ish
used the lathe yesterday for one hour ...it's on a rotary converter.
lathe is 2 hp converter is rated at 5.5 hp
20 units used in 24 hours according to the new meter. didn't do any cooking ...only TV and lights, computer and lathe used in the 24 hours.
All i ask people to do is ...check their digital meter when operating things with windings etc .
Just so that I've got something to back up me up when on the phone to them.
all the best...mark
I have a secondary meter so that I could check if I wished. This is an old pre-payment meter that has had the coin box removed and trivial electronics added to generate an opto-isolated pulse every rev of the disk which triggers an interupt on my energy monitoring software. I display three bargraphs of power consumed : a/ per minute for the last 60 minutes. b/ per hour for the last 24 hours and c/ per day for the last 31 days. I also monitor water consumption on the same system and when I wrote the software made provision for gas consumption but haven't found an easy or safe method of metering the gas so its display just mimics the electricity ! Gets a bit alarming when I've been running my new 15KW converter for a bit - whacking great graphics bars sticking out of a low field !!!
AWEM
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Biggest problem I had was that they billed us based on estimates for two years. The estimates were substantially less than the meter readings would have been. I didn't notice it because the domestic management dealt with the bills... A £700 pound electric bill after they did finally read the meter was a bit of a shock.
Mark Rand RTFM
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

used in

operating
to
two
would
with the

meter was

...pah you think you have problems !!! ..... I've just paid Powergen £2,900 for gas as we've been on estimated readings at one of my shops for the past year.
AWEM
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 29 Sep 2006 17:57:42 +0100, Mark Rand

And if the price of electric went up in that 2 years they almost certainly charged you at the new price for the 'old' juice. It's called back-billing and they have been told to stop it but still try it on. Inflated my bill by over £100 but I got it back, took over a year and 2 energywatch referrals but I won!
Sorry for butting in - newby lurking - but this thread got my attention!
Cheers Andy Parker, Agate House Lapidary Ulverston, Cumbria, England snipped-for-privacy@agatehouse.co.uk www.agatehouse.co.uk
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I was with powergen for about two years when I moved into this house. In all that time they didn't manage to send me a single correct bill. Each time I rang someone up they would change it, but by the time it got out to me they would have got it wrong again. Most incompetent company I have ever dealt with. Even when I gave them meter readings they would send out bills with "estimated" figures. But as they had never read the meter there was no accurate data to base the estimate on. Final straw came when they sent me an "estimated" bill that said I'd used several hundred pounds worth of electricity in a week!! And then changed my direct debit to a ridiculous figure based on the estimated bill. I am now with a different power company.
Regards Kevin
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

A typical one measures just kWh, the "technical" manual is available for download here. http://www.econtrols.co.uk/downloads/5196B%20USER%20MANUAL.PDF
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

That one measures both active and reactive power separately, is that what they are installing now?, it would certainly fit with what I've heard about their plans to meter kVAr hours in the future.
But the fact remains they presently bill on active power only, and any meter either mechanical or electronic is supposed to read only active power so the kVAr hours display on that meter should be ignored.
Greg
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Looking closer, that manual covers a range of meters including a kW hour only type for domestic and even an export power for use with grid connected generators, they're obviously thinking ahead to the micro CHP market.
Greg
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Greg wrote:

Thats the exact one I have
but it says in the literature that there are a few different models
I want one that sorts out my lathe and converter so it does not get read as if its using 5500 watts per hour ... my old mechanical meter didn't work like that ...I want it back !!!
if every time I use my lathe for an hour its going to cost me dear ...I'm not going to use them .;..because ...I will end up with bills of £300
in simple terms .. what one model is it .
The one I have now is model number 5235a and is the wrong one for my application
All this reactive stuff etc is over my head
What do I tell the guy on the phone ...
All the best..mark
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 29 Sep 2006 16:58:17 -0700, mark wrote:

If you still power the lathe from a 13 amp socket then take a trip to Maplins and get a plug style power meter.
It will read voltage, current drawn, power factor and watts used including peek load.
Very useful little tool for checking computers etc.
Takes up to 3Kw I think and costs generally less the £24
Adrian
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

You occasionally see these in Lidl (or Aldi ?) for under a tenner the display is rather hard to read but they seem to work OK.
-another adrian
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Adrian Hodgson wrote:

Everything is three phase and powered by a rotary converter.
That is hard wired.
I've had one of those maplins things before ...and it lasted a week before it went faulty.
I had bought it from the catalogue.
I returned it ... They lost it .. or the post lost it.....and would not refund my money.
I have a proper mechanical meter that I picked up from a car-boot this year ...may install it in my workshop and check things out .
All the best....mark
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It's totally up to them what model or make they install, but any MUST meet the legal requirements for metering so if it's not broken it should give you the correct result, within the required 1% anyway.
To try and clarify, any load 'draws' both watts and vars but domestically you are only metered on the watts at present. Any meter will count the watt hours, but some additionally count the var hours, this is in effect a totally separate meter in the same box and should in no way affects the watt hour reading. Any display of var hours can be ignored., they simply shouldn't record the number and you shouldn't worry about it, at least not until they start charging for vars in a few years time.

That you believe their meter is faulty and request that they test it, in response they should either just change it or test it on site.
As others have suggested, you could get some sort of meter to do your own test, either a proper electronic watt hour meter or an old mechanical one, but all this will do is reinforce your view as they're very unlikely to take you seriously with a £24 Maplins job. To put it into perspective, I have a proper power analyser on my bench at work and it cost about £8000 (I design control and metering systems for the power generation industry) .
A couple of points though: Are you sure you're not just reacting to the staggering increase in electricity cost over the last few months? Are you sure that both you and they are reading the right numbers?, don't take offence at this, I had the unbelievable situation that a meter reader swapped the day and night readings around. The fact that this meant one had gone DOWN drastically did not phase them, the Muppet just recorded it as an initial reading so the computer stopped complaining !!!
Remember you are dealing with a Muppet on the phone, the very best you can do is persuade them to press the button that says the customer believes he has a faulty meter, any talk of technicalities is completely pointless.
Greg
Add pictures here
✖
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload