why do you need integral action for level control

Apr 03, 2007 31 Replies

OOPS! MY APOLOGIES TO ALL and to Mr Lu Hing. I must have updated my program since that thread and forgotten that I had done that. We were talking apples and oranges. All of you were correctly looking at what I had referenced and I was looking at the updated version. I should have posted a link to the program I was talking about on my FTP site. I APOLOGIZE , I can see how all of you came up with the conclusions you did and I wasted valuable time.

Please see this site ftp://ftp.deltacompsys.com/public/NG

The .gif and the updated tanklevel.sce is there. It has the disturbances and the better PID control.

Peter Nachtwey

No problem Peter, apologies accepted. We all make mistakes sometimes.

I do want to go back on this thread to pick up the main unresolved point, but first some other points though:

a) First John started it about modelling his tank level control, and this issue has been sorted out, I think.

b) There was a lot of other messages and ideas, but before going back to John's difficult level control that has been side-tracked significantly by Peter's small mistake, maybe first a comment on Fred Thomasson's two cents. I quote from his posting:

I support this tuning method for level control on tanks that are used to steady out the flow; this is typical used on surge vessels and are very applicable in oil refineries where I have done a lot of work. The objective is to keep the outflow as steady as possible, without violating the level limits. So you ensure the proportional control action will "catch" the maximum allowable error, caused by an inflow disturbance, using the smallest amount of control effort. And then you calculate the integral action for critical damped response to bring the level back to setpoint again. So your tuning method starts from, not a given time response, but a maximum allowable level variation (ALV).

This concept (albeit in a slight different format), was first explained to me by a Shell process control engineer, Fatolla Azodi, more than 15 years ago, so I think it's safe to say that this method is reasonably well established in industry and it works well.

c) Then there is John's difficult tank level where we were somewhat side-tracked. Let me quote him again:

...

I have worked on a number of similar "difficult" level control applications too. Although Peter's model coefficients that he used (in the very nice Scilab level control models, thanks Peter) is very typical of many tank levels in industry, it does not capture the essence of this specific problem of John's. In a most tank level control, like Peter's, you can use relatively very strong control action without stability problems. Peter's example of his best tuning is a case in point. It's a good desk top exercise to demonstrate the concept, but you would not really implement strong control action like this on a chemical plant. But let's return to John's difficult level control application: In all the "difficult" level controls, similar to John's, that I have come across, the relative magnitudes of the tank capacity and apparent dead time of the actuator response is such that the control system becomes unstable and force you to use weaker control settings, with the result that level deviation on an inflow disturbance is sometimes too large to prevent level trips.

Let me side-track a bit: now this type of application would be suitable for Peter's derivative control; there's nothing like derivative control to allow stronger proportional control action without the loop going unstable. But .. I would be very careful in using derivative for level control. The little waves on the liquid surface that Peter referred to in one if his postings get amplified by the derivative action, so it's not always a good idea. I say "not always", if you can not "catch" the level from tripping, you might want to consider derivative action. Some DCSs (I know ABB's has), PID algorithm let you filter the derivative only, making it less risky using derivative of course.

So let's stay with PI only for now (but keeping derivative for plan B of course). For John's application, it would be valid to say that to use proportional control only (well, you would have a tiny bit of integral of course, but for all practical purposes you can say it is proportional only), is the best fit for this purpose. Now the question is of course: how do you find the proportional gain. Well, there is more than one way to skin a cat. There are people, like Peter, who seem to have a very strong dislike of iterative tuning, so you can model your process and use desk-top tools, nothing wrong with that at all.

Or you can simply use on-line iterative tuning.

If P-only does not work, then try derivative, you would still use very little Integral, so it would almost become a PD-controller, or feed- forward on inflow.

It's up to you and your tank level now my friend, good luck.

Please keep us updated on your progress on this one.

Regards Pieter Steenekamp

I have a NG ( news group ) directory on my FTP site where I will put files so we are all talking about the same thing. That way this will not happen gain.

Yes, over damped is good too if you don't want over shoot. I was mainly objecting to P only control with gains at -9200.

I will check that out. I don't normally deal with models like K/s so I don't have a lot of pre made examples I can modify. That is why I haven't responded. It takes time.

In this simple model the Kp is the product of the Kt and Kp in the Scilab model. Why can't you calculate this?

I will check this out.

If you have the model you can calculate the error. In the original problem on

formatting link
the mellow tuning was enough.

It is hard to know exactly why this happens but I suspect that it is improper tuning coupled with a poor implementation of the integrator. In my tanklevel.sce the worst case occurs if the last in_flow is set to

  1. In this case the integrator must wind down and during this time the level keeps going down.

The stronger integrator gain means that it should unwind faster too.

If you were using a Rockwell PLC I was tell you to get a trend.. These are very informative. Plot the SP PV and CO.

Doesn't the pump goo off while the level is low?

So can you graph this event?

I hope not. If you notice the pump will stop pretty quickly when the in_flow drops.

I don't think original control with Tc = .25 is very strong. If the Tc is changed to 3*Tp then the derivative gain isn't required.

If you are using a control valve to control the out flow then that is a WHOLE different problem. The valve probably is non-linear and the flow through it isn't linear as it changes as a function of the pressure drop. I don't see where there would be a dead time in a simpler application like tanklevel.sce example.

I was wondering when someone would call me on that. There are cures for that ranging from a simple low pass filter on up. Since PLCs can do anymore than the low pass filter technique I think I will limit the tricks to that, for now.

I say "not always", if you can not "catch" the

SIGreg's application on plcs.net requires a derivative gain most of the time because it has two poles. One for the tank integrator and one for the pump time constant. Each system must be evaluated on a case by case basis. A simple Kp/s plant shouldn't require an derivative gain.

Yes, it is a standard feature.

I don't know and am reluctant to say because we really don't know the kind of information about John's plant. SIGreg on the plcs.net forum supplied us with the required information.

I think John is using a poorly implemented integrator which makes the situation worse.

If John's system works like Fred's model ( K/s ) you are probably right P gain will do the trick. The problem with using P gain only is shown by your example. The output term from the proportional gain gets too high. The integrator filters things out a bit. One could do better by just having an in-flow meter using feed forward with just a P gain.

Look at the interative tuning thread. I used the Ackermann equations to compute the gains. Look at Pandiani's .pdf on

formatting link
. He computes the gains although I think he made a mistake in calculating the derivative gain. I need to check that.

The problem with iterative tuning is that people change the gains without knowing what is happening to the poles. Look at Fred's response. I need to verify what he said but it looks like he has a good approach and is very mindful of where the poles are.

Tuning shouldn't be a hit or miss process.

Peter Nachtwey

???? Where does this come from? Look at the T1 pi.pdf at the bottom. The result will be critically damped when the square root term is 0. This happens when Ti = 4/(Kc*Kp) or Kc=4/(Ti*Kp) and the poles are at Kp*Kc/2. Remember I define Kp as negative because it reduces the level. Ki should be Kc/Ti. There must be some confusion here.

Yes.

If Kc is increased further, the

Yes and no. See the equation for Kc. Increasing Kc could just move both poles to the left. It depends on what Ti is doing too.

I don't agree with the Ki/15Kp but if you substitute my numbers I agree.

If you want it be critically

YES, EXACTLY. That is what I do using the formulas for the gains as a function of the closed loop time constants.

Yes, but making the integrator time constant too long means it takes a long time for the controller to eliminate the error.

That seems too work. I picked an ALV of .020 meters which yields a gain of -5000. I adjusted the time constants until Kc = 5000. You can see the error is about half that ( 0.010m )when the integrator is used ftp://ftp.deltacompsys.com/public/NG/Mathcad%20-%20t1%20pi.pdf when the integrator is not used the error is a little larger 0.017m ftp://ftp.deltacompsys.com/public/NG/Mathcad%20-%20t1%20p.pdf

So far we agree except for the Ki=15KcKp. Where does this come from? I show how I derive my Ti = 4/(Kc*Kp) at the bottom of the .pdf.

Peter Nachtwey

The difference is in the definition of Kp. My value comes from making a step change in the controller output and record the change in level (level needs to be steady first) over a given time period(in seconds).

Kp = delta_level / [(delta_CO)(delta_time)]

If I had used the time period in minutes, my Kp would have been smaller by a factor of 60 and Ki = (Kc*Kp)/4 or Ti = 4/(Kc*Kp). Hence we have the same value.

One last comment. When I tuned level controllers for tanks, I rarely used Kc above 20. But I usually used ALVof 20% to 50%. There may be some instances where you can only tolerate a very small deviation from the setpoint but in most industial applications the purpose of the tank is to take the surge in process demand that defines the disturbance. Using a large Kc passes the disturbance and create quality problems in the product.

One doesn't normally think that a proportional term has a time element to it.

Peter Nachtwey

You do if the plant model has an integrator in the transfer function. Kp is a slope for this type. You can use any delta time you want. The slope will be constant. If you want to to know more, look at the book titled: "Process Control Fundamentals for the Pulp & Paper Industry" published by TAPPI. I wrote Chapter 7: Controller Tuning Methods. This method of tuning level control is discussed thoroughly including simulation results.

Yes, I see. When you used Ki and Kp together I think in terms of motion control gains here Kp is the proportional gain, not a plant gain, and Ki is the integrator gain not a time constant. It would have been clearer if you said you were dealing in seconds, that would have explained the 15, and used Ti instead of Ki like we were.

OK, we are on the same page now.

I have been playing around with level control tuning optimisation using Scilab. What I have come up with is a draft Scilab program that will find the optimum PID settings to minimise a cost function with configurable weighting coefficients so that you can specify the relative importance of: a) Max level error on inflow disturbance b) Sum of error c) Small valve movements all on an inflow disturbance. (I should really add setpoint responses too)

Please note that I haven't properly tested it, there are most probably bugs in.

The using of integral gain instead if time constant is because you get better optimiser performance like that.

To use it, copy from below the "level Optimse.sce" and "level.sci" into two separate files and change the Scilab directory to there and then "exec" the "level Optimse.sce" from the menu in Scilab. It will then prompt you for values and return the optimised tuning coefficients.

Regards Pieter Steenekamp

*************************************************
  • Fiirst the "level Optimise.sce" program *
************************************************* // This program finds the PID settings to optimise the response // on a level controller with significant dead time in the actuator

// it uses the SciLab functions "NDcost" and "optim" // to do the optimisation

clear; plotON=0; exec('level.sci') Thold=evstr(x_dialog('Tank holdup in seconds ?','50')); Tpdt =evstr(x_dialog('actuator dead time ?','10')); maxErrorWeight=evstr(x_dialog('maxErrorWeight ?','10')); sumAbsErrorWeight=evstr(x_dialog('sumAbsErrorWeight ?','1')); sumDeltaCoSquaredWeight=evstr(x_dialog('sumDeltaCoSquaredWeight ?','1'));

// initial tuning values: x(1)= -1; // for proportional gain x(2)= 0; // for integral gain x(3)= 0; // for derivative gain

printf(' Maybe now is a good time to have coffee, because this optim- function is sometimes slow \n'); [f,xopt,gopt]=optim(list(NDcost,level),x)

Kc=xopt(1) Ki=xopt(2) Kd=xopt(3)

plotON=1; g=level(xopt);

*************************************************
  • Now for the "level.sci" function *
*************************************************

function f = level(x)

// The basic intent of this function is to be called by "optim" from outside of this to find the optimum x

// This fuction calculates the optimisation cost function as a function of Kc, Ki & Td, supplied as vector x // Thold, Tpdt, plotON,maxErrorWeight,sumAbsErrorWeight,sumDeltaCoSquaredWeight must be global variables, declared outside

// The approach on units taken is to work in percent of range and not in engineering units

// Optimisation variables: max_error = 0; sumAbsError=0; sumDeltaCoSquared=0; // To penalise fast cahnges in controller output

// Read tuning variables x Kc=x(1); Ki=x(2); Kd=x(3);

T=1; // simulation update period in seconds Kp = -T/Thold; // Tank gain - take it as negative because control on outflow PV(1)=0; // fluid level in meters CO(1)=0; // Control output in percent of full output ui(1) = 0; // integrator contribution to CO up(1) = 0; // proportional contribution to CO ud(1) = 0; // derivative contribution to CO flow_out(1)=0; // flow pumped out in cubic meters per minute flow_in = 10; new_error=0; // error in level meter old_error=0; // error in level meter

max_time = 200; // length of simulation in seconds N=round(max_time/T); // convert to sample periods

// intialise dead time buffer if Tpdt>0 then for j = 1:Tpdt, opBuffer(j) = 0; end end

for n=1:N;

t(n) = n*T; // Compute time indexes. This is needed for time index

SP(n)=0;

// calculate the new flow, as a function of controller output and dead time: if Tpdt > 0 then flow_out(n+1) = opBuffer(Tpdt) ; //pure dead time is applied to out floe else flow_out(n+1) = CO(n); end

// update dead time buffer if Tpdt>1 then for j = 0:Tpdt-2, j1 = Tpdt - j; opBuffer(j1) = opBuffer(j1-1); end end opBuffer(1) = CO(n);

// Integrate the difference between the flow in and flow out. PV(n+1) = PV(n) + Kp*(flow_in - flow_out(n))*T; if PV(n+1) > 100 then PV(n+1)=100 elseif PV(n+1) max_error then max_error = abs(new_error(n+1)); end sumAbsError = sumAbsError + abs(new_error(n+1)); up(n+1) = Kc*new_error(n+1); // calculate the proportional control output percent ui(n+1) = ui(n) + Ki*new_error(n+1); // calculate the integrator control output percent

if ui(n+1) > 100 then ui(n+1)=100 elseif ui(n+1) 100 then CO(n+1)=100 elseif CO(n+1) 0.5 then subplot(2,1,1); // Level on top plot(PV); xtitle('Level'); legend("level"); subplot(2,1,2); // Control output at bottom

plot(CO); xtitle('Control Output'); legend("CO"); end

f = maxErrorWeight*max_error + sumAbsErrorWeight*sumAbsError + sumDeltaCoSquaredWeight*sumDeltaCoSquared;

endfunction

This is very good. I would have started a new thread because this is actually more related to the iterative tuning thread than the level control thread.

I have used lqrsolve but not optim. I will have to see if there is a difference. From what I have seen evaluation function for qrsolve returns a vector of errors that lqrsolve uses to calculate the gradient of the error function as a function of the change in gains. It looks like optim only requires the evaluation function only return an error value. I doubt the optim can be as smart about how it changes the gains as the lqrsolve. This may result in more iterations because the gradient may not be calculated. I think this point is VERY important because it is critical that the number of iterations be minimized.

Do you mind if I put this on my FTP site in the NG directory and update it as you update your files?

I can see you added a dead time to the model. That will make things interesting but very general.

Peter Nachtwey

I concur. Another reason why the choice of solver is important is to ensure you do find the global optimum. I haven't tried lqrsolve, but found Matlab's Optimisation and Genetic Algorithm Toolboxes to be significantly better than Scilab's optim; both in terms of speed and ability to find "difficult" global optimums.

I don't mind.

Pieter Steenekamp

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required