3-pole circuit breaker voltage rating on single phase

Consider a 3-pole circuit breaker with the pole sections side by side so that pole 1 and pole 3 have pole 2 in the middle. This is a very
typical circuit breaker design for molded case breakers from companies like Cutler-Hammer and Square-D. These typically have a voltage rating giving a single number, and suitable for that voltage line to line and relative to ground. For example a 480 volt rating would allow use in a 480Y/277 volt WYE system, as well as a 480 volt corner grounded delta system. These breakers typically have ampere ratings as high as 1200. This would be in contrast to typical miniature branch breakers that have a dual voltage rating, one for line to ground and the other for line to line, such as 120/240 or 480/277.
Here's what I want to learn more about. Presumably these breakers might not have any greater line to line voltage rating than line to ground because they may be constructed with no extra insulation levels between the poles. The insulation between poles could very well be just the same as the insulation to the outside. This would contrast with placing two or three single pole breakers side by side where you would have double the insulation between poles, and some amount of greater voltage capability between them (perhaps).
What I want to focus on in a 3-pole molded case breaker is the voltage "endurance" capability (I'm avoiding the term "rating" here so as not to be confused with formal standard ratings such as UL, or manufacturer specifications that could incur legal liability) between the FAR poles, e.g. between pole 1 and pole 3 of a three pole breaker. Is there any reason there could not be an even higher voltage "endurance" between these far poles, as long as the middle pole in between does not have a relative voltage any greater than the formal rating?
Consider a 480 volt 3 pole breaker, such as Square-D model FAL34100 or others like it. It can be used on a 480 volt delta three phase power system. But what about a single phase system where there are two poles at 180 degrees phasing, with 480 volts relative to ground on each, e.g. a 480-0-480 system, with the middle pole connected to the grounded neutral wire of this system? Between pole 1 and pole 2 there would be 480 volts. Between pole 2 and pole 3 there would be 480 volts. But between pole 1 and pole 3 there would be 960 volts! But these poles are well separated by the middle pole.
If that's a little high for you, then try a lower voltage breaker such as the QDL32100 (rated for 240 volts, including 240 delta) being used on a 240-0-240 single phase system connected as described, where it would see 480 volts between pole 1 and pole 3.
In what way could a breaker like that NOT have a voltage "endurance" capability of 960 volts between poles 1 and 3 when the middle pole is connected to the grounded conductor that has no more than 480 volts relative to either phase?
Please note that I am NOT asking about formal specification or rating. I'm NOT asking of such a connection would be in compliance with any electrical code, or if such a connection would be consistent with the purpose it is safety listed for. I am asking about the physics of the design, and any aspect of electricity that would make it not possible for a breaker to generally be capable of doing this. such systems are in common use.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
...

--
> | Phil Howard KA9WGN | http://linuxhomepage.com /
http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| |> Consider a 3-pole circuit breaker with the pole sections side by side | | ... | |> -------------------------------------------------------------------------- | --- |> | Phil Howard KA9WGN | http://linuxhomepage.com / | http://ham.org/ | |> | (first name) at ipal.net | http://phil.ipal.org / | http://ka9wgn.ham.org/ | |> -------------------------------------------------------------------------- | --- | | Not knowing about circuit breaker construction, I would consider that there | could be something conductive (or even 'less insulative') in the breaker | construction which would 'bridge' some of the separation between the 1st and | 3rd poles, without effecting the effective insulation between pole 1 and | pole 2 or between pole 2 and pole 3. Imagine there were a metal pin (about | the width of pole 2) that the breaker handle hinged on. Maybe a voltage | difference of 900V between pole 1 and pole 3 would be enough to wear down | insulation between 'pole 1 and hinge' and between 'hinge and pole 3'. For | example.
That is very plausible. But I don't care to spend $500 or more for one of these to bust it open to see what's in there (I'm sure someone will suggest that at some point).
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

|> ------------------------------------------------------------------------- -

|> ------------------------------------------------------------------------- -

there
and
(about
down
For
suggest
--
> | Phil Howard KA9WGN | http://linuxhomepage.com /
http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| I never thought about destructive testing. If you use ebay and the like, | maybe you could find something for $15 since it doesn't actually have to | work. Or if you happen to know some electrical contractors, maybe they | could bring you a 200A breaker they pulled out of a reno that they were | going to throw away.
The test might not prove anything. It might stand up fine to the extra voltage in the test, but in reality have a limited lifetime due to it.
Maybe it might be better if someone who designs such breakers were to consider what it would take to upgrade the design to handle twice the voltage between A and C.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
You might want to look at the DC rating of these breakers. Some are rated by Square D to handle over 500VDC in UPS service, in which the DC system is ungrounded. Typically, the positive DC lead is broken through two adjacent breaker poles in series while the negative DC lead is broken through the third breaker pole. Merlin Gerin has an IEC rating of 1000VDC on their Masterpact brekaer. Regards, Chris Johnston

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:
| You might want to look at the DC rating of these breakers. Some are | rated by Square D to handle over 500VDC in UPS service, in which the | DC system is ungrounded. Typically, the positive DC lead is broken | through two adjacent breaker poles in series while the negative DC | lead is broken through the third breaker pole. Merlin Gerin has an | IEC rating of 1000VDC on their Masterpact brekaer.
Supposedly having the poles in series will increase the effective total voltage withstand, especially with respect to breaking the arc. And that is especially important for DC given no zero crossover to help extinguish the arc.
But I'm just wondering about the AC aspect. If a single pole can handle 480 volts on its own, then wouldn't two poles in series be able to handle 960 volts together? At least with single phase, the zero crossings happen at the same time.
So if we have line A coming in through pole A then to the load, and back from the load is line B back through pole C (not B), we have 960 volts going through 2 poles. This is an Edison style split single phase supply, but at 480/960 volts (I picked this level as there are common breakers for 480 and not for 960 specifically).
Suppose there is a fault to ground in line A. The breaker will open due to the current surge, and an arc forms across the contacts as pole A opens. But this is a 480 volt arc, fully within the capability of the breaker to interrupt and extinguish the arc at least by the next zero crossing.
Now suppose there is a fault between line A and line B. This is a fault across 960 volts. But this fault also is going through two poles opening at the same time. So the voltage should be split across the two arcs. The question here at this point is: does the wiring of 2 poles in series really work like that, and for AC? Is this the theory that should apply for the arc issues?
Then there is the breaker case dielectric issue. Obviously it should be able to withstand 480 volts to ground, so one layer of the dielectric would have that rating. If there were two such layers between adjacent poles, that should give them a higher withstand capability. Would it be the 960 volts? But since these breakers are a single unit design, I can imaging that only one layer of dielectric wall exists between adjacent arc chambers. So that's why I am wondering about the voltage withstand specifically between the far poles of A and C, where B would be (held if necessary) at a potential half way between (that would be 480 volts relative to either side if 960 is applied to A and C). Since it is an Edison style single phase system, the middle pole can be held at ground potential, and thus no more than 480 volts to either of the other poles, by connecting both its in and out lugs to neutral (this is not implying that it switches the neutral ... just connect both of them to the solid neutral bar).
| Regards, | Chris Johnston | |>Consider a 3-pole circuit breaker with the pole sections side by side |>so that pole 1 and pole 3 have pole 2 in the middle. This is a very |>typical circuit breaker design for molded case breakers from companies |>like Cutler-Hammer and Square-D. These typically have a voltage rating |>giving a single number, and suitable for that voltage line to line and |>relative to ground. For example a 480 volt rating would allow use in |>a 480Y/277 volt WYE system, as well as a 480 volt corner grounded delta |>system. These breakers typically have ampere ratings as high as 1200. |>This would be in contrast to typical miniature branch breakers that have |>a dual voltage rating, one for line to ground and the other for line to |>line, such as 120/240 or 480/277. |> |>Here's what I want to learn more about. Presumably these breakers |>might not have any greater line to line voltage rating than line to |>ground because they may be constructed with no extra insulation levels |>between the poles. The insulation between poles could very well be |>just the same as the insulation to the outside. This would contrast |>with placing two or three single pole breakers side by side where you |>would have double the insulation between poles, and some amount of |>greater voltage capability between them (perhaps). |> |>What I want to focus on in a 3-pole molded case breaker is the voltage |>"endurance" capability (I'm avoiding the term "rating" here so as not |>to be confused with formal standard ratings such as UL, or manufacturer |>specifications that could incur legal liability) between the FAR poles, |>e.g. between pole 1 and pole 3 of a three pole breaker. Is there any |>reason there could not be an even higher voltage "endurance" between |>these far poles, as long as the middle pole in between does not have a |>relative voltage any greater than the formal rating? |> |>Consider a 480 volt 3 pole breaker, such as Square-D model FAL34100 |>or others like it. It can be used on a 480 volt delta three phase |>power system. But what about a single phase system where there are |>two poles at 180 degrees phasing, with 480 volts relative to ground |>on each, e.g. a 480-0-480 system, with the middle pole connected to |>the grounded neutral wire of this system? Between pole 1 and pole 2 |>there would be 480 volts. Between pole 2 and pole 3 there would be |>480 volts. But between pole 1 and pole 3 there would be 960 volts! |>But these poles are well separated by the middle pole. |> |>If that's a little high for you, then try a lower voltage breaker such |>as the QDL32100 (rated for 240 volts, including 240 delta) being used |>on a 240-0-240 single phase system connected as described, where it |>would see 480 volts between pole 1 and pole 3. |> |>In what way could a breaker like that NOT have a voltage "endurance" |>capability of 960 volts between poles 1 and 3 when the middle pole is |>connected to the grounded conductor that has no more than 480 volts |>relative to either phase? |> |>Please note that I am NOT asking about formal specification or rating. |>I'm NOT asking of such a connection would be in compliance with any |>electrical code, or if such a connection would be consistent with the |>purpose it is safety listed for. I am asking about the physics of the |>design, and any aspect of electricity that would make it not possible |>for a breaker to generally be capable of doing this. |>such systems are in common use. |
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Phil-emon: I see what you mean:
To answer: The Bimetalic strip in a beaker can loose it's resilience to the target current/voltage limit (or flex response to temp>) with time but none of this is mentioned in books or mfgr's specs.that i am familiar with.
I think when the Bimetalic strip starts to wear out it's heat sensing characteristic the darn thing starts tripipng over nothing and then comes the time it just doesn't reset: then you throw it out and replace it with a new or functioning one.
It can fail due to Bimetalic Strength Failure does that answer your question.
oy
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Phil-emon: I see what you mean: | | To answer: The Bimetalic strip in a beaker can loose it's resilience to | the target current/voltage limit (or flex response to temp>) with time | but none of this is mentioned in books or mfgr's specs.that i am | familiar with. | | I think when the Bimetalic strip starts to wear out it's heat sensing | characteristic the darn thing starts tripipng over nothing and then | comes the time it just doesn't reset: then you throw it out and replace | it with a new or functioning one. | | It can fail due to Bimetalic Strength Failure does that answer your | question.
How is this a failure mode that is specific to L-L voltage on breakers at the 480/960 level, and not at the 120/240 level (which do exist)? Or how is this a failure mode that is specific to voltage. If a breaker can fail (and it can, and many do) then it can fail in many circumstances and cause these same problems.
The heat dissipation in the breaker is a function of current since it is a very low impedance in the circuit. The voltage drop across the strip is going to be a function of its resistance and current flowing through. Change the supply voltage, and adjust the load to use the same current at the new supply voltage, and the bimetal strip will still get the same current and as long as it has the same resistance, get the same wattage and the same heat.
But of course there are many way it can change. Years of hot operation can loosen or change its mounting points. Or it's metallurgy can change in some way and it no longer flexes the same way. Or the ability of the breaker case to dissipate heat can be reduced (insects crawling into the little holes and plugging them up). But all of these problems exist in any case. They would not be specific to a breaker running double the L-N voltage on the A-to-C poles.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Phil: you are not going to let this rest are you???
what you're saying seems to point to magnetic interference from chambers A-C to the extent of causing the anomaly you've described.
oy
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Phil: you are not going to let this rest are you???
Roy: you are never going to address what I ask are you???
| what you're saying seems to point to magnetic interference from chambers | A-C to the extent of causing the anomaly you've described.
I do not see how you draw such a conclusion out of what I am saying. And if that were true, it would negate being able to use a 2-pole breaker as is commonly found in distributed bus phasing panels (for either single or three phase). But in fact there are plenty of breakers with adjacent chambers in which magnetic interference could occur. So it really seems that this is a non-issue.
If you want me to put it to rest, then due to a total lack of any technical evidence put forth to the contrary, I would have to conclude that voltage withstand between pole A and pole C of a three pole breaker constructed with the poles laid out in a linear fashion (as virtually all of them are) will be about twice that of the voltage withstand between adjacent poles.
I take it, Roy, that you do not, and never have, designed circuit breakers for a living, or else if you do, you are under an NDA from divulging any technical info about any circuit breakers whatsoever.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
From: snipped-for-privacy@ipal.net
| Phil: you are not going to let this rest are you??? Roy: you are never going to address what I ask are you??? | what you're saying seems to point to magnetic interference from chambers | A-C to the extent of causing the anomaly you've described. I do not see how you draw such a conclusion out of what I am saying. And if that were true, it would negate being able to use a 2-pole breaker as is commonly found in distributed bus phasing panels (for either single or three phase). But in fact there are plenty of breakers with adjacent chambers in which magnetic interference could occur. So it really seems that this is a non-issue. If you want me to put it to rest, then due to a total lack of any technical evidence put forth to the contrary, I would have to conclude that voltage withstand between pole A and pole C of a three pole breaker constructed with the poles laid out in a linear fashion (as virtually all of them are) will be about twice that of the voltage withstand between adjacent poles. I take it, Roy, that you do not, and never have, designed circuit breakers for a living, or else if you do, you are under an NDA from divulging any technical info about any circuit breakers whatsoever. -- ---------------------------------------------- I have done nothing but pick the living daylight off those beaker characteristics with you., No, and I will be presuming the doubled voltage withstanding between said poles in HV= panels =(from whence you reference) until & if i encounter the contrary myself. * Besides every time i address your query you change to a different Angle in your Hypothesis. oy ----------------------------------------------
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"Roy Q.T." wrote:

If he was serious about design issues he would be contacting the engineering departments of Square D, or other manufacturers of Circuit breakers.
--
Former professional electron wrangler.

Michael A. Terrell
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:
| If he was serious about design issues he would be contacting the | engineering departments of Square D, or other manufacturers of Circuit | breakers.
Actually I did a few months ago. I spoke with one engineer who said "as long as the line to ground voltage does not exceed XXX volts, it will be fine". I asked for more details but that was denied for trade secret reasons. The manufacturers will not be forthcoming for many legal reasons. Since I'm not going to be buying their products, they have no reason to deal with me any further. If I were in the market for them, as opposed to just in the learning process, maybe they would. It could well be that if I had an application for using a breaker on a single phase 480/960 volt Edison configuration power source, they could recommend using a 480 volt 3-pole breaker as I had previously suggested. Or maybe they would have to tweak something in the design or manufacture of the breaker. Or maybe they would have to start all over and make a specific 960 volt model. I sensed that engineer did know what he needed to know to figure it out; he just wasn't allowed to tell me. I also sense that almost everyone who has replied in this thread doesn't know what they are talking about. Of course I'm no expert, but I suspect I could accidentally stumble on the correct theory and you guys wouldn't recognize it at all. Maybe I already have and it offends some that I did so.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The breaker may very well be capable of doing what you suggest. Remember that you need to allow for unequal voltage division, as one pole may see more than half of the 960 volts if there is a line-line fault.
The real issue is that nobody (ie. UL) has tested and rated it under these conditions. The manufacturer would need to pay for this, and it is not an application that they need to be concerned with.
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| The breaker may very well be capable of doing what you suggest. Remember | that you need to allow for unequal voltage division, as one pole may see | more than half of the 960 volts if there is a line-line fault.
That would also be an issue on 120/240 volt single phase circuits with the 120 volt L-N rated breakers. But they are rated for 240 volt L-L in 2-pole versions, so they clearly have the capability in those models. But from what I can tell, the 2-pole models are essentially the same atwo 1-pole models stuck together and using a common handle tie (internally or externally). Is there something in the design above and beyond what makes it a 120 volt L-N breaker that can make it do 240 volts L-L with 2 breakers?
| The real issue is that nobody (ie. UL) has tested and rated it under these | conditions. The manufacturer would need to pay for this, and it is not an | application that they need to be concerned with.
That's one of the general difficulties with these listings. Instead of doing them in a generalized way (e.g. specify the maximum rating in all aspects, rather than just one that the market most commonly uses), they are done in a most narrow way. That's probably to keep testing costs low (e.g. test at a specified parameter for consistent performance). At all voltages below 347 volts L-N every breaker I see has a L-L rating at least as much as you really would get from 3-phase power at those voltage combinations. There being a gap of common usage of voltages between 600 volts and 2400 volts, you pretty much don't see anything there. This is really what I have suspected all along.
-- ----------------------------------------------------------------------------- | Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ | | (first name) at ipal.net | http://phil.ipal.org/ http://ka9wgn.ham.org/ | -----------------------------------------------------------------------------
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Use for intended purpose only. Maybe you have read that somewhere in the NEC.
Consider a 3-pole circuit breaker with the pole sections side by side so that pole 1 and pole 3 have pole 2 in the middle. This is a very typical circuit breaker design for molded case breakers from companies like Cutler-Hammer and Square-D. These typically have a voltage rating giving a single number, and suitable for that voltage line to line and relative to ground. For example a 480 volt rating would allow use in a 480Y/277 volt WYE system, as well as a 480 volt corner grounded delta system. These breakers typically have ampere ratings as high as 1200. This would be in contrast to typical miniature branch breakers that have a dual voltage rating, one for line to ground and the other for line to line, such as 120/240 or 480/277.
Here's what I want to learn more about. Presumably these breakers might not have any greater line to line voltage rating than line to ground because they may be constructed with no extra insulation levels between the poles. The insulation between poles could very well be just the same as the insulation to the outside. This would contrast with placing two or three single pole breakers side by side where you would have double the insulation between poles, and some amount of greater voltage capability between them (perhaps).
What I want to focus on in a 3-pole molded case breaker is the voltage "endurance" capability (I'm avoiding the term "rating" here so as not to be confused with formal standard ratings such as UL, or manufacturer specifications that could incur legal liability) between the FAR poles, e.g. between pole 1 and pole 3 of a three pole breaker. Is there any reason there could not be an even higher voltage "endurance" between these far poles, as long as the middle pole in between does not have a relative voltage any greater than the formal rating?
Consider a 480 volt 3 pole breaker, such as Square-D model FAL34100 or others like it. It can be used on a 480 volt delta three phase power system. But what about a single phase system where there are two poles at 180 degrees phasing, with 480 volts relative to ground on each, e.g. a 480-0-480 system, with the middle pole connected to the grounded neutral wire of this system? Between pole 1 and pole 2 there would be 480 volts. Between pole 2 and pole 3 there would be 480 volts. But between pole 1 and pole 3 there would be 960 volts! But these poles are well separated by the middle pole.
If that's a little high for you, then try a lower voltage breaker such as the QDL32100 (rated for 240 volts, including 240 delta) being used on a 240-0-240 single phase system connected as described, where it would see 480 volts between pole 1 and pole 3.
In what way could a breaker like that NOT have a voltage "endurance" capability of 960 volts between poles 1 and 3 when the middle pole is connected to the grounded conductor that has no more than 480 volts relative to either phase?
Please note that I am NOT asking about formal specification or rating. I'm NOT asking of such a connection would be in compliance with any electrical code, or if such a connection would be consistent with the purpose it is safety listed for. I am asking about the physics of the design, and any aspect of electricity that would make it not possible for a breaker to generally be capable of doing this. such systems are in common use.
-- ----------------------------------------------------------------------------- | Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ | | (first name) at ipal.net | http://phil.ipal.org/ http://ka9wgn.ham.org/ | -----------------------------------------------------------------------------
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Use for intended purpose only. Maybe you have read that somewhere in the NEC.
Ah, another person who hits reply without reading the posting. If you did read it, you could see I am not asking about what is legal or compliant. If you did read it, you would see that I am asking about theory. But just for you I'll try it with a different wording. Maybe being shorter you might read it.
Consider that your job is to design circuit breakers. A new product is to be offered in the form of a breaker that can handle a 240/480 volt single phase system, where both lines are 240 volts to ground. The product manager suggests taking an existing 3-phase 240 volt delta breaker that is rated for up to 240 volts, and making changes so that the two phases can be connected though pole A and pole C, with pole B being connected to neutral (and optionally even switching it). So how much work would be required to take a _typical_ breaker of that type (can handle 240 volt corner grounded delta) and make it handle 240/480 volt single phase.
Now, if you are a real designer of circuit breakers, you might be able to answer the question (aside from any trade secret issues that might exist). OTOH, if you don't know enough about inside these breakers to answer it, then there isn't anything you could contribute to answering this. But maybe you know enough about them to speculate.
I suspect the possibility is that the breaker would handle it with no changes needed, and this is simply has never been tested for that voltage because of the lack of market, and lack of a listing program at UL for that voltage level.
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Breaker on the neutral?!? WTF! Since when does anyone need to have surge protection on the neutral? Do you remember Ohms Law?
| Use for intended purpose only. Maybe you have read that somewhere in the NEC.
Ah, another person who hits reply without reading the posting. If you did read it, you could see I am not asking about what is legal or compliant. If you did read it, you would see that I am asking about theory. But just for you I'll try it with a different wording. Maybe being shorter you might read it.
Consider that your job is to design circuit breakers. A new product is to be offered in the form of a breaker that can handle a 240/480 volt single phase system, where both lines are 240 volts to ground. The product manager suggests taking an existing 3-phase 240 volt delta breaker that is rated for up to 240 volts, and making changes so that the two phases can be connected though pole A and pole C, with pole B being connected to neutral (and optionally even switching it). So how much work would be required to take a _typical_ breaker of that type (can handle 240 volt corner grounded delta) and make it handle 240/480 volt single phase.
Now, if you are a real designer of circuit breakers, you might be able to answer the question (aside from any trade secret issues that might exist). OTOH, if you don't know enough about inside these breakers to answer it, then there isn't anything you could contribute to answering this. But maybe you know enough about them to speculate.
I suspect the possibility is that the breaker would handle it with no changes needed, and this is simply has never been tested for that voltage because of the lack of market, and lack of a listing program at UL for that voltage level.
-- ----------------------------------------------------------------------------- | Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ | | (first name) at ipal.net | http://phil.ipal.org/ http://ka9wgn.ham.org/ | -----------------------------------------------------------------------------
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Breaker on the neutral?!? WTF! Since when does anyone need to have surge protection on the | neutral? Do you remember Ohms Law?
I know Ohms law. How do _you_ think Ohms law applies in this case?
It is done in many places for good reason. It can be done in others for any reason. As long as the breaker or disconnect can ensure that the neutral never opens before all others are open, and never closes after any others are closed, it can be done.
However, in the scenario I describe, it is not necessary to actually break the neutral connection. Instead, you have a solid neutral bar as you would with a 2-pole breaker, but with the 3-pole breaker you connect both in and out lugs of the middle (B) pole to the neutral bar, along with the supply and load wires (4 total, and maybe even the ground bond if this is the service entrance).
The idea is to hold the mechanism of the middle pole at a reference voltage, rather than let it float between the 2 hot poles.
wrote: | | | Use for intended purpose only. Maybe you have read that somewhere in the NEC. | | Ah, another person who hits reply without reading the posting. | If you did read it, you could see I am not asking about what is | legal or compliant. If you did read it, you would see that I | am asking about theory. But just for you I'll try it with a | different wording. Maybe being shorter you might read it. | | Consider that your job is to design circuit breakers. A new | product is to be offered in the form of a breaker that can | handle a 240/480 volt single phase system, where both lines | are 240 volts to ground. The product manager suggests taking | an existing 3-phase 240 volt delta breaker that is rated for | up to 240 volts, and making changes so that the two phases | can be connected though pole A and pole C, with pole B being | connected to neutral (and optionally even switching it). So | how much work would be required to take a _typical_ breaker | of that type (can handle 240 volt corner grounded delta) and | make it handle 240/480 volt single phase. | | Now, if you are a real designer of circuit breakers, you might | be able to answer the question (aside from any trade secret issues | that might exist). OTOH, if you don't know enough about inside | these breakers to answer it, then there isn't anything you could | contribute to answering this. But maybe you know enough about | them to speculate. | | I suspect the possibility is that the breaker would handle it | with no changes needed, and this is simply has never been tested | for that voltage because of the lack of market, and lack of a | listing program at UL for that voltage level. | | -- | ----------------------------------------------------------------------------- | | Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ | | | (first name) at ipal.net | http://phil.ipal.org/ http://ka9wgn.ham.org/ | | ----------------------------------------------------------------------------- | |
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
  Click to see the full signature.