Hot tub earthing question

Hi. UK question. I have a bit of a dilemma about a job that I was sent out on today. It was to install a feed for a new hot tub that a customer was getting at
the end of the month. The concrete base was already down just outside the bedroom double patio doors and the tub was to be fitted about 2 meters away from the doors. The CCU was located at the front of the house on completely the opposite side, Grrr. We ran a 6mm T&E cable (4mm earth core) from the CCU (32A breaker (I think)), connecting it into the RCB side of the CCU, through the loft space and out and down the wall (in 25mm conduit) into a suitable isolator. About a 13 meter run from the CCU to the isolator, then another 4 meters to the hot tub. We then run 3 core 6mm SWA from the isolator, down the edge of the concrete, and eventually into the hot tub (when it's fitted). We also ran a 2.5mm T&E from the CCU (16A breaker), again connected to the RCD side in the CCU, out and down the same wall to feed a waterproof MK Masterseal double socket (NON RCD). The socket and the isolator where either side of the double patio doors from the bedroom. The customer mentioned, while we where there, that she was having a wooden enclosed structure built over and around the hot tub, once fitted, with a see through corrugated, plastic roof. She wanted the sockets, fitted within the enclosed area, less than 2 meters from the hot tub, for lights, Tv, radio etc etc My questions are:- are the sockets legal where they are situated and with this being a PME supply to the house, should the hot tub have an earth stake ? I heard a report today that one of the hot tubs we fitted, in a similar situation, by a colleague of mine under the same employer, had a problem in that when the customer stood outside the hot tub and touched the water within it, they had encountered a mild electric shock. I can only put this down to a potential difference building between the true earth (the ground outside the tub) and the water within the tub, PME earth. Could this possibly be down to the 13 meter run of the feed cable, the potential difference between the Neutral and Earth of the PME system and the 4mm size of the T&E Earth ?
Any help on this subject will be greatly received, thanks. Jim
--
Smog



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
That should read 'the RCD side of the CCU' and not RCB !

away
completely
then
within
stake
in
this
size
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Jim,
some thoughts.....
I presume that the earth checks out ok when tested and is within the statutory limits for a combined neutral earth sytem.
My own hot tub / outside socket network is similar but I have made small alterations. All outside wiring run thro' an MK split board with a 30mA rcd. I laid an earth mat around the area of the decking and bonded this to the main earth treminal incoming. I have no concrete slab. This was 70mm bare copper with earth rods every 6'. tested value was 1ohm. This suplements the CNE service.
The housing of the hot tub had a seperate earth conection and I was able to connect this to the main earth also via a 6mm Cu conductor.
there is no potential difference ( I just tried with a fluke )
Hope this helps????