Question about PI control integration time

Hello, I am working on a PI controller for a pump system, and I am trying to figure out how to relate the gain and integration time to the physical system. The system set point is 60 psi. If the system is in manual mode, sitting at 40 psi, and I give a step input of 20 psi, it takes about 15 seconds to reach the set point of 60 psi. As I remember from controls class way back when, the 15 seconds represent four time constants for the system. And so the system time constant is around 3.67 seconds. How do I use this information to set the integration time? And, what is the integration time with respect to the physical system? I would assume that I could set the gain to 1 and adjust in the field. Is there a method of system testing which would give me an initial ball park estimate for gain?

thanks for your help.

Andy

Reply to
Andrew
Loading thread data ...

The integrator has two main effects: it eliminates steady-state error and it reduces stability. The linger you can comfortably wait for a steady-state error to be removed, the stabler your system will be and the less overshoot it will experience. The more overshoot you can tolerate, the shorter the has to last. Ideal solutions exist on paper. The real world is a compromise.

Jerry

Reply to
Jerry Avins

formatting link
is the closest example I could find on the net quickly but it should be all you need. The heat exchanger example is different because its gain is negative whereas you gain will be positive but the rest should apply. Is your pressure proportional to the control output when you are in manual? If so follow the example on the page. There are other pages that explain how to do the different steps. It look like you found Tp on your own. If you look down the page you will see that Ti=Tp=3.75. If you look some more you will see there is a formula for the controller gain.

Peter Nachtwey

Reply to
pnachtwey

"Andrew" schrieb im Newsbeitrag news: snipped-for-privacy@w5g2000hsg.googlegroups.com...

See page 1 and page 2

formatting link

Reply to
JCH

. snipped-for-privacy@w5g2000hsg.googlegroups.com...

Where did this come from? It isn't right. Kp*(1+3.67*s) =3D Kc*[1+1/(Ti*s)]

Where did Ti=3D3.3 come from? It works but it looks like you really 'tuned' this system instead of calculating the gains You certainly didn't use Kp*(1+3.67*s) =3D Kc*[1+1/(Ti*s)] You are confusing the rookies again.

see

formatting link
know I have posted the link above before in the last month or two.
formatting link
links will show you how to calculate the gains using direct synthesis which is the method used on the
formatting link
site.

What does ITAEcriterion =3D t*|e|*dt =3D 1.273 MIN =3D optimum mean? You certainly didn't use the minimum ITAE technique to tune your system. The minimum ITAE tuning is under damped so the response would over shoot the set point. Your response didn't noticeably over shoot. It is also doubtful that the minimum ITAE would return nice numbers such as 3 or 3.3.

Peter Nachtwey

Reply to
Peter Nachtwey

Peter:

Where did this come from? It isn't right. Kp*(1+3.67*s) = Kc*[1+1/(Ti*s)]

Reply to
JCH

_____ Andrew,

The example Peter N. referred to above is good, and practical. The information you provided for your open loop test was incomplete. You must always provide four figures (as documented in my Control Engineer's Training Manual, p96): 1) steady-state gain (Kp) of your process = delta(measured variable)/delta(manipulated variable) in any suitable engineering units 2) theta = approximation of the dead time 3) t25 = time when 25% of the response has been achieved 4) t75 = time when 75% of the response has been achieved

Assuming that your plant is a first-order plus dead time (FOpDT) process, we can use the following simple formulas to estimate the plant's transfer function: a) tau = 0.91(t75-t25) (first-order time constant) b) theta = t75-1.386*tau (first-order dead time)

You did *not* provide the steady state gain. Hence, it is not possible to calculate the controller gain Kc.

Using a typical plant response curve that shows steady-state after 15 seconds give a first-order time constant of 5.0 to 5.5 seconds.

Assuming that you obtained the Kp of the plant, then the following simple formulas give you a starting point for your PI controller tuning constants: i) Kc = 1/Kp (say, Kp = 5, then Kc = 0.18) ii) Ti = tau (say, tau = 5.5, then Ti = 5.5)

This is also the tuning that results from the "moderate response tuning" in reference

formatting link
All the above assumes that you are working with an electronic (or pneumatic) analogue controller. The equations hold also if you are using a digital controller with a loop sample time that is at least 10 times faster than the first-order time constant, or in your case 5.5/10 = 0.55 seconds or faster.

The process you need to go through to obtain a plant response is the same for any plant, regardless of time constants and steady-state gains. In the process industry we see time constants that vary from seconds to hours (large reactors, distillation trains, etc). Once you get that skill down pat, and you can tune controllers well, you will be in demand.

Reply to
jch

_____ Above should read i) Kc = 1/Kp (say, Kp = 5, then Kc = 0.2)

When you ask questions about control loop tuning it would most helpful if you describe the process in simple terms. All we know is that your plant has to do with a pump system. The major first-order time constant is quite small; in the order of seconds. Perhaps you are measuring and controlling a fast pressure process?

It is standard (and best) practice to show the plant as a "black box", clearly identifying the controlled variable (Y), and the manipulated variable (M) [in engineering units] like this:

---------- Where G(s) is a first-order plus dead time M(s) | | Y(s) process

-------->| G(s) |--------> G(s)=Y(s)/M(s)=Kp[1/(1+tau*s)]e^(-theta*s) | | ----------

The process gain Kp is thus delta(Y)/delta(M). It is customary to keep the delta(M) as small as possible to avoid large process upsets, but big enough to get an open-loop response curve that can be charted easily. A common starting value for delta(M) is in the 10% to 15% of range.

There are other tuning methods around. Ziegler-Nichols and others developed methods that rely on getting the plant into a sustained oscillation. I personally dislike that method. The plant operator(s) may not like you doing the Z-N method.

I often use a graphical method. The graphs were developed (via simulations) for "setpoint tuning" as compared to "load tuning" because the tuning for these two cases differ. From my graphs i get Kc = 0.2, and Ti = 4.2.

Reply to
jch

This is not ITAE optimal soulution!

Your ITAE index is J=3D1.27. Your controller output is 300psi. The plant is destroyed (RIP). Congratulations.

Use this settings to get ITAE index J =3D 0.32. Kc=3D10, Ti=3D0.6 You can see your solution is not optimal in ITAE sense.

I can get even better ITAE index but completely unrealistic in practise just like yours is.

You use software to get results but you don't understand them. You don't know control theory nomenclature so you are misleading people.=

You haven't shown us not even once your calculation so my conclusion is that you are having fun with some software and than you are trying to find on the internet what does your results mean.

You are not serious oponent to debate, you must be kid or self-taught person or some very mentally-ill former =

engineer. You are wasting my and others time and you will go to troll room (PLONK)= .

Reply to
Mikolaj

"Mikolaj" schrieb im Newsbeitrag news:op.tticxxk43r65ff@xmasnew...

This is not ITAE optimal soulution!

Your ITAE index is J=1.27. Your controller output is 300psi. The plant is destroyed (RIP). Congratulations.

My ITAE is based on 0.2...1 and is "relativ".

My "process value" is 60 psi in a range of 0...100 psi:

formatting link
output is max. 1 (note max 1!). Look at it.

Thanks for the PLONK! For the next 300 years, I hope.

Reply to
JCH

Newsbeitragnews:op.tticxxk43r65ff@xmasnew...

Mikolaj is saying your indexd is 1.27 and is not optimal. You misunderstood what Mikolaj was saying.

What do you mean by that? Your should read this thread.

formatting link
Y and I basically proved that the origanal coefficients for ITAE were wrong. I don't know if someone has a better set of coefficient other than those that Dave Y and I posted. JCH, by now you should realize that I wasn't asking about minumum ITAE because I don't know what it is. I was asking to get you to explain discrepencies that Mikolaj has pointed out.In most case I questions just to get you to think about what you are doing wrong. I could be far more blunt. I think every know this except you.

psi:

formatting link
Controller output is max. 1 (note max 1!). Look at it.

I agree with Mikolaj, you never show your calculations so it is hard to explain exactly where your are wrong. I do know that you don't know how to tune PID because you always make them look bad. I know you really don't understand feed forwards. Your feed forward coefficients for velocity, acceleration and jerk feed forwards are not right. JCH must always use a target filter. I dont know why. I don't need one for simple applications.

Were is Jerry, Tim and PaulM? I know Tim and Jerry have challenged the fractor, why not JCH?. There are many more people that just lurk or only participate in the non-technical threads. Study some so you can challenge what doesn't seem right. I have thought for years that there is no intelligent life on this newgroup. Don't let JCH prove me right.

JCH, be sensible and show your calculations and answer the questions asked about your posts. If you don't want to then don't post links to your site that you are unwilling to back up. You still didn't answer why your response isn't underdamped like a minimum ITAE response should be. WELL?

Peter Nachtwey

Reply to
pnachtwey

schrieb im Newsbeitrag news: snipped-for-privacy@q75g2000hsh.googlegroups.com...

[...]

Subject: Question about PI control integration time

Did Mikolaj show calculations (plots)!? Did YOU show calculations (plots)!?

I DID! All the plots are '100% calculated' according to the task defined.

The formulae and start conditions are input and the calculation is done by a program. You see the well defined results (v1, v2 plots) in time domain.

See again: definitions and results (plots)!

formatting link
Page 1 definitions! Page 2 are results! (plots)

v1 = process value v2 = controller output

If you solve this very easy task under the same conditions you will have the same result (plots) because it's mathematics.

Internal calculation ranges:

v1 = 0.2...1 (for 0...100 psi) v2 = 0.2...1 (for 4... 20 mA)

See again: definitions and results (plots)!

formatting link
Do not exceed (note: not exceed!) 0.2...1 and make the best of it and show it.

I LIMITED the proportional step to max. v2 = 1 ^^^^^^^^^^^ Set Kc = 3 and Ti = 3.3 seconds as example. The primary task is not to exceed limits if testing.

See definitions for Kp, Kc, Ti

See again: definitions and results (plots)!

formatting link
Just use these data and we will have the same results. Show your plot! And you can prove that I am right, not wrong.

What are you thinking I am doing? Just painting the plots?

Reply to
JCH