Right?

I am confused. The supplied bar isn't bonded to the case? The Square-D I bought a few months ago (for a sub) had a ground bar across the bottom. I added neutral bars along the sides. Perhaps it's like accountants with their "credits" and "debits"? ;-)

Then why is it called a neutral bar if it can be either used as a ground bar or a neutral bar, and the added bars are used as neutral bars?

Ok, there is obviously something in the definition I'm missing.

The NEC requires the neutral be bonded to "ground" (the enclosure) at the service (and earthing electrode(s) be connected to the N-G).

(This is a critical connection that insures there is a high fault current for a H-G fault, with the fault current returning to the transformer on the service neutral. The high current trips the breaker.)

As I noted, virtually all services come with a neutral.

All the SquareD panels I have seen come with a neutral bar. A neutral bar is isolated from the enclosure and has a lug to connect to the source neutral.

Because almost all service panels have the service neutral bar bonded to "ground" (the enclosure) there is a means (a "main bonding jumper") supplied that can be installed to make that connection. Sometimes it is a strap that is screwed to the enclosure that connects to the neutral bar. Often it is a screw that goes through a hole in the neutral bar to the enclosure (it can look a lot like a mounting screw - probably the green screws for the "solid neutral assembly" in Michael's post).

Ground bars (as in Michael's post) are normally screwed directly to the enclosure - "ground".

(Occasionally an "isolated ground" is used and the ground bar is isolated and fed by a ground wire from the source. This could connect to "isolated ground" receptacles.)

(And it is possible that the N-G bond is not located in the service circuit breaker panel (it is elsewhere), so the neutral bar is not bonded to the enclosure.)

The only configuration I have seen is where a neutral bar is supplied and the source neutral, which is included in almost all panels, is connected to the bar. A panel could also be supplied with an installed ground bar, but it often isn't and it is added as a "kit" as in Michael's post.

If used as a service panel, a bond is added from the neutral to the enclosure ("ground"). The neutral bar can then also be used as a ground bar. Since that often happens I assume most panels do not come with a ground bar.

If a subpanel has ground wires it needs a ground bar.

Regarding the 2008NEC, you can't connect a neutral wire to a separate ground bar. The neutral current path would be through the enclosure and "main bonding jumper" to the neutral bar. The path using the enclosure is now explicitly prohibited.

============== I am astounded to read you are another sock-puppet for dimbulb.

If you believe anything that Proteus writes, you are an even bigger idiot than he is himself.

I suppose I should have used an emoticon.

krw is one of the main people that harass dimbulb.

You are talking to a dimbulb sockpupet.

How embarrassing. It is even in your approved list. How's a person to keep up?

Maybe you could create a Thunderbird add-on that would flag sockpuppets from a constantly updated list?

Sure, I got all that. I just misremembered incorrectly what I put in the panels. Every box needs a ground, not all need a separate neutral so I was misremembering that I added the neutral bar, when I did indeed add a ground bar (just looked) and removed the screws from the neutral bar*S* (one on each side). I'd remembered adding the two bars down the side of the bus, but they were indeed ground bars. In another box I fixed (my MIL's house failed inspection when we sold it) the ground bar was along the bottom.

Not as much as am *I*!

Hell, I *named* DimBulb, "DimBulb", after his insane insistence (for weeks) that a 100W light bulb didn't put out as much heat as a 100W heating element. John Larkin gave the ditz the "AlwaysWrong" moniker, and I don't remember who named him "Nymbecile". All fit perfectly.

Check the header record "NNTP-Posting-Host:" for something in the

72.197.138.nnn range.

If you can filter on any header record (most newsreaders don't) it's easy. Jim Thompson has a really good Nybecile filter, evidently.

You worded that 100% correctly. He is all about harassment.

Shame that his retarded ISP does not agree.

Although I have never lodged a complaint against the dopey f*ck.

You are a little, and I mean *little*, boy, Dimmie. Mommy's hamper is calling again!

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required