Protecting aluminum wire not in use

Hi,
I have #2 aluminum wire going to a fuse panel. I need to disconnect the wire for a few months and then reconnect it to a circuit breaker panel.
How do I protect it when it is not connected say, from oxidation, to be able to reuse it. Also when I reconnect it do I just coat it with a antioxidant?
Thanks.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
js5895 wrote:

Wrap it with electrical tape. In several months not much is going to happen. By all means use an antioxidant when reconnecting. However, if this is a service the utility company may require crimp on copper to aluminum pigtails. They do here and we are in a relative dry climate.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 17 Oct 2006 19:34:10 -0700 snipped-for-privacy@electrician2.com wrote: | | js5895 wrote: |> Hi, |> |> I have #2 aluminum wire going to a fuse panel. I need to disconnect the |> wire for a few months and then reconnect it to a circuit breaker panel. |> How do I protect it when it is not connected say, from oxidation, to be |> able to reuse it. Also when I reconnect it do I just coat it with a |> antioxidant? |> |> Thanks. | | Wrap it with electrical tape. In several months not much is going to | happen. By all means use an antioxidant when reconnecting. However, | if this is a service the utility company may require crimp on copper to | aluminum pigtails. They do here and we are in a relative dry climate.
Is there space in today's circuit breaker panels to do that?
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@ipal.net wrote:

There is usually sufficient space to meet the Code's 75 per cent rule for splices in panelboards. If there isn't use a block of wood or the hammer handle to push the wire snug in for a tight fit. Believe me that is the way it is done. Not too many pay attention to the 75 per cent rule since it is very difficult to determine the dimensions and perform the calculations. Besides at 75 per cent it looks stuffed anyway.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@electrician2.com wrote:

I should add where the 75 per cent rule comes from. So here it is from the 2005 NEC:
408.1 Scope. This article covers the following: (1) All switchboards, panelboards, and distribution boards installed for the control of light and power circuits (2) Battery-charging panels supplied from light or power circuits 408.2 Other Articles. Switches, circuit breakers, and overcurrent devices used on switchboards, panelboards, and distribution boards, and their enclosures shall comply with this article and also with the requirements of Articles 240, 250, 312, 314, 404, and other articles that apply. Switchboards and panelboards in hazardous (classified) locations shall comply with the requirements of Articles 500 through 517.
312.1 Scope. This article covers the installation and construction specifications of cabinets, cutout boxes, and meter socket enclosures.
312.8 Enclosures for Switches or Overcurrent Devices. Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 18 Oct 2006 16:51:51 GMT, snipped-for-privacy@ipal.net wrote:

Phil, this guy is a troll. No PoCo will make you pigtail copper so they can crimp it on their aluminum drop! Laterals land on a lug somewhere and that is CU/AL.
... unless you are in a mobbed up union town.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Wed, 18 Oct 2006 19:26:41 -0400 snipped-for-privacy@aol.com wrote:
| Phil, this guy is a troll. No PoCo will make you pigtail copper so | they can crimp it on their aluminum drop! | Laterals land on a lug somewhere and that is CU/AL. | | ... unless you are in a mobbed up union town.
I left New Jersey long ago.
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@aol.com wrote:

Golden Valley Electric Coop in Fairbanks, Alaska will not accept aluminum terminations at a service. If you use aluminum conductors you have to pigtail copper to the aluminum. I suggest you broaden your scope of knowledge and stop the personal attacks. I was a State of Alaska Electrical Inspector based in Fairbanks, Alaska for 8 years from 1988 to 1993. One of my tasks was to inspect commercial services outside the city limits prior to Golden Valley hookups. Additionally, I am an IBEW journeyman electrician with over 30 years experience licensed in Alaska as an electrician and electrical administrator, and licensed in Washington as a General Electrician. Your anti-union bias makes you look like a fool, now doesn't it. Or, are you drinking in which case I might excuse you.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 19 Oct 2006 13:09:51 -0700, snipped-for-privacy@electrician2.com wrote:

I'm sorry. I have just never heard of that. We don't ever see copper on the utility side. Again no offense intended.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

You're getting it reversed. It's copper on the customer side, aluminum on the utility side. They want to use copper to aluminum pressure crimps, then have the customer land copper on the meter terminals.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 19 Oct 2006 13:09:51 -0700 snipped-for-privacy@electrician2.com wrote:
| Golden Valley Electric Coop in Fairbanks, Alaska will not accept | aluminum terminations at a service. If you use aluminum conductors you | have to pigtail copper to the aluminum. I suggest you broaden your | scope of knowledge and stop the personal attacks. I was a State of | Alaska Electrical Inspector based in Fairbanks, Alaska for 8 years from | 1988 to 1993. One of my tasks was to inspect commercial services | outside the city limits prior to Golden Valley hookups. Additionally, | I am an IBEW journeyman electrician with over 30 years experience | licensed in Alaska as an electrician and electrical administrator, and | licensed in Washington as a General Electrician. Your anti-union bias | makes you look like a fool, now doesn't it. Or, are you drinking in | which case I might excuse you.
I'd love to see some pictures of pigtails on a 350 kcmil service.
At what point are we talking about this? At the transformer on the pole, or at the meter?
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

I'm assuming at the meter. Beyond the meter is the customer's world, on the pole is the utilities world.
350kcmil implies 400A service, doesn't it? I have that, but there is a _LOT_ of room in a 400A meter main or 400A meter box. I have the CH 400A "house panel" meter main, and the meter section is 15" wide, 44" tall and 6" deep. Lots of room to make a splice if needed.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
|
| wrote: |> |> | Golden Valley Electric Coop in Fairbanks, Alaska will not accept |> | aluminum terminations at a service. If you use aluminum conductors you |> | have to pigtail copper to the aluminum. I suggest you broaden your |> | scope of knowledge and stop the personal attacks. I was a State of |> | Alaska Electrical Inspector based in Fairbanks, Alaska for 8 years from |> | 1988 to 1993. One of my tasks was to inspect commercial services |> | outside the city limits prior to Golden Valley hookups. Additionally, |> | I am an IBEW journeyman electrician with over 30 years experience |> | licensed in Alaska as an electrician and electrical administrator, and |> | licensed in Washington as a General Electrician. Your anti-union bias |> | makes you look like a fool, now doesn't it. Or, are you drinking in |> | which case I might excuse you. |> |> I'd love to see some pictures of pigtails on a 350 kcmil service. |> |> At what point are we talking about this? At the transformer on the |> pole, or at the meter? |> | | I'm assuming at the meter. Beyond the meter is the customer's world, on the | pole is the utilities world. | | 350kcmil implies 400A service, doesn't it? I have that, but there is a | _LOT_ of room in a 400A meter main or 400A meter box. I have the CH 400A | "house panel" meter main, and the meter section is 15" wide, 44" tall and 6" | deep. Lots of room to make a splice if needed.
I'd like to see how that splice is made up and how the bending is done to minimize stress on the splice.
But I don't see why they can't have aluminum going to one set of terminals and copper on the other, when the customer and utility use different metal.
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

Check on this link: http://www.tnb.com/contractor/docs/colorkeyed_spec.pdf
Look on page E49 to E51 for splices. The connectors are fairly compact and they have insulating covers.
If you look on page E70, they have terminals that are meant to go into copper only connections for putting on the ends of aluminum wire.

Normally they would. I don't like screw down terminals on aluminum. I prefer compression connectors. Conveniently so does my utility - they require meter bases with bolt holes, and they land their aluminum wire on the meter base using compression lugs for underground service when they run their wires all the way to the base.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Normally they would. I don't like screw down terminals on aluminum. I | prefer compression connectors. Conveniently so does my utility - they | require meter bases with bolt holes, and they land their aluminum wire on | the meter base using compression lugs for underground service when they run | their wires all the way to the base.
What about screw clamp connections?
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

I'm not a fan of those either. Aluminum likes to flow, and I prefer the die crimped connectors because they don't allow any flowing of the conductor.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

Why not? If it can flow out of a set screw connector, why not a crimp?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

A clamp connector does not compress the wire to the point that air is excluded from the voids. Aluminum is prone to creep and fill the air voids between the wires, releasing the clamping pressue. The T&B (or other good brands) crimp properly done leaves no voids.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 23 Oct 2006 16:09:57 -0400 snipped-for-privacy@aol.com wrote:
| wrote: | |>I'm not a fan of those either. Aluminum likes to flow, and I prefer the die |>crimped connectors because they don't allow any flowing of the conductor. | | | Why not? If it can flow out of a set screw connector, why not a crimp?
That's what I'm curious about.
I don't have any experience with the compression crimps. But it looks to me like they are deforming the wire at the points of crimp such that the undeformed portion toward the end of the wire cannot slip past the crimp point without having some huge force being applied to do it. A screw connector can't normally do that. Maybe a clamp with some teeth that is pressured down with a high torque screw might accomplish it. But I would be quite comfortable with having these compression crimps.
What I wonder is if they could be used for a big grounding system made entirely of copper in lieu of cadwelds, even for the buried joints.
--
|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org) / Do not send to the address below |
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

These can:
http://www-public.tnb.com/contractor/docs/blackburn_grounding.pdf
For ground grid work, check out pages F97 to F99
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload