On Thu, 2 Aug 2007 18:04:02 -0400 JER67 wrote: | I can not seem to find any listings for massachusetts electrical code(s) | for grounding an OTA antenna. | | To be used for an Eave/gable mounted CM 4221 with a 5' mast | | From what I can find it is recommended that I should ground the antenna, | the mast & the RG-6 with a grounding block. | | ALL should be attached to a grounding wire in the most direct route. | With it ALL going to a ground rod in the earth.
Ground the mast and antenna frame together and lead that down to a ground rod. Keep it away from other metal, but it can follow the mast if the mast goes into the ground.
Ground the coax arrestor to the same ground rod, but via a separate wire to the rod.
To prevent building up ground differential charges between antenna coax and power connections, the electrical service ground rod should be connected with this. Or just share the same one (but don't share the ground wires electrical service uses).
| Questions: | | 1) What gage ground wire should be used? i.e: 10AWG, 8AWG, 6AWG
This isn't electrical service ground, so smaller isn't such a big deal, but larger is better to some degree. You have to consider costs, too. Big wire costs big bucks. But in this case you are doing 2 things. One is keeping the antenna from building a charge that could bring in more lightning. And
| 2) Should I use a copper ground or Aluminum?
Whatever avoids an unlike metal joint. Else copper.
| 3) Stranded wire or Solid?
Stranded.
| 4) what length ground rod? How deep in the ground?
8 feet deep is a good idea. There are probably not specific requirements for an antenna purpose. Power purposes do have this requirement, but that is in part for other purposes.