I am confused. The supplied bar isn't bonded to the case? The Square-D I bought a few months ago (for a sub) had a ground bar across the bottom. I added neutral bars along the sides. Perhaps it's like accountants with their "credits" and "debits"? ;-)
Then why is it called a neutral bar if it can be either used as a ground bar or a neutral bar, and the added bars are used as neutral bars?
Ok, there is obviously something in the definition I'm missing.
Didn't find your answer? Ask the community — no account required.
M
Michael A. Terrell
formatting link
B
bud--
The NEC requires the neutral be bonded to "ground" (the enclosure) at the service (and earthing electrode(s) be connected to the N-G).
(This is a critical connection that insures there is a high fault current for a H-G fault, with the fault current returning to the transformer on the service neutral. The high current trips the breaker.)
As I noted, virtually all services come with a neutral.
All the SquareD panels I have seen come with a neutral bar. A neutral bar is isolated from the enclosure and has a lug to connect to the source neutral.
Because almost all service panels have the service neutral bar bonded to "ground" (the enclosure) there is a means (a "main bonding jumper") supplied that can be installed to make that connection. Sometimes it is a strap that is screwed to the enclosure that connects to the neutral bar. Often it is a screw that goes through a hole in the neutral bar to the enclosure (it can look a lot like a mounting screw - probably the green screws for the "solid neutral assembly" in Michael's post).
Ground bars (as in Michael's post) are normally screwed directly to the enclosure - "ground".
(Occasionally an "isolated ground" is used and the ground bar is isolated and fed by a ground wire from the source. This could connect to "isolated ground" receptacles.)
(And it is possible that the N-G bond is not located in the service circuit breaker panel (it is elsewhere), so the neutral bar is not bonded to the enclosure.)
The only configuration I have seen is where a neutral bar is supplied and the source neutral, which is included in almost all panels, is connected to the bar. A panel could also be supplied with an installed ground bar, but it often isn't and it is added as a "kit" as in Michael's post.
If used as a service panel, a bond is added from the neutral to the enclosure ("ground"). The neutral bar can then also be used as a ground bar. Since that often happens I assume most panels do not come with a ground bar.
If a subpanel has ground wires it needs a ground bar.
Regarding the 2008NEC, you can't connect a neutral wire to a separate ground bar. The neutral current path would be through the enclosure and "main bonding jumper" to the neutral bar. The path using the enclosure is now explicitly prohibited.
============== I am astounded to read you are another sock-puppet for dimbulb.
L
lurch
If you believe anything that Proteus writes, you are an even bigger idiot than he is himself.
B
bud--
I suppose I should have used an emoticon.
krw is one of the main people that harass dimbulb.
M
Michael A. Terrell
You are talking to a dimbulb sockpupet.
B
bud--
How embarrassing. It is even in your approved list. How's a person to keep up?
Maybe you could create a Thunderbird add-on that would flag sockpuppets from a constantly updated list?
K
krw
Sure, I got all that. I just misremembered incorrectly what I put in the panels. Every box needs a ground, not all need a separate neutral so I was misremembering that I added the neutral bar, when I did indeed add a ground bar (just looked) and removed the screws from the neutral bar*S* (one on each side). I'd remembered adding the two bars down the side of the bus, but they were indeed ground bars. In another box I fixed (my MIL's house failed inspection when we sold it) the ground bar was along the bottom.
Not as much as am *I*!
K
krw
Hell, I *named* DimBulb, "DimBulb", after his insane insistence (for weeks) that a 100W light bulb didn't put out as much heat as a 100W heating element. John Larkin gave the ditz the "AlwaysWrong" moniker, and I don't remember who named him "Nymbecile". All fit perfectly.
K
krw
Check the header record "NNTP-Posting-Host:" for something in the
72.197.138.nnn range.
If you can filter on any header record (most newsreaders don't) it's easy. Jim Thompson has a really good Nybecile filter, evidently.
L
lurch
You worded that 100% correctly. He is all about harassment.
Shame that his retarded ISP does not agree.
Although I have never lodged a complaint against the dopey f*ck.
K
krw
You are a little, and I mean *little*, boy, Dimmie. Mommy's hamper is calling again!