How to caclulate Short Circuit Impedance For A Industrial Plant .

We have 33KV in 4MVA and 33/6kv Trans and 6/0.4kv Trans. How We Can calculate Short Circuit Impedance ?

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 5/26/06 2:09 PM, in article snipped-for-privacy@localhost.talkaboutelectronicequipment.com,

Hire a qualified PE to do this. You would be a fool to get someone unlicensed, and anyone unlicensed would be a fool to accommodate you.
Bill -- Ferme le Bush
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
We have an Industrial plant with primery voltage 33KV and secondry 6KV and th-ry voltage 400V . I want to calculate short circuit current. It means that i should to know equal Impedance of all circuits. all of consumers loads totaly is 4MVA. i Want an Algorythm or program or sample sheet calculation. thnks.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Please would be nice.
Jaymack
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
eoots2000 wrote:

insuficient data.... you can not get there from here.
the smart ass answer is zero current because the breakers will have tripped.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

You need to know more about the transformer. They typically include synchronous reactance, as well as transient and sub-transient reactances. And the line feeding the transformer primary.
This really is an involved calculation, it is best to hire a pro rather than get advice on USENET for this.
daestrom
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

and
than
Transient and subtransient for a transformer? Really?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Ah, you got me. I slipped up. I was thinking he had an industrial generator feeding a transformer (I work mostly with power plants, and that is the common configuration we work with for such calcs). Then the generator is feeding the fault through the transformer.
But as I look again, I guess he's talking about a primary line feeding a substation into his 'industrial plant'. The other factor he would need then is the line impedance and its short-circuit capability.
daestrom
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
daestrom wrote:

If the plant has any good sized rotating machinery, that can contribute to the fault current as well. Like others have said, the OP needs a PE to look at the problem.
--
Paul Hovnanian mailto: snipped-for-privacy@Hovnanian.com
------------------------------------------------------------------
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Short out the power plant, measure the current, and you can calculate the impedance, probably by grunting at the nurse that follows your limbless body around.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Easy! The impedance of a short circuit is zero!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

Is it?
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Well, technically, you have to use the special, non-inductive short circuits.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
The impedance of the short circuit itself is zero. But this would mean you have an infinitely high short circuit current, which is of course impossible.
You still have the impedance of the power lines, the transformer,...
Take these into account, and then you can calculate the short circuit current by dividing the voltage by the total impedance.
Kristof
Doofus wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Only in text books. In the real world, there is always contact resistance, arc impedance, etc. at the fault. Add to that all of the other impedances that you mentioned.
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

True, but in fault analysis and when determining interrupting rating of protective devices, generally only the source impedance and intervening lines are used, the fault is assumed 'bolted' with zero impedance. Slightly conservative, but there you are.
daestrom
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

True. We use bolted faults because we can't know what will actiually occur. I was just taking exception to the statements that the short-circuit impedance is zero. A more accurate statement is "we assume for calculations that it is zero".
Ben Miller
--
Benjamin D. Miller, PE
B. MILLER ENGINEERING
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

occur.
calculations
In customer fault level calculations here we are generally required to assume that the Utility impedance is zero as well. Plus we are forced to use low impedance assumptions for utility transformers. I wonder if they will lighten up for calculating arc flash hazards when that becomes mandatory. I don't think I'll hold my breath.
j
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

'arc flash'
Oooooh, now *that's* been a head-ache lately. 600V MCC's especially :-(
daestrom
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

of
intervening
to
they
I recall a distributor mentioning a new product they have, high speed relaying or something solid state, that they use for tough arc flash applications. He used 600V MCCs as the example. They knocked 100cal/cm^2 down to 8cal/cm^2 in one instance.
So far I haven't had to do any arc flash calculations. What are the dominant factors in a calculation? I? I^2t? SCMVA? V? Got any advice to share for situations that look like a high cal/cm^2 value is likely?