In a print shop, the service entrance equipment has three 125A breakers. These feed three 120/208 breaker panels. There is a fourth space in the SE
panel for another breaker.
We have need to power one new printing press which draws just under 150A. If the total load calculations work out, is there any reason we couldn't use a suitable-sized breaker in the SE panel to supply this one load rather than install another 120/208 breaker panel?
Thanks.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

You didn't say how much current you are being supplied. If your SE can handle the extra breaker with safety margin then you may be fine. I agree about seeking a licensed electrician.
Tom
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Thanks Tom and others for your comments.
Yes, we will consult with an electrician or the Utility to avoid any assumptions before we do the work.
Cheers!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 12/4/2011 1:09 AM, Mike Cook wrote:

Ask your insurance company.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Insurance is OK with anything within NEC.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

As long as the load calc works, why not? What are you cruising at now?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It depends upon what the SE panel is rated for. Yes the Panels them selves have ratings for the bus bars. Obviously your running 375A so far. Is it a 400A panel or .... If you pop the cover you should see a tag inside as to what the rating is. Be careful you got Niagara Falls behind that panel ;)
Cheers
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It strikes me that this is not a do it yourself project. What is the size of your service? You need to contact your power company to find ot what they are delivering to the premies. How will they react to such an unbalanced load? If you have to ask this question, you should farm out the job.
--

Sam

Conservatives are against Darwinism but for natural selection.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 04 Dec 2011 09:04:53 -0800, Salmon Egg

Why do you think this is an unbalanced load? I have to think a 150a printing press is 3p.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It is 3-phase.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@aol.com wrote:

IIRC, there was one extra slot available for the circuit breaker. How do you protect a three-phase load that way?
--

Sam

Conservatives are against Darwinism but for natural selection.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Ah. OK, technically there's 3 slots available. There are only 3-pole breakers in this panel so I didn't count individual bus tabs, but 3-pole breaker locations.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

3-pole breaker.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

From the description I am assuming there is one three phase spot in the panel, not a single phase spot. I can't think of a panel arrangement that could have 3 3 phase breakers and a single phase slot. (would anyone even make a single phase 150A device?)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@world.std.spaamtrap.com (Michael Moroney) wrote:

Again, IIRC there were three slots used, each with a breaker for a single phase load. To me, it seemed to be a typical arrangement for lighting. I don't think any of this was explicitly spelled out.
--

Sam

Conservatives are against Darwinism but for natural selection.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
This is an OpenPGP/MIME signed message (RFC 2440 and 3156) --------------enigCD5E18B1A393050D33D48C2A Content-Type: text/plain; charset=ISO-8859-1 Content-Transfer-Encoding
Salmon Egg wrote:

From the original post: ==============================================In a print shop, the service entrance equipment has three 125A breakers. These feed three 120/208 breaker panels.
============================================== A breaker can have more than one phase going through it.
mike
--------------enigCD5E18B1A393050D33D48C2A Content-Type: application/pgp-signature; name="signature.asc" Content-Description: OpenPGP digital signature Content-Disposition: attachment; filename="signature.asc"
-----BEGIN PGP SIGNATURE----- Version: GnuPG v2.0.18 (GNU/Linux)
iQEcBAEBAgAGBQJO4BSyAAoJECGtZwCbtgwXq/YH/1wJPRXsWZow917J0nTa5bin 5qGwQHVR4tpKH7w7aSU9ss652RLSgKPjyVMjCJNxnYHJI3JWaVciYFQigwRxvPH9 73dqwiuUd7TLAlSv/UxQuII5iXkCtuS96s10jZve+BadxgqLNF+eU4Bhq5tT9XPt cdXWKTvC4O2QhcQVZU/3dAj+OuWKvNUOLObe4b+435Bix0qzYQ7wa6k6ox9uAMh6 vH56JfVaNFaxyV/QXGlVENTucRvPRQUU7UNkKTMqs9SMhOWwXHKf1yW6KCPnou9F pF9UD7dS/NJLLgiqnSJWEfwAibMdgiFh9s4IjrCQJByyvEOZCnTj+E6k/26KncA=6uAS -----END PGP SIGNATURE-----
--------------enigCD5E18B1A393050D33D48C2A--
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

This another example where the problem is one of communication. It behooves a technical person to use unambiguous language. Too many engineers, as well as other professionals, do not value good communication.
--

Sam

Conservatives are against Darwinism but for natural selection.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload