| need help clearing up this issue. Some electricians that work for me | often ask me is something is 208V single pahse or 3 phase. In these | cases there is no high leg system, so as I understand it 208 single | phase can't exist without the high leg. I always assume they are | talking about a 2 pole breaker in a 3 phase panel. Am i right about | this, or am I missing something.
There are 2 different power configurations generally wired 3 different ways in common use that can give you 208 volts:
The 240 volt with a center tapped winding for lighting gives you 208 volts between the high leg and ground:
*-----*-----*
You can also make the same configuration like this:
*-----*-----*
by tapping the primaries in a way to get a 90 degree phase angle and supplying that phase angle at 208 volts relative to the neutral of a regular 120/240 transformer.
Then there is the WYE configuration:
*
Which has 120 volts between any leg and ground, and 208 volts between any two legs.
| Also I have an electrician who wired some panels for a job we are | doing. He used a 200A 120/208 3 phase panel and installed a 2 pole | 100A breaker to feed a 2 pole 125 A panel. The smaller panel he refers | to as the 120/240 panel (residential type.) I know the phase angles | relative to each other are still 120 degrees. True 120/240 panels have | the same phase thus same phase angle right. So what is this smaller | panel 120/208 2 pole???? And wouldnt this configuration cause an | unbalaced condition on the 200A 3 phase panel? | Thanks
The smaller panel is getting just 2 of the 3 phases. And yes, there is a 120 degree phase angle instead of the usual 180 for single phase. And that does deliver only 208 volts to what might be an appliance expecting
240 volts. And yes, there will be an imbalance because power is drawn only from 2 of the 3 legs for the single phase panel.
If you do have three phase power, it would be better for balancing to run all the 120 volt loads right from the three phase panel. And if you are going to run anything from 208 volts, you get that by putting a 2-pole breaker in the three phase pnael. If you have 3 such 208 volt loads with their own breakers, you and arrange those breakers to put each circuit on a different pairing of hot wires.
If the total number of poles of all the circuits would fit in the main panel, I would have just done it that way (one three phase panel). And even if a 2nd panel was needed, I'd probably have done it as three phase as well. You are not going to magically get 240 volts by using a single phase panel (you'd need expensive transformers to do that).
This is all part of the hassle of three phase power in a world with mostly single phase loads. In Europe, they have 230 volts (plus or minus 10 volts) between any leg and ground. That voltage has allowed them to power stuff we would normally use 240 volts on with what they power everything else with. They can do that with a single pole of single phase power. What that means is there has been almost no need for double voltage, so almost nothing exists for 460 volts, since 230 volts is adequate for so many more things. For very high power loads, then they go with three phase and get 400 volts (and occaisionally a 230/400 volt 2 pole scheme like the single phase panel described above). So mixing single phase and three phase in Europe is easier because they don't have the issue of many common devices wanting "2x voltage" like we have in the US.
Had the US adopted universal three phase, it might well have been 208Y/120. Appliances that need more than 120 volts would then have been designed for
208 volts, not 240 volts. But that would have meant running three phase everywhere, and that costs a lot of money in rural locations. It was electrical rurification that shut out three phase power. But it was the lower 120 volts that forced the issue of 240 vs 208. Had the US decided to go with 277 volt single pole single phase to homes (and "one upped" the Europeans on the voltage), we wouldn't have this problem. We'd have stoves, dryers, and air conditioners running on 277 volts, and then only occaisionally someone needing 480 volts for big things like saunas and kilns. We'd also have a slightly lower population because back when the big decisions like this were being made, we really didn't understand electrical safety very well, and hadn't yet invented the ground fault interruptor. But I'd say more people were killed by grounding ignorance than were saved by having only 120 volts instead of 277 volts.
In Japan, single phase is 100/200 volts, and three phase is 200Y/115 volts. I don't know if commercial offices that get three phase run their lights on 115 volts or not. I do know half the country is on 50 Hz (east) and half on 60 Hz (west). That makes for a fun electrical grid. As far as I know they don't any higher voltages until you get into primary power well over 1000 volts.