I have finally given up trying to use GFCI protection when I move move my nutrient (salt) solutions around with pumps. I was just tripping the GFCI too often. I decided to ground the pumps and use outlets that were not GFCI protected. That seems to work well. I would feel more comfortable with GFCI protection.
I measured the leakage between the pump motor winding and ground with a DVM. It was about 80k?. Tripping at 5mA would require a leakage equivalent to a
24k? resistor. I think that the discrepancy arises because the leakage resistance is nonlinear and affected by the moisture-conductor contact.
Is it too much to expect of low cost submersible pumps to have less leakage than I measured? How much water can leak in?