| My thought was not to pull off just one phase but to have some way to pull | off all three evenly no matter how much load I require.
A given single phase load is only going to be able to draw power at one phase angle. You can manipulate that to some degree with wiring tricks or transformers, but at the expense that your have low power factors on one or two of the phases. While a 120 volt load draws from one phase at a power factor of 1.0, a 208 volt load draws from two phases at a power factor of 0.866 (30 degrees), one leading, one lagging. But your loads are most likely 120 volt, not 208 volt.
If the circuits in each shelter or tent were three phase, the balancing can be done with each individual load within a shelter or tent. But if things are wired as single phase (two poles), then each shelter or tent is drawing from two phases (a pole to a phase). You can still do SOME tweaking of the balance WITHIN a shelter or tent by moving circuits between poles on the breaker panels. So if the C phase is light due to it not being connected to as many shelters/tents as A and B, you could go to the shelters/tents where C is connected, and move some of the 120 volt loads from the A or B phase to the C phase. That would make the shelters/tents themselves slightly out of balance, but to a degree that corrects the overall system.
| As for the load analysis, it is definately half assed. I spent 2 days | plugging all the systems in in diffrent combinations to get as even a load | as possible.
Did you manage the individual loads within a shelter/tent?
| My sheters are only wired for single phase so I cant go in and change the | way they draw off the phases. We will get new ones in 3-4 years that are | configured in the way you suggest. I will definately keep your | recomendation for when we get them though.
Yes you can. If a tent is fed with A and B, you can balance between A and B within that tent, and hence overall. Likewise of a tent is fed with B and C, you can move some loads from B to C to balance the system.
This is *assuming* you have control over individual loads with in each of the facilities (a shelter or tent). They are NOT usual single phase where the opposite poles are 180 degrees apart, giving 240 volts, as a home would have. Instead, these are 2 legs of 3 phase, at 120 degrees apart, and give you 208 volts between phases.