Another hot tub wiring question (long) - best 3-phase service?

A Scott-T converts between 90 degree 2 phase and 3 phase. It will work fine with two equal single phase loads, the same way 3 phase Y works fine with 3 equal single phase loads.

I saw a mathematical discussion that shows how a (properly loaded) Scott-T does not have any reactive power issues. While it appears at first glance the transformer connected phase-phase would have 30 degree reactive load on each of two phases, the current through its center tap counteracts it. Unfortunately, I don't remember the proof other than the CT current was the key, and it does present a unity power factor (given resistive loads and ideal transformers) on all phases.

I suppose one way to look is the power drawn in purely resistive loads. The two loads differ by 90 degrees so the voltage across one will go as sin(theta) the other as cos(theta). The power drawn will be as sin^2(theta)*R+cos^2(theta)*R = 1*R or R. Reflected back through ideal transformers will mean the draw on the 3 phase will also be constant, or equal draw from all phases.

Reply to
Michael Moroney
Loading thread data ...

On Sat, 14 Feb 2004 05:35:08 +0000 (UTC) Michael Moroney wrote: | snipped-for-privacy@ipal.net writes: | |>On Fri, 13 Feb 2004 20:33:37 +0000 (UTC) Michael Moroney wrote: | |>| Now that I think of it, you can cheat even more and use only |>| one transformer! Again, get a 240V center tapped grounded delta |>| service, and use a "Scott-T" transformer configuration. This essentially |>| generates 2 phase service from 3 phase service, and yes it is balanced |>| among the 3 phases as long as the load is balanced among the two |>| sources. The transformer is 208V-240VCT and has to be 50% beefier |>| than the transformers in the previous examples. Connect as follows: | |>I believe the current angle will be plus and minus 30 degrees reactive |>on 2 of the phases with this. A Scott-T is meant to supply a 3 phase |>load, not a 1 phase load. The power company might not like this due to |>the low power factor (0.5). | | A Scott-T converts between 90 degree 2 phase and 3 phase. It will work | fine with two equal single phase loads, the same way 3 phase Y works fine | with 3 equal single phase loads. | | I saw a mathematical discussion that shows how a (properly loaded) Scott-T | does not have any reactive power issues. While it appears at first glance | the transformer connected phase-phase would have 30 degree reactive load | on each of two phases, the current through its center tap counteracts it. | Unfortunately, I don't remember the proof other than the CT current was | the key, and it does present a unity power factor (given resistive loads | and ideal transformers) on all phases. | | I suppose one way to look is the power drawn in purely resistive loads. | The two loads differ by 90 degrees so the voltage across one will go as | sin(theta) the other as cos(theta). The power drawn will be as | sin^2(theta)*R+cos^2(theta)*R = 1*R or R. Reflected back through ideal | transformers will mean the draw on the 3 phase will also be constant, or | equal draw from all phases.

I still don't see how you're getting the current phase angle changed for the one winding that is attached to the high leg.

If this really does work, then would not a cascade of several (3 or more) T-T transformers in 120 rotation be able to spread a 1 phase load over a 3 phase supply almost in balance?

Reply to
phil-news-nospam

It is already in phase. It goes to the ct of the other transformer whose voltage would be halfway between the other phases.

Or are you talking about the fact that it uses a transformer for half the load and none for the other, and the transformer introduces a phase shift by being reactive? If so, yes that is a flaw.

? I don't understand why you'd mention something like that.

Anyone have access to electrical simulation software like the old SPICE who can run a Scott-T configuration through it?

Reply to
Michael Moroney

Reply to
BFoelsch

| I think that this issue is one where the simplest, most direct answer is | also the best - Just use a single phase 208 to 120/240 transformer on each | unit. No modifications to the building wiring, no modification to the tub, | no issues with "floating" neutrals.

That depends on if his building is already wired for what configuration of power. I've seen the effect of switching things from 240/120CT to 208Y/120. If the building is already wired up for 208Y/120, then it is probably cost effective to just leave it that way. He mentioned 6 hot tubs. Whether the best solution would now be 6 transformers (1 for each tub) or 3 (1 for two tubs, but still keeping the load balanced) would be an issue to consider. But if the building is yet to be wired (or rewired by remodeling) I would tend to go with 3x240/120CT just so I have true 240 available where needed. There are other factors that could sway the decision, such as how much load there is, if there is any real 3 phase load, and if I am getting power in at some other voltage (e.g. 416Y/240 or 480Y/277) that forces a transformer to be involved for everything, anyway. If there have to be whole-building transformers, that makes going with 3x240/120CT an easier decision for me. Then I have to weigh the cost of using a normal 3 phase transformer to get

208Y/120 plus the costs of the individual transformers for the 240/120 loads, vs. the cost of 3 single phase 480x240 to 240/120 transformers and no more needed for loads that do want real 240 or 240/120CT.
Reply to
phil-news-nospam

Thanks to all for a good discussion. The spa building is still in the planning stages (without existing service) so that will figure into the specifications. Much useful input was given from these discussions.

Transformers are interesting, seemingly simply devices... In reality however, they are quite complex, like a game of chess, in terms of a theoretical analysis of the basis underlying principals.

For those interested in a little bit of history...

The inventors of the transformer (Lucien Gaulard & John Gibbs) experienced years of difficulty with their invention because they kept on hooking up their circuits with the primaries in series instead of parallel. The end result was that they could transmit power for long distances, but the practicality of the invention suffered due to poor load regulation. The parallel primary connection (for multiple transformers) that seems so obvious to us today, was not perfected until a theoretical understanding was applied by men like Tesla, Stanley, and Westinghouse.

Lucien Gaulard was born in Paris in 1850. Gaulard was a French scientist, primarily interested in chemistry of explosives, but later he shifted his interests to electrotechnics. He developed a thermochemic battery and he is particularly known for his work with induction coils (transformers). In 1882, Goulard and his English colleague Gibbs patented a system of distributing power using alternating current and two-coil induction devices. They used devices (then known as secondary generators) of the Ruhmkorff type in the first alternating current distribution system and had a 1:1 ratio and were used with their primaries in series.

A power transformer developed by Lucien Gaulard and John Gibbs was demonstrated in London in 1881, and attracted the interest of Westinghouse. Transformers were nothing new, but the Gaulard-Gibbs design was one of the first that could handle large amounts of power and promised to be easy to manufacture. In 1885, Westinghouse imported a number of Gaulard-Gibbs transformers and a Siemens AC generator to begin experimenting with AC networks in Pittsburgh. In hands of Westinghouse the transformers received really practical implementations.

Gaulard's transformers were successfully presented in 1884 on the international exhibition in Turin. The farthest lamp fed, on the Torino-Lanzo railway line, was at 40 km distance from the 2,000 V generator with 133 Hz frequency. The series connection led to unsatisfactory regulation unless all the transformers were equally loaded. However, these transformers were in use until 1912.

Gaulard was ingenious, but unlucky inventor. During his life his work was not recognized in France. Gaulard fell in depression state and seems he went mad, was sheltered in clinic where 1888 died the 26 November. Now Gaulard fame is memorized with tombstone in the railway station of Lanzo, there is also a street with his name in Paris.

This man was the co-inventor of one of the world's most revolutionary inventions that gave the world the ability to transmit electric power for long distances, but for some reason he just couldn't get the connections correct.

Beachcomber

Reference: (excerpts from)

formatting link

Reply to
Beachcomber

| Thanks to all for a good discussion. The spa building is still in the | planning stages (without existing service) so that will figure into | the specifications. Much useful input was given from these | discussions.

That will mean you have a choice in the way you do this. You could go with getting 208Y/120 service and smaller transformers to take 208 volts up to 240/120CT. Or you could go with that or other three phase voltage and use transformers for your full capacity. With that choice you can either go with 240/120CT for the whole building, or do 208Y/120 and more transformers to get 240/120CT just for the tubs. You will need to see what else you might have that needs, or works better, on 240/120, and evaluate the cost of all your options.

| The inventors of the transformer (Lucien Gaulard & John Gibbs) | experienced years of difficulty with their invention because they kept | on hooking up their circuits with the primaries in series instead of | parallel. The end result was that they could transmit power for long | distances, but the practicality of the invention suffered due to poor | load regulation. The parallel primary connection (for multiple | transformers) that seems so obvious to us today, was not perfected | until a theoretical understanding was applied by men like Tesla, | Stanley, and Westinghouse.

You mean multiple transformers feeding different loads where the primaries for each are in series? Yeah, that would be bad.

You can get transformers would double primaries which can be wired either in series or parallel. One rated 480x240 would handle 480 volts when wired in series and 240 volts when wired in parallel, with the same kVA capacity.

If you get 480Y/277 power, you could get one 3 phase transformer to take 480 volts in to a delta winding, with a secondary of 208Y/120 (three 120 volt windings in wye configuration). Then instead of doing

208 volts to 240/120CT, you could tap off the 480 volt side with the tub transformers and use the cheaper (because they are more common) 480x240 to 240/120 transformers that are out there.

| Lucien Gaulard was born in Paris in 1850. Gaulard was a French | scientist, primarily interested in chemistry of explosives, but later | he shifted his interests to electrotechnics. He developed a | thermochemic battery and he is particularly known for his work with | induction coils (transformers). In 1882, Goulard and his English | colleague Gibbs patented a system of distributing power using | alternating current and two-coil induction devices. They used devices | (then known as secondary generators) of the Ruhmkorff type in the | first alternating current distribution system and had a 1:1 ratio and | were used with their primaries in series.

Ah, I see. They probably didn't have a real grasp on the designing for particular voltages, capacities, saturation, heat rise, etc, as we (not me personally, but those who do make them) do today.

| Gaulard's transformers were successfully presented in 1884 on the | international exhibition in Turin. The farthest lamp fed, on the | Torino-Lanzo railway line, was at 40 km distance from the 2,000 V | generator with 133 Hz frequency. The series connection led to | unsatisfactory regulation unless all the transformers were equally | loaded. However, these transformers were in use until 1912.

Interesting frequency. I wonder how they picked that one.

| Gaulard was ingenious, but unlucky inventor. During his life his work | was not recognized in France. Gaulard fell in depression state and | seems he went mad, was sheltered in clinic where 1888 died the 26 | November. Now Gaulard fame is memorized with tombstone in the railway | station of Lanzo, there is also a street with his name in Paris. | | This man was the co-inventor of one of the world's most revolutionary | inventions that gave the world the ability to transmit electric power | for long distances, but for some reason he just couldn't get the | connections correct.

Perhaps he was victim to the same kind of misunderstanding I once had where transformers didn't make sense (despite knowing they should). It seemed to me back then that having _more_ windings in the primary would create _more_ flux, and that should produce more "secondary generated" power. Of course the reality is more winding is more impedance and less current. You don't want to tie them all in series with each other on different loads, or else you are making current transformers out of them (and pathetic ones at that).

Reply to
phil-news-nospam

My first inclination would be to ask why you want to install hot tubs rated for residential use in a commercial installation?

Presumably you have 120/208/4w coming in already. I'd be inclined to buy transformers and make 240v/3w (i.e. - three 208 to 240 center tap). They won't be real cheap or something you can get at home depot tomorrow, but acme or some other xfmr mfr can make them up pretty quick these days.

I am not a big fan of buck/boost xfmrs, having seen way too many of them applied improperly, just to save a few bucks.

Reply to
bob peterson

I thought I stated it earlier, but perhaps I did not make myself clear., these would be commercial units. Most, if not all of the commercial units available would still be rated for 240V. (same as residential).

Beachcomber

Reply to
Beachcomber

| I am not a big fan of buck/boost xfmrs, having seen way too many of | them applied improperly, just to save a few bucks.

Neither am I. And they are even trickier with three phase.

"Save a buck and get a boost in the rear".

Reply to
phil-news-nospam

That could be said about almost any installation of any product!

The problem you've seen is crap installations not the Buck-Boost Xfmr proper. Properly specified, and installed, a Buck-Boost xfmr installation is neither complex or unreliable. Just the opposite is usually the case. Proper application can extend the life of the connected components due to operating within a proper voltage window.

There are ample sources to guide the proper application of a Buck-Boost application. A Google search is just one of many.

Louis--

********************************************* Remove the two fish in address to respond

Louis

Reply to
Louis Bybee

On Mon, 16 Feb 2004 20:04:01 GMT Beachcomber wrote: | |>

|>

|>My first inclination would be to ask why you want to install hot tubs |>rated for residential use in a commercial installation? |>

|>

| I thought I stated it earlier, but perhaps I did not make myself | clear., these would be commercial units. Most, if not all of the | commercial units available would still be rated for 240V. (same as | residential).

I'll add to this that my bad experiences with air conditioners were with commercial units rated for 240 volts. Apparently they are made with a motor option, either 240 volt 1-phase or 208 volt 3-phase. But you can't just switch between them by wiring; it's a whole motor changeout. The problem at the place I used to work where they had this issue was that even though the building had 3 phase power, the wiring out to the rooftop for the A/C units did not allow for 3 phase. They hooked the 240 volt single phase motors to 208 volts, and under heavy loads in the summer they were burning out. Eventually the A/C guys tracked down a 208 volt single phase motor that fit and the problems were solved.

Just because things are commercial units, don't assume three phase.

My points are:

  1. Commercial stuff does come made for either 240/120 volt single phase or 208/120 volt three phase (or other voltages). Single phase stuff on voltages only seen with three phase service is rare, if it makes sense to make it in genuine three phase (lighting, for example, does come in 277 volts for places with 480/277 since it doesn't make sense to make 3 phase light bulbs).

  1. Stuff made for 240 volts does not work well on 208 volts (such as ovens and heaters, due to the slower warmup times), and in some cases causes problems and breakdowns (motors drawing heavier current at lower voltage causing greater heat buildup and damage).

  2. Stuff made for 240 volts often includes 120 volt components due to the usual expected center tapped wiring, so a neutral in the middle is still needed.

  1. 240 volta delta three phase service can have a center tap on one winding to provide 240/120 volt service, but the load is limited to 5% of the overall capacity (usable in many industrial shops to power big motors at 240 volts three phase, and several office lights at 120 volts.

If we had never allowed a center tapped single phase service to be offered, then we would not have to deal with equipment designed for that in cases where we have to take three phase power for whatever reason. In much of Europe, three phase is available even for residential, and where you get 2 or even 1 leg of it, the voltages match the design of available products. With 230 volts there's less need for the next higher voltage, and when it is needed, it's always 1.732 times as much.

There, I get my "Europe did electricity right" plug in, yet again :-)

Reply to
phil-news-nospam

Where does this 5% limit come from, and why?

Thanks in advance.

Reply to
BFoelsch

On Mon, 16 Feb 2004 19:05:17 -0500 BFoelsch wrote: | Where does this 5% limit come from, and why?

That's a good question. Where I got it from is transformer manufacturer specifications. It seems to be very consistent: every one that has that much detail has exactly the same 5% figure. As to why, I don't know. I would think there is some limit, but my first guess would have been not less than 33%. It could also be as simple as that's the capacity they put on that center tap because that's what the market has wanted.

If I hang a 240 to 240/120CT transformer across 2 legs of 240 delta, what would be the limitation there under various 3 phase loads from

0% to 100%? Of course I expect 0% for what I could draw from that tap when the 3 phase load is 100%. But what I can do with less, and does that translate into the load I can put on the delta's center tap?

| Thanks in advance. | | | wrote in message | news: snipped-for-privacy@enews4.newsguy.com... |> On Mon, 16 Feb 2004 20:04:01 GMT Beachcomber wrote: | |> 4. 240 volta delta three phase service can have a center tap on one | winding |> to provide 240/120 volt service, but the load is limited to 5% of the |> overall capacity ....................... | |

Reply to
phil-news-nospam

That may be the reason we see so much "Open Vee" center tapped delta. They will upsize the center tapped transformer to handle any extra 120v loads. I am not sure what the limit is but it is certainly a lot more than 5%. I had a data center running on an "Open Vee" and they had a lot of 120v office stuff along with the 3p computer system. They had one real fat transformer and a smaller one.

Reply to