Phase ground lamps circuit for 600V Delta system

| Today, many of these buildings are being converted to multi-use commercial | application, where most of the loads are single-phase. They either add | 480-240/120 single-phase transformers feeding various panels, or replace the | service with 208/120. In the latter case, the few three-phase loads, such as | elevators or a/c, run on the 208 with no problems.

I hope they are using motors rated for 208 volts. I've been involved in a couple cases of motors burning out because they were getting 208 volts and were not rated for it. But given that 208Y/120 is common, I would think lots of motors, especially three phase models, would be available for the voltage. The cases I was involved with were single phase motors.

Reply to
phil-news-nospam
Loading thread data ...

|> > Installing an outdoor construction power transformer...4160 Delta/600 |> > Delta. |> >

|> > Need phase ground lamps on the 600V side. |> >

|> > Anyone know of a circuit diagram...specs for a simple phase loss lamp | box? |> >

|> > Thanks |> >

|> > Best to All |> >

|> > Fred |> >

|>

|>

| | It appears the OP may be in Canada and you may be in New York. In most of | Canada messing around with 480 volt really makes a mess when things go bad.

So that's why 600 volts is more common there.

Reply to
phil-news-nospam

I think in many cases it is for industrial use where if power is removed, something bad happens, such as molten glass solidifying in equipment, ruining it. They run ungrounded delta so the system can tolerate one ground fault, if the fault happens, they can shut down the system properly and find/repair the fault. With a grounded wye or a grounded (anywhere) delta, the single fault will trip a breaker/blow a fuse and something will shut down unexpectedly.

Reply to
Michael Moroney

You might want to consider an impedance grounding system (in addition to an alarm). By itself, an alarm might suffer from false fault indications if the phase to ground capacitance is sufficient and unbalanced.

Reply to
Paul Hovnanian P.E.